Manual Chapter : System Monitoring Overview
Applies To:
  • F5OS-A
    2.0.0
You can monitor the configured system settings in the system webUI and CLI.
You can view active system alarms and events in the webUI and CLI.
The Alarms & Events screen lists alert information for system components (such as PSU, firmware, and LCD) that have currently crossed a performance or health threshold. Use this screen to identify the specific component that is affected.
  1. Log in to the webUI using an account with admin access.
  2. On the left, click System Monitoring > Alarms & Events.
  3. Choose from one of these actions:
    • To refresh the alarms or events list, under the Alarms area click Refresh icon on the right of the screen.
    • To display events result by time preference, under the Eventsarea select a value from the Time dropdown.. The default value is one hour. For example, select five minutes to display any event that occurred in the last five minutes.
    • To display events by severity, select a value from the Severity list. The default value is INFORMATIONAL.
    Option Description
    Emergency Emergency system panic messages
    Alert Serious errors that require administrator intervention
    Critical Critical errors, including hardware and file system failures
    Error Non-critical, but possibly important, error messages
    Warning Warning messages that should be logged and reviewed
    Notice Messages that contain useful information, but might be ignored
    Informational Messages that contain useful information, but might be ignored
    Debug Detailed messages used for troubleshooting
You can view information about active system alarm conditions from the CLI.
  1. Connect using SSH to the management IP address.
  2. Log in to the command line interface (CLI) of the system using an account with admin access.
    When you log in to the system, you are in user (operational) mode.
  3. View a list of active system alarm conditions.
    show system alarms | tab
    This example shows a power supply unit (PSU) redundancy fault:
    appliance-1# show system alarms | tab
    ID     RESOURCE        SEVERITY  TEXT                           TIME CREATED
    65793  psu-1           ERROR     PSU fault detected             2022-06-01-11:11:11.999825828 UTC
You can import, export, download, or delete files asynchronously depending on which directory you select to work in. All file transfers are done using the HTTPS protocol.
You can import a file from an external server into the system from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.
Note: If you want to import the contents of a tar file, you need to extract the contents first before you can import them onto the F5 system.
You can import files into these directories on the system:
  • configs/
  • diags/shared
  • images/import/services
  • images/staging
  • images/tenant
  • images/import/iso/
  • images/import/os/
You can download files in these directories from the system to your local workstation from the webUI:
  • log/host
  • configs
  • diags/core
  • diags/crash
  • diags/shared
  • log/confd
  • log/system
You can upload files in these directories from your local workstation to the system from the webUI:
  • configs
  • images/staging
  • images/tenant
  • images/import/os/
  • images/import/services/
You can export a file from the system to an external server from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.
You can export files into these directories from the system:
  • configs
  • log/
  • log/confd
  • log/controller
  • log/host
  • log/system
  • diags/
  • diags/core
  • diags/crash
  • diags/shared
  • images/
  • images/import
  • images/staging
  • images/tenant
  • images/import/os/
You can delete files (to which you have file permissions) on the system only from the diags/shared or configs directories from either the webUI or the CLI.
File Utilities are available in the webUI. You can use File Utilities to upload, download, import, export, and/or delete files asynchronously depending on which directory you select to work in. All file transfers are done using HTTPS protocol.
  2. On the left, click System Monitoring > File Utilities.
  3. From the Base Directory dropdown, browse the directories and click subfolders to view their contents and the commands that are available from each one.
    From a subfolder, click the left arrow next to the path to navigate back to the main folder.
  4. To import a file:
    1. Click Import.
    2. In the drawer, enter the URL of the file to import.
    3. Provide the Username and Password only if required by the remote host.
    4. Select Ignore Certificate Warnings if you want to skip warnings when importing files (such as if the remote host does not have a valid CA-signed certificate).
    5. Click Import File to begin the import.
  5. To export a file:
    1. Select the file and click Export.
    2. In the drawer, enter the Server URL for where to export the file.
    4. Select Ignore Certificate Warnings if you want to skip warnings when importing files.
    5. Click Export File to begin the export.
  6. To upload a file:
    Click Upload and select the file you want to upload. The selected file will be uploaded.
  7. To download a file:
    Select the file and click Download. The selected file will be downloaded.
    On the system controller and chassis partition, you can delete files from diags/shared.
  8. To delete a file, select the file and click Delete.
    You can delete files only from the diags/shared directory.
You can view the status of a file transfer operation to view its progress and see if it was successful. If you want to cancel an in-progress file transfer operation, click Cancel button. If an operation fails, hover over the warning icon to see the error that occurred.
Note: A runtime error displays in the File Transfer status area, if an invalid operation is performed.
You can view the contents of a file from the CLI.
  1. Log in to the command line interface (CLI) of the system using an account with admin access.
  2. View the contents of a file.
    file show <*local-file-path*>
    This example shows how to view the contents of the platform.log file:
    appliance-1# file show log/system/platform.log | until 5
    2022-12-27T21:34:24.718946+00:00 appliance-1 tmstat-agent[1]: priority="Info" version=1.0 msgid=0x1601000000000008 msg="TMSTAT directory set from command line." directory="cluster".
    2022-12-27T21:34:24.719592+00:00 appliance-1 ihealthd[8]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
    appliance-1# file show log/system/platform.log | until 15
    2022-12-27T21:34:24.720155+00:00 appliance-1 alert-service[9]: priority="Notice" version=1.0 msgid=0x2201000000000001 msg="Alert Service starting." version="3.11.7" date="Thu Nov  3 13:25:15 2022".
You can import a file from an external server onto your system from the CLI.
  2. Import a file.
    file import remote-url <*ip-address-and-file-path*> local-file <*local-file-path*> username <*user*> password [ remote-port <*port-number*> } [ protocol [ https | scp | sftp ]] [insecure]
    Note: The insecure option ignores certificate warnings during the transfer.
    This example shows how to import a Base OS ISO to the system:
    appliance-1# file import remote-url https://files.company.com/images/F5OS-A-1.6.x-xxxxx.R5R10.iso
      local-file images/staging username admin password
    Enter the password at the prompt:
         Value for 'password' (<string>): ********
    result File transfer is initiated.(images/staging/F5OS-A-1.6.x-xxxxx.R5R10.iso)
    Note: If the file import doesn’t work, you can alternatively use secure copy (SCP) to copy the image file to the images/staging directory of the system.
  3. Optionally, you can check the file transfer status.
    appliance-1# file transfer-status
    When the file transfer completes, the Status displays Complete.
  4. Export a file.
    file export remote-url <*ip-address-and-file-path*> local-file <*local-file-path*> username <*user*> password [ remote-port <*port-number*> } [ protocol [ https | scp | sftp ]] [insecure]
    appliance-1# file export local-file configs/backup1.xml remote-file /tmp/backup1.xml
      remote-host 192.51.100.75 username root
    The system requests the password for the remote account.
    result File transfer is initiated.(configs/backup1.xml)
  5. Delete a file.
    file delete local-file diags/shared/<*file-name.xml*>
    This example shows how to delete a file:
    appliance-1# file delete local-file diags/shared/backup1.xml
    You can only delete files from the diags/shared or configsdirectory.
You can cancel an in-progress file import onto your system from the CLI.
  2. Get the operation identifier for the file transfer process.
    show file transfer-operations
    A summary similar to this example displays:
    appliance-1# show file transfer-operations
    file transfer-operations transfer-operation images/import/iso/F5OS-A-1.6.0-1234.iso
      files/F5OS-A/images/F5OS-A-1.6.0-1234.iso "Import file" "HTTPS   "
     operation-id IMPORT-C16QYpun
     status       "In Progress (13.0%)"
     timestamp    "Fri Mar 24 23:05:54 2023"
  3. Cancel the specified file transfer.
    file abort-transfer operation-id <*id*>
    This example shows canceling a specified in-progress file transfer:
    appliance-1# file abort-transfer operation-id IMPORT-C16QYpun
    Aborting will stop the file transfer. Do you want to proceed? [yes/no] yes
    result File transfer abort operation initiated.
You can export a file to an external server from your system from the CLI.
  2. Export a file.
    file export insecure local-file <*local-file-path*> protocol { https | scp | sftp } remote-file <*remote-file-path*> remote-host <*ip-address-or-fqdn*> remote-port <*port-number*> remote-url <*ip-address-or-fqdn*> username <*user*> web-token <*remote-system-token*>
You can delete files from the CLI.
  2. Delete a file.
    You can delete files only from the diags/shared or configsdirectories.
This release supports F5 rSeries platform Foreground diagnostic processes which include Foreground diagnostic profiles. These profiles include the diagnostic analysis of specific components (Such as, CPU, memory, disk).
Foreground diagnostics let you troubleshoot F5 rSeries hardware while the system is still running. You can check the health of hardware components and services without taking tenants offline.
What foreground diagnostics include:
  • Profiles and governance model: A set of rules that control how and when diagnostics run safely on active systems.
  • Task operating model: A framework that defines diagnostic tasks, who runs them, and the business value each task provides.
  • In-service troubleshooting: The ability to run diagnostic checks on live, active hardware without disrupting tenant workloads.
You can perform the diagnostics operations using a CLI, webUI, and REST API. This diagnostic tool allows you to perform following operations:
  • You can start, stop, and execute profile diagnostics for individual nodes.
  • You can view the state of a diagnostic profile, including its unique profile ID, input parameters, run result (passed, error, failure, or inconclusive), run state (running, completed, or aborted), total execution duration, start time, and estimated progress percentage.
Troubleshooting workflows
Foreground diagnostic results are captured as part of the QkView collection, providing enhanced visibility into system health for issue identification and resolution. When you generate a QkView, the system captures diagnostic data.
You can find the Foreground diagnostic profile results in theQkView 'diag-agent/file-system/tmp/profile-results' directory. TheQkView collection process is standard on both F5 rSeries platforms. For QkView generation, see System reports (QKView) overview
The following is a list of nodes and diagnostic profiles of the platforms:
Node Profile Profile summary
Appliance file-system-status Reports file system status (r5000, r10000, and r12000 only): checks file system space, reports additional status indicators, and reports RAID status if available.
Appliance platform-test Runs platform diagnostics: verifies CPLD read/write from both the host and the LOP, identifies CPLD registers for system health insight, performs PCIe device checks (bus presence, speed, width, and link errors — except CC), scans a device subset excluding internal-to-CPU devices, and checks TPM status (except P5a).
Appliance memory-test Performs DIMM consistency check (verifies all DIMMs are the same vendor and model) and DIMM count/memory size verification (confirms all DIMMs are present and correctly sized for the platform).
Appliance aom-test r5000, r10000, and r12000: Checks AOM health — verifies LOPd is running and the UDP socket is present, confirms the USB device is present, and checks LOP health.
r2000 and r4000: Checks BMC-based AOM health — verifies the IPMI bus is operational and checks BMC health status.
Appliance hardware-suite Runs the Appliance hardware suite, which includes: aom-test, drive-status, fan-status, lcd-status, memory-test, platform-test, and psu-status.
Drive drive-status Reports the current state of a specified drive, or all drives if no input parameter is provided: serial number, model name, firmware version, user capacity, SMART status, error log status, and important SMART attributes.
LCD lcd-status Verifies LCD info, checks that the LCD is reporting healthy, confirms LCD services are reachable, and queries LCD sensors.
Fantray fan-status Checks device presence, reads device sensors (checks limits and sensor faults), reads device status, and checks fan RPM.
PSU psu-status Checks PSU consistency and presence, reports PSU model/serial number/firmware version, and checks all generated binary alerts (sensors and PMBus status registers).
You can monitor health and state of system from the CLI and webUI.
The list of tasks are performed during the diagnostics operation.
Diagnostic Operations Description
Nodes Displays the list of available nodes for the current system
List List all of the available profiles for the given node
Profile Help Displays the help for a given profile, shows descriptions, parameters and example run commands
Health Displays the high-level health of each node within the system
Start
Status
Stop Stop a profile that is currently running
Run
Results Displays the results of a profile that is running or has run in the past
History A list of profiles that have run in the past
The listed tasks outline key attributes monitored during the operation of a profile.
Field Description
Profile Id The unique ID of the profile being run.
Parameters The parameter name/value pair used to invoke the profile.
Result The run result of the profile, which can be one of the following: passed, error, failure, inconclusive.
Execution State The current execution state of the profile, which can be: running, completed, aborted.
Execution Duration The total execution time for the given profile, presented as a string.
Started At The timestamp indicating when the profile was started.
Progress An estimated percent of progress towards completion, with 100% indicating the profile is done.
  2. On the left, click System Monitoring > Foreground Diagnostics.
  3. Select the Node from the dropdown for which you want to run the diagnostics.
    In the Profiles area, list of profile associated with the Node are displayed.
  4. Run the diagnostics for a profile:
    • Run the system’s health diagnostics for a profile without parameter value:
      • Select the profile checkbox for which you want to run the diagnostics and click Run Diagnostics.
    • Run the system’s health diagnostics for a profile with parameter value:
      • Select the desired profile checkbox and click RunDiagnostics.
        A new drawer with list of parameters and parameter values opens.
        • Click the Run All button to run diagnostics on all parameters using default values.
        • Select your desired options and click Run Selected to run diagnostics on selected parameters. Use the dropdown next to each parameter to modify its value.
      • The drawer closes when the diagnostic run starts, and the Diagnostics Status section displays the run details.
  5. In the Diagnostics Status area, the state of the current diagnostics running on your profile is displayed:
    • Active runs include runs triggered from the CLI or runs in progress from previous sessions
    • Health check initiated. The table displays a Stop button next to the progress indicator.
    • The table displays current result information for the running check.
    • Health check initiated on parameterized profile displays parameter name and parameter value along with health check progress state.
    • When Health check aborted a table displays the aborted execution state. You can expand the row to view detailed result information.
  6. To stop the diagnostics, click Stop button. Upon clicking, a popup will appear displaying the latest status information.
You can view the history and results of system’s health diagnostics for a profile from the webUI.
  3. Select the Node from the dropdown for which you want to view the information.
  4. Select the profile checkbox, click View History.
    The system displays a drawer with the profile’s diagnostic history details.
  5. Click View Results.
    The system displays both the parameter table (for profiles that support parameters) and the results table.
You can run the system’s foreground diagnostics for a profile from the CLI
  2. Change to config mode. config The CLI prompt changes to include (config).
  3. Run the diagnostics:
    • Run diagnostics for a profile without a parameter value:
      system health diagnostics nodes node <node-name> profiles profile <profile-name> start
      A summary this example displays:
        appliance-1(config)# system health diagnostics nodes node appliance profiles profile platform-test start
        profile {
            result inconclusive
            exec-state starting
            exec-duration 1.139377ms
            started-at 2025-09-03T09:38:33Z
            progress 0
            profile-id A.68b7dc2c.3c
    • Run diagnostics for a profile with a parameter value:
      system health diagnostics nodes node <node> profiles profile <profile-name> start parameters { parameter { name <node> value <parameter-value>} }
      A summary to this example displays:
      appliance-1(config)# system health diagnostics nodes node psu profiles profile psu-status start parameters { parameter { name psu value psu-1 } }
          profile {
              parameters {
                  parameter {
                      name psu
                      state {
                          value psu-1
              result inconclusive
              exec-state starting
              exec-duration 1.36711ms
              started-at 2025-01-21T19:02:28Z
              progress 0
              profile-id A.678fef33.21
You can stop diagnostics for a profile, if it is currently in the running state. A unique profile identifier is generated during the Start command.
You can use the profile ID to stop the execution of the diagnostic process.
  3. Stopping a diagnostic process for a profile:
    system health diagnostics nodes node <platform> profiles profile <profile-name> action stop <profile-id>
You can view and monitor the system’s health statuses of a profile from the CLI.
  2. Display the system’s health.
    show system health diagnostics nodes node <node name> profiles profile <profile id> state
    appliance-1# show system health diagnostics nodes node appliance profiles profile platform-test ids id A.68b7dc2c.3c state
    state result  passed
    state exec-state complete
    state exec-duration 0.372
    state started-at 2025-09-03T09:38:33.084076831Z
    state progress 100
You can view results of the system’s health statuses for the specific parameters and profiles from the CLI
  2. Display the history and results of diagnostics for a profile:
    show system health diagnostics nodes node <node name> profiles profile <profile name> ids id < profile id > full
    Example:
    appliance-1# show system health diagnostics nodes node appliance profiles profile file-system-status ids id A.69faf35e.28 full
The webUI includes options for configuring remote log servers and the log severity level for individual software components and services.
From the webUI you can generate a system report, or QKView file, to collect configuration and diagnostic information from the rSeries system if you have any concerns about your system operation. The QKView file contains machine-readable (JSON) diagnostic data and combines the data into a single compressed tar.gz format file. You can upload the QKView file to F5 iHealth where you can get help to verify proper operation of the system and get help with troubleshooting and understanding any issues you might be having and ensure that the system is operating at its maximum efficiency.
You can view event logs and configure secure remote logging from the CLI. You can also send host log files, which are in the /var/log directory, as well as audit.log files to the remote server from the CLI.
You can add and display information about configured remote log servers from the webUI. You can also change the log severity level for individual software components and services.
  2. On the left, click System Monitoring > Log Settings.
  3. To include hostname configured for your system in the log:
    1. On the Include Hostname tile, click the edit icon.
    2. Select True from the Include Hostname field dropdown.
    3. Click Save.
    Note: By default, the Include Hostname dropdown value is set to false.
  4. To add access to a Remote Log Server, click Add.
    1. In the Server field, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the remote server. After the remote log server is saved, you cannot modify the server address.
    2. In the Port field, enter the port number of the remote server.
      The default port value is 514.
    3. For Protocol, select UDP or TCP to choose between TCP or UDP input.
      Note: The Authenticationfield is displayed only when the TCP protocol is selected.
    4. From the Selectors field,
      • Select LOCAL0 or AUTHPRIV
      • From the Severity list, select the severity level of the messages to log
      Option Description
      Debug Verbose messages used for troubleshooting
      Note: To add more selectors, click Add. To remove the existing selectors, select it and click Delete.
    5. For Authentication, select the enable or disable option from the list. The default value is Disabled. This option is visible when the TCP protocol is selected while configuring the remote log server. If the UDP protocol is selected, the authentication value is saved as N/A.
    6. Click Save.
  5. To delete a remote log server, select the server and click Delete.
  6. To configure Host Log Settings, click on the edit icon on the Host Log Settings card.
    1. For Host Log Forwarding, select the enable or disable button for remote forwarding. The default value is Disabled.
    2. To add the required host log files to the Selected Files panel, click the required host log files checkboxes. Click on directories to view the files and sub-directories and select individual files within the directory.
      The Selected Files option allows the host logs files to be forwarded from the directory and subdirectories.
    3. For Selectors, select the required facility and severity options from the list. To add more selectors, click Add. To remove the existing selectors, select it and click the Delete.
    4. For Custom Log File, enter the log file in the text box and click Add to manually add host log file names to the Selected Files panel.
    5. Click Save.
  7. For TLS Certificate & Key, click chevron/expand icon to view the configured TLS Certificate and Key values. Click on edit icon on TLS Certificate & Key card.
    1. Update the values in the TLS Certificate and TLS Key fields.
    2. Click Save.
    Note: If the authentication value is set as enabled for any of the remote log servers, you cannot be able to clear the TLS configuration fields.
  8. For CA Bundles, click Add to enter the Name and TLS certificate.
    1. Enter the Name of the CA certificate.
    2. Update the value in the TLS Certificate field.
    3. Click Save.
    Note: When any of the remote server authentication is enabled, you cannot delete the CA bundle.
  9. On the Log Settings screen, click the chevron icon to review the software component log levels for individual software components and adjust them as needed. Click Update if you made changes.
    The log levels determine at what level events (and all higher levels) are logged for each service. Informational is the default so all except debug-level events are logged.
    Component
    Description
    alert-service
    Software component that handles ‌alerts and events at the system level. These components use ConfD to process updates and manage the status of the Alarm LED depending on the severity of the alert.
    dagd-service
    Software component that manages the distribution of Tenant traffic.
    fips-service
    Software component for System FIPS configuration and handles system integrity check requests.
    kubehelper
    Software component triggered during tenant deployment and runs as a assistant task before tenant container is created. For BIG-IP
    • Covert qcow2 image to raw format for BIG_IP tenant only.
    • Reserves huge pages for the tenant
    • Creates host-net interface for host and tenant communication purposes.
    • Creates a tenant management interface for BIG-IP NEXT tenants and includes route integration.
    lldpd
    Software component for LLDP configuration.
    orchestration-agent
    Software component for Tenant Orchestration which includes tenant configuration and deployments.
    platform-monitor
    The Monitoring Agent is responsible for: - Creating telemetry pipelines that query data periodically.
    • Applying processors to the data.
    • Sending the data to various destinations.
    rsyslog-configd
    Software component for remote syslog configuration handling.
    sys-host-config
    Software component responsible for: - Setting up management IP to access the device, collecting management interface stats, and enabling/disabling of management interface.
    • Setting up DNS configurations.
    • Updating required files for internal subnet changes.
    • Exchanging internal subnet changes to LCD server.
    • Updating Base MAC and MAC pool size in ConfD.
    • Addition/Deletion of SSH IP table rules.
    • Additionally, it offers backend code support for various ConfD configurations such as:
      • Hostname
      • Date
      • Motd Banner
      • System Reboot
      • SSH idle timeout
    utils-agent
    Software component that manages file transfer operations such as import, export, delete, and download/upload.
    api-svc-gateway
    Software component that manages requests and subscriptions for Tenants on the appliance.
    datapath-cp-proxy
    Software component that manages Tenant datapath setup requests and configuration.
    firewall-manager
    One software component that enables the setting up of a whitelist for designated source IP addresses and destination ports such as HTTP, HTTPS, RESTCONF, SNMP, and vConsole.
    l2-agent
    Software component responsible for managing the setup and status of physical connections (such as interfaces and portgroups) and the configuration and status of Layer-2 components (such as VLANs, LAGs, and FDB).
    lopd
    Software component to manage communication with the LOP (AOM).
    partition-common
    The system component incorporates standard ConfD utility functions that enhance the CLI interface.
    platform-stats
    Software component responsible for capturing the various utilization stats of the CPU, drives and memory and storing the data in TMSTAT stat tables.
    snmp-service
    Software component used to configure system SNMP configuration such as community, target, and user.
    system-control
    System component that implements configuration backup and restore.
    vconsole
    Software component for providing authenticated virtual console access to F5OS tenants.
    appliance-orchestration-manager
    Appliance Onboard Monitoring Daemon (OMD) is a service daemon that oversees the internal coordination of tasks via Kubernetes (K3S). It is responsible for setting up and controlling all required device plugins that enable communication with different hardware components.
    diag-agent
    The Diagnostic Agent is responsible for running various diagnostic profiles, gathering and exporting telemetry data and providing system health information and producing the hardware alerts.
    http-server
    Software component responsible for running the apache HTTPD server.
    lacpd
    Daemon responsible for negotiation of LACP over system interfaces.
    network-manager
    Software component responsible for managing datapath related resources, such as MAC Addresses. It also manages datapath tables that route traffic between Tenants and Interfaces.
    platform-diag
    Software component for providing statistics reports and measurements on top of the low-level hardware.
    platform-stats-bridge
    Software components responsible for handling the platform statistics to display on user interfaces.
    snmp-trapd
    Software component that process the system alerts/events as traps and sends it to SNMP manager.
    tmstat-agent
    Software component for providing the framework which can be used to store the statistics data in centralized location on each host.
    audit-service
    Software component for capturing the system configuration related logs in audit log.
    diag-data
    Software component for primarily tasked with collecting important information periodically from an F5OS device and sending that data back to F5 for analysis purposes.
    ihealth-upload-service
    Software component for providing secure way of transporting support package to F5 to different target destination. This service offers historical track records of support package uploads with configurable data retention policy.
    lacpd-proxy
    Daemon responsible for reporting the results of LACP negotiation from lacpd.
    nic-manager
    Software component which manages the datapath network interfaces.
    platform-fwu
    Software component responsible for updating and reporting firmware.
    qat-confd-service
    Service for communicating QAT device tenant assignments to ConfD tables.
    sshd-crypto
    Service that manages all the crypto algorithms configuration for sshd.
    tmstat-merged
    Software component for providing framework to integrate and divide statistics streams.
    authd
    Software component responsible for managing the configuration settings for various AAA (Authentication, Authorization, Accounting) mechanisms supported by the F5OS system.
    disk-usage-statd
    None
    ihealthd
    Software component responsible for handling ihealth configuration parameters and start a qkview upload by sending a request to ihealth.
    license-service
    Software component responsible for system licensing installation.
    node-agent
    Software component triggered during tenant deployment and node reboots. - Creates a tenant management interface for BIG-IP NEXT tenants and includes route integration.
    • Adds water-marking rules for BIG-IP NEXT tenants.
    • In charge of allocating large pages for chassis during tenant deployments.
    platform-hal
    Software component that provides other services with access to platform/hardware data and configuration.
    qat-plugin
    Kubernetes device plugin for reporting and managing QAT device resources and resource activities related to their respective tenant assignments.
    stpd
    Software component for configuring STP L2 protocol in platform.
    upgrade-service
    Software component for processing the system image and package upgrade requests.
    confd-key-migrationd
    The software component for transfering ConfD configuration from one system to another requiring the same encryption key. This is necessary to migrate encrypted element values successfully.
    dma-agent
    Software component for Core Offload feature that functions as a buffer broker, allowing multiple tenants to share access to the FPGA while remaining isolated from one another.
    image-agent
    A software module that manages the validation of imported tenant images and displays the current status of both tenant and platform images on the user interface.
    line-dma-agent
    Software component which is an fundamental layer of tcpdump in the VELOS/rSeries family.
    optics-mgr
    Software component that is responsible for storing the tuning values for supported optics. When provided with an optic, returns the proper tuning.
    platform-mgr
    This software component displays the versions of platform components, CPUs, memory, and firmware. It also automatically initiates firmware upgrades when upgrading or installing a new ISO and rebooting.
    qkviewd
    Software component designed to create diagnostic snapshots in containerized systems, known as QKView. A QKView file is a compressed file with diagnostic info from containers, the host, and other systems.The main qkviewd service operates within a container, while qkviewd-host service collects data on the host. A peer system is another system running the qkviewd daemon.
    sw-rbcast
    Software component that is responsible for forwarding broadcast traffic received on a shared VLAN to the tenants which share that VLAN. A secondary responsibility is to forward DLF (destination look-up failures) requests to the fpgamgr component, so that they can be resolved.
    user-manager
    Software component responsible for the management and configuration of local users on the system such as user accounts, groups/roles, and passwords.
    fpgamgr
    Software component, which manages the datapath FPGAs. ‌This includes ‌front panel interfaces, L2 functionality, and other advanced FPGA features.
    lcd-webserver
    Software component providing a webserver to operate the LCD user interface.
    sshd-crypto
    Software component for handling sshd crypto agility configurations.
  10. Click Save to save the log settings.
The system logs events to the appliance.log file located in the log/host directory. To list files and view the contents of log files, you use the file command from the CLI.
  3. List all files in the log directory.
    file list path [ log/confd/ | log/host/ | log/system/ }
    This example shows an excerpt of the contents of the log/host/ directory:
    appliance-1# file list path log/host
    entries {
        name anaconda/
        date Thu May 12 17:01:36 UTC 2022
        size 4.0KB
    entries {
        name ansible.log
        date Fri Jun 17 16:18:02 UTC 2022
        size 0B
    entries {
        name appliance.log
        date Fri Jun 17 16:18:19 UTC 2022
        size 9.8KB
    entries {
        name audit/
        date Fri Jun 17 14:59:04 UTC 2022
        size 4.0KB
    entries {
        name boot.log
        date Thu May 12 17:02:35 UTC 2022
        size 105B
  4. Show the contents of a log file.
    file show [ log/confd/<*filename*> | log/host/<*filename*> | log/system/<*filename*> ]
    This example shows the contents of the log/host/boot.log file:
    appliance-1# file show log/host/boot.log
    May 12 10:02:35 localhost NET[1605]: /etc/sysconfig/network-scripts/ifup-post : updated /etc/resolv.conf
  5. Show only the most recent entries in a log file.
    file tail [ log/confd/<*filename*> | log/host/<*filename*> | log/system/<*filename*> ]
    This example shows the last ten lines of the appliance.log file and uses the -f option to append output as the file grows:
    appliance-1# file tail -f log/host/appliance.log
    2022-06-17 16:18:03.267761 - OMD log is initialized
    2022-06-17 16:18:03.267761 - 8:-738199808 - applianceMainEventLoop::Orchestration manager startup.
    2022-06-17 16:18:03.270244 - 8:-754985216 - Can now ping appliance-1.chassis.local (100.65.60.1).
    2022-06-17 16:18:03.723485 - 8:-754985216 - Successfully ssh'd to appliance 127.0.0.1.
    2022-06-17 16:18:14.399076 - 8:-738199808 - Appliance 1 is ready in k3s cluster.
    2022-06-17 16:18:14.399095 - 8:-738199808 - K3S cluster is ready.
    appliance-flannel_image|localhost:2003/appliance-flannel:0.13.0
    No Image Changes Found for normal reboot
    appliance-multus_image|localhost:2003/appliance-multus:3.6.3
    _
The system logs events to the appliance.log file located in the var/log directory and enables you to send these logs to a remote server. By configuring secure remote logging from the CLI, you can send logs in audit.log to a remote server. Secure logging is disabled by default.
  3. Change to config mode.
    config
  4. Configure secure remote logging. The default value is disabled.
    system logging remote-servers remote-server <*ip-address*> config proto { udp | tcp | remote-port <*port-number*> authentication { disabled | enabled }
    The default protocol is upd, and the default port number is 514.
    This example enables secure remote logging:
    appliance-1(config)# system logging remote-servers remote-server
      192.0.2.58 config proto tcp remote-port 80 authentication enabled
  5. Add certificate or key details for secure remote logging.
    system logging tls { certificate | key } <*string*>
  6. Add CA bundle details for secure remote logging.
    system logging tls ca-bundles ca-bundle <*name*> config name <*name*> content <*ca-cert-contents*>
    Note: The certificate bundle that you specify must include the certificate chain of the certificate authority.
  7. Commit the configuration changes.
    commit
  8. Return to user (operational) mode.
    end
  9. Verify the authentication, certificate, key, and CA bundle configuration.
    show running-config system logging tls { certificate | key | ca-bundles } <*string*>
You can disable secure remote logging from the CLI.
    config
  4. Disable secure remote logging.
    This example disables secure remote logging:
      192.0.2.58 config proto tcp remote-port 80 authentication disabled
  5. Remove authentication details from secure remote logging.
    no system logging remote-servers remote-server <*ip-address*> config authentication
  6. Remove certificate or key details from secure remote logging.
    no system logging tls { certificate | key } <*string*>
  7. Remove CA bundle details from secure remote logging.
    no system logging tls ca-bundles ca-bundle
  8. Commit the configuration changes.
    commit
  9. Return to user (operational) mode.
    end
  10. Veify the authentication, certificate, key, and CA bundle configuration.
Simple Network Management Protocol (SNMP) is an industry-standard protocol that enables you to use a standard SNMP management system to remotely manage network devices. F5 rSeries systems support SNMPv1, SNMPv2c, and SNMPv3. You can configure the system from both the CLI and webUI.
SNMP support is available in different ways, depending on which F5OS software version you are using. On F5 rSeries systems, SNMP is available from both the CLI and webUI.
F5 recommends using the newer system snmp commands, which include support for SNMP versions 1, 2c, and 3. For more information on the older commands, see:
  • F5 rSeries CLI Reference
  • F5 rSeries Planning Guide
    F5OS-A software version
    Older CLI (v1/v2c only)
    Newer CLI (v1/v2c/v3)
    1.2.0
    SNMP-COMMUNITY-MIB
    SNMP-NOTIFICATION-MIB
    SNMP-TARGET-MIB
    SNMP-VIEW-BASED-ACM-MIB
    SNMPv2-MIB
    system snmp communities system snmp engine-id
    system snmp targets
    system snmp users
Before you configure SNMP access for F5 rSeries systems:
SNMPWALK is an application on an SNMP management system that performs SNMP GETNEXT requests to query a network device for information. You can provide an object identifier (OID) to specify which portion of the object identifier space to search using GETNEXT requests. The SNMP management system queries all variables in the subtree below the specified OID, displays these values to the user, and stops when it returns results that are no longer inside the range of the specified OID.
These SNMP system object IDs (OIDs) are defined for each F5 rSeries system type:
  • 1.3.6.1.4.1.12276.1.3.1.1 (f5OsAppR5x00)
  • 1.3.6.1.4.1.12276.1.3.1.2 (f5OsAppR10x00)
  • 1.3.6.1.4.1.12276.1.3.1.3 (f5OsAppR2x00)
  • 1.3.6.1.4.1.12276.1.3.1.4 (f5OsAppR4x00)
The IDs display in text format when the corresponding MIB is loaded in your SNMP management system. If the MIB is not loaded, the walk displays in OID format.
To more accurately map these system OIDs, you must download the F5-OS-SYSTEM-MIB.mib file and load it into your SNMP management system. To download the F5 MIB files, use File Utilities in the webUI on the left, click System Monitoring > File Utilities, and then from Base Directory, select mibs, select a .tar.gz file, and click Download.
You can configure the SNMP port from the rSeries webUI.
  2. On the left, click System Monitoring > SNMP.
  3. Click on the edit icon on the Properties card.
  4. For Port, enter the required value. The allowed values for the Port are either 161 or in the ranges of [1024-7000, 7033-8887, 8889-65535]. To check whether a port is valid or not, we have inline validation.
    Note: The port configured in the SNMP Configuration area is reflected on the Allow List Entry screen of the Allowed IP Addresses section under System Security in the System Settings chapter. When an allowlist is created with an SNMP port, the user is not allowed to change the SNMP Port on the SNMP Configuration area, which can cause an error. For more information, see Configure the system allow list from the webUI.
  5. Click Save.
You can configure the SNMP properties from the webUI.
  3. In the Properties section, click the edit icon to specify values in the required fields.
    • System Contact
    • System Location
    • System Name Note: The maximum number characters limit is 255.
  4. Click Save.
You can configure SNMP communities with either version 1, version 2c, or both security models from the webUI.
  3. In the Communities area, click Add.
  4. For Name, enter a descriptive name for the community.
  5. For Security Model, select from these security models: v1, v2c, and v1 and v2c.
  6. Click Save.
You can configure SNMP version 3, which is a user-based security model, from the webUI. This model provides support for additional authentication and privacy protocols.
  3. In the Users area, click Add.
    The Add v3 User drawer displays.
  4. For User, enter the user name.
  5. For Authentication Protocol, select from these protocols: MD5, SHA, SHA256, SHA512, or None.
  6. For Authentication Password, enter the password for the specified user.
  7. For Privacy Protocol, select from these protocols: AES128, AES192, AES256, DES, or None.
  8. Click Save.
Before you can add an SNMP target, you must have already configured either the SNMPv1/v2c community or SNMPv3 user.
You can configure SNMP targets from the webUI. These are required to send system-generated traps to a manager. You can choose either community (v1/v2c) or user-based (v3) security.
  3. In the Targets area, click Add.
    The Add Target screen displays.
  4. For Name, enter a descriptive name.
  5. For Security Model, select from these security models: v1, v2c, or v3.
  6. Select one of these options, depending on the selected security model:
    • If you selected v1 or v2c, for Community, select the community that you created with that security model.
    • If you selected v3, for User, select the user that you created.
  7. For IPv4/IPv6, select either IPv4 or IPv6.
  8. For Address, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the target.
  9. For Port, enter the port number for the target.
    The default value is 162, and the range is from 1024 to 65535
  10. Click Save.
You can configure the SNMP port from the CLI.
    config
  3. Configure SNMP port
    system snmp config port <*value*>
    he following example configures SNMP port ‘5000’:
    appliance-1(config)# system snmp config port 5000
    Note: The allowed values for the Port are either 161 or in the ranges of [1024-7000, 7033-8887, 8889-65535]. The port configured in the SNMP Configuration area is reflected on the Allow List Entry screen of the Allowed IP Addresses section under System Security in the System Settings chapter. When an allowlist is created with an SNMP port, the user is not allowed to change the SNMP Port in the SNMP Configuration area, which can cause an error. For more information, see Configure the system allow list from the webUI.
  4. Commit the configuration changes.
    commit
You can configure the SNMP properties from the CLI.
    config
  3. Configure SNMP properties
    SNMPv2-MIB system sysName <*system name*> sysLocation <*location name*> sysContact <*contact details*>
    A summary of this example displays:
    appliance-1(config)# SNMPv2-MIB system sysName f5System sysLocation boston sysContact support@f5.com
    commit
You can configure SNMP communities with either version 1, version 2c, or both security models from the CLI.
    config
  4. Configure a community.
    system snmp communities community <*community-name*> config security-model { v1 | v2c }
    This example creates a community that uses the v2c security model:
    appliance-1(config)# system snmp communities community v2comm config
      security-model v2c
    This example creates a community that uses both v1 and v2c community models:
    appliance-1(config)# system snmp communities community v1v2c config
      security-model [ v1 v2c ]
  5. Commit the configuration changes.
    commit
  6. Return to user (operational) mode.
    end
  7. Verify the community configuration.
    show system snmp communities
    appliance-1# show system snmp communities
                          SECURITY
    NAME       NAME       MODEL
    v1v2c      v1v2c     [ v1 v2c ]
    Note: This example shows both security models configured. If you configure only one security model, then only the configured model displays in the output.
You can configure SNMP version 3, which is a user-based security model, from the CLI. This model provides support for additional authentication and privacy protocols.
    config
  4. Configure a user, including authentication and privacy protocols.
    system snmp users user <*user-name*> config authentication-protocol { md5 | none | sha | sha256 | sha512 } privacy-protocol { aes | aes192 | aes256| des | none } authentication-password
    This example creates a user that uses MD5 authentication and AES for password authentication:
    appliance-1(config)# system snmp users user jdoe config
      authentication-protocol md5 privacy-protocol aes authentication-password
    After you press Enter, you are prompted to enter the authentication password.
    (<string, min: 8 chars, max: 32 chars>): ********
    After you press Enter, configure the privacy password.
    appliance-1(config-user-v3-user)# config privacy-password
    After you press Enter, you are prompted to enter the privacy password.
    (<string, min: 8 chars, max: 32 chars>): *********
    commit
    end
  7. Verify the user configuration.
    show system snmp users
    appliance-1# show system snmp users
                      AUTHENTICATION  PRIVACY
    NAME     NAME     PROTOCOL        PROTOCOL
    jdoe     jdoe     md5             aes
You can configure SNMP targets with community-based security (SNMPv1/SNMPv2c) from the CLI. These are required to send system-generated traps to an SNMP management system.
    config
  4. Configure a target with community-based security.
    system snmp targets target <*target-name*> config community <*community-name*> security-model { v1 | v2c } { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>
    This example creates a target with community-based security:
    appliance-1(config)# system snmp targets target v2c-target
      config community v2c-comm security-model v2c ipv4 address 192.0.2.24
      port 5001
    commit
    end
  7. Verify the target configuration.
    appliance-1# show system snmp targets
                                              SECURITY
    NAME       NAME       USER     COMMUNITY  MODEL     ADDRESS         PORT  ADDRESS  PORT
    v2c-target v2c-target jdoe     -          -         192.0.2.24      5001  -        -
You can configure SNMP targets with user-based security (SNMPv3) from the CLI. These are required to send system-generated traps to an SNMP management system.
    config
  4. Configure a target with user-based security.
    system snmp targets target <*target-name*> config user <*user-name*> { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>
    This example creates a target with user-based security:
    appliance-1(config)# system snmp targets target v3-target
      config user jdoe ipv4 address 192.0.2.24 port 5001
    commit
    end
                                              SECURITY
    v3-target  v3-target  jdoe     -          -         192.0.2.24      5001  -        -
If you have any concerns about your system operation, you can use the QKView utility to generate a system report to collect configuration and diagnostic information from the system.
The QKView file contains machine-readable (JSON) diagnostic data and combines the data into a single compressed tar.gz format file. You can upload the QKView file to F5 iHealth at ihealth2.f5.com, where you can get help verifying proper operation of the system, understanding and troubleshooting any issues you might be having, and ensuring that the system is operating at its maximum efficiency.
For information about generating a QKView for BIG-IP Next or other tenants, see the documentation on my.f5.com and clouddocs.f5.com.
You can generate a QKView file from the webUI. The report contains diagnostic information, such as configuration data, log files, and platform information.
  2. On the left, click System Monitoring > System Reports.
    The System Reports screen displays. A list of QKView files that were previously generated are shown with any reports that were uploaded to iHealth.
  3. To generate a system report, click Generate QKView
    The Generate QKView drawer form displays these additional options:
    Option
    Description
    Filename
    Specify a name for the file to which QKView file data is written. The default filename is <*system-name*>.qkview.
    Timeout Value
    Specify the time in seconds after which to stop QKView file data collection. The default value is 0, which indicates no timeout.
    Max File Size
    Exclude all files greater than the specified size (in MB). The range is from 2 MB to 1000 MB. The default value for maximum file size is 500 MB.
    Max Core Size
    Exclude core files greater than this size (in MB). The range is from 2 MB to 1000 MB. The default value for maximum core size is 25 MB.
    Exclude Cores
    Specify whether core files should be excluded from the QKView file. The default is to include core files.
Note: The system runs many commands to collect the diagnostic information, so generating the report might affect its performance.
It takes a few minutes for the system to finish creating the report and list it on the screen. The QKView Status changes to `File generated successfully` when it is done.
  1. To upload the report to the F5 iHealth server:
    1. Select the check box next to the QKView to be uploaded.
    2. Click Upload to iHealth.
    3. In the Upload to iHealth drawer form, enter your iHealth credentials.
      Optionally, you can include your F5 Support case number and a brief description.
    To do the upload, the system must have DNS configured, and have Internet access to these services using the HTTPS/443 remote service/port:
    • api.f5.com
    • ihealth-api.f5.com The QKView tar file uploads to iHealth, where you can get help to diagnose the health and proper operation of the system.
  2. To delete a QKView file, select it and click Delete.
You can generate a QKView file from the CLI. The report contains diagnostic information, such as configuration data, log files, and platform information.
  2. List existing QKView files.
    show system diagnostics qkview
  3. Generate a QKView file.
    system diagnostics qkview capture exclude-cores { false | true } filename <*filename*> maxcoresize <*size*> maxfilesize <*size*> timeout <*time*>
    These options are available:
    Option
    Description
    exclude-cores
    filename
    maxcoresize
    maxfilesize
    timeout
    In this example, you generate a QKView file named client-qkview.tar that excludes core files, sets the maximum core size to 500 MB, sets the maximum file size to 500 MB, and sets a timeout value of 0 (zero), which indicates no timeout:
    appliance-1# system diagnostics qkview capture filename client-qkview exclude-cores true maxcoresize 500 maxfilesize 500 timeout 0
    result  Qkview file client-qkview is being collected
    return code 200
  4. Check the status of the QKView generation process.
    system diagnostics qkview status
    appliance-1# system diagnostics qkview status
    result  {"Busy":true,"Percent":12,"Status":"collecting","Message":"Collecting Data","Filename":"client-qkview"}
    resultint 0
  5. Delete a QKView file.
    system diagnostics qkview delete filename <*filename*>
    In this example, you delete a QKView file named “c3-test.tar.canceled” on the local system:
    syscon-1-active # system diagnostics qkview delete filename c3-test.tar.canceled
Before you can upload QKView files to F5 iHealth, you must already have configured the system with iHealth credentials.
You can upload a QKView file from the CLI. The report contains diagnostic information, such as configuration data, log files, and platform information.
    config
  4. Upload a QKView file to iHealth.
    system diagnostics ihealth upload qkview-file <*filename*> description <*qkview-file-description*> service-request-number <*sr-number*>
    In this example, you upload a QKView file named client-qkview.tar to iHealth using configured iHealth credentials:
    appliance-1(config)# system diagnostics ihealth upload qkview-file
      diags/shared/qkview/client-qkview.tar description testing service-request-number C523232
    message HTTP/1.1 202 Accepted
    Date: Mon, 11 Jul 2022 12:09:08 GMT
    Content-Length: 00
Finally, you view the uploaded report on F5 iHealth at ihealth2.f5.com.
You can monitor data and metrics related to the usage, performance, and behavior of the system from the webUI. These statistics are crucial for monitoring, managing, and optimizing the system. You can monitor the following system details:
  • System CPU Usage: Shows the measurement of CPU utilization by the system.
  • System Memory Usage: Shows the measurement of memory utilization by the system.
  • System Disk Usage: Shows the measurement of disk utilization by the system.
To monitor the system’s statistics, follow the steps below:
  2. On the left, click System Monitoring > System Statistics.
    You can now see the following statistics and status of the system.
    • System CPU Usage: Displays the vCPU’s current utilization of the system by default. However, if multiple vCPUs are available, you can monitor the usage for a limited set of vCPUs depending on the screen resolution. You can view the next set of vCPUs by clicking the right chevron icon to go to next page or you can select a specific set of vCPUs from vCPUs dropdown, and change the time series to view the historical data and analyze the vCPU utilization.
    • System Memory Usage: Displays the current memory utilization of the system by default. However, you can change the time series to view the historical data and analyze ‌memory utilization.
    • System Disk Usage: Displays the disk’s current utilization of the system by default. However, if multiple disks are available, you can select a disk, data type, and change the time series to view the historical data and analyze ‌memory utilization
You can monitor data and metrics related to the usage, performance, and behavior of a system from the CLI. These statistics, tenant CPU usage, memory usage, and disk usage, are crucial for monitoring, managing, and optimizing the system.
    config
  3. Show ‌tenants status and statistics.
    tenants tenant <*tenant name*> state <*action*>
    Note: You can get the stats with an average of 10 seconds, 30 seconds, 1 minute, 5 minutes, and 10 minutes.
    This example displays the tenant status and statistics for a BIG-IP tenant running on the rSeries system.
    • For CPU stats:
      appliance-1(config)# tenants tenant cbip state cpu-thread-stats average 1m-avg
      averages {
              unix-seconds 1717588320
              cpu-threads {
                  cpu-thread {
                      thread-index 0
                      busy-percent 1
                  cpu-thread {
                      thread-index 1
                      busy-percent 0
                  cpu-thread {
                      thread-index 2
                      busy-percent 0
                  cpu-thread {
                      thread-index 3
                      busy-percent 4
                  cpu-thread {
                      thread-index 4
                      busy-percent 4
                  cpu-thread {
                      thread-index 5
                      busy-percent 4
                  cpu-thread {
                      thread-index 6
                      busy-percent 4
                  cpu-thread {
                      thread-index 7
                      busy-percent 12
                  cpu-thread {
                      thread-index 8
                      busy-percent 4
                  cpu-thread {
                      thread-index 9
                      busy-percent 1
                  cpu-thread {
                      thread-index 10
                      busy-percent 4
                  cpu-thread {
                      thread-index 11
                      busy-percent 4
                  cpu-thread {
                      thread-index 12
                      busy-percent 4
    • For disk stats:
      appliance-1(config)# tenants tenant cbip state disk-stats average 1m-avg
      averages {
              unix-seconds 1717588260
              used-percent 88
              disk-list {
                  disk {
                      disk-name nvme0n1
                      total-iops 0
                      read-iops 0
                      read-bytes 148
                      write-iops 154
                      write-bytes 1691163
    • For interface stats:
      appliance-1(config)# tenants tenant cbip state interface-stats average 1m-avg
      averages {
              unix-seconds 1717588380
              interface-list {
                  interface {
                      interface-name 1.0
                      ifc-bytes-in 1466
                      ifc-bytes-out 0
                      ifc-packets-in 0
                      ifc-packets-out 0
                  interface {
                      interface-name 2.0
                      ifc-bytes-in 135
                      ifc-bytes-out 0
                      ifc-packets-in 0
                      ifc-packets-out 0
    • For memory stats:
      appliance-1(config)# tenants tenant cbip state memory-stats average 1m-avg
      averages {
              unix-seconds 1717588440
              available 8493508881
              free 1060426615
              used-percent 93
              platform-total 16107667456
              platform-used 8114811835
OpenTelemetry streamlines observability in distributed systems through standardized APIs, libraries, and tools for collecting telemetry data, including traces, metrics, and logs.
F5OS OpenTelemetry enables the efficient collection of streaming metrics and logs in a structured format from the F5OS product to display in your observability platform. All the metrics and logs will be exported through a gRPC connection. The F5OS supports gRPC endpoints and each OpenTelemetry Line Protocol (OTLP) endpoint is provided with the ability to toggle instrument based filtering.
Telemetry subsystem within the F5OS platform layer generates common attributes and different metrics to display in your observability platform.
An instrument is an area of metrics, which contain multiple metrics and can be enabled selectively. F5OS Resource includes instruments.
Summarizes the metrics that are associated with each tenant as they enters and exits the platform hardware at the DMA level.
The following tenant metrics are currently reported by the BIG-IP tenant into the F5OS platform layer. The metrics visible at the platform layer are only a limited subset of the total number of metrics available to the tenant. You can view the full tenant metrics by using the BIG-IP metric reporting capability.
F5OS OpenTelemetry exporter will only report the metrics that are associated with the Docker containers managed by the platform layer. For more information about the docker container metrics, see Docker stats documentation.
The platform hardware sensors represent physical sensors associated with the hardware which measure: temperature, current, power, voltage, RPM and percent humidity.
The metric schema is heavily dependent upon the internal representation of the tmstat tables within F5OS.
Instument name Description
all All the logs and metrics produced by the F5OS platform layer except docker container metrics
logs All the F5OS logs file
platform-log All the F5OS platform logs file
event-log All the F5OS ConfD event log
metrics All the F5OS metrics except docker container metrics
platform Standard platform metrics such as memory, disk, CPU, and interface
hardware The low-level platform hardware sensors
optics The front-panel optic DDM metrics
tenant Tenant-initiated metrics such as memory, disk, CPU, and interface
datapath F5OS data-path metrics such as those generated by the FPGA and DMA
tmstat F5OS tmstat tables exported as metrics
container Docker container metrics for F5OS services
Note:
  • Support for the intrument “tenant” is provided only for BIG-IP tenants.
  • The intrument “Datapath” is applicable for F5 r5000/r10000/12000 platforms only.
This image provides a representation how the F5OS Resource includes instruments with multiple metrics:
The table lists the set of attributes that can be applied to all metrics produced by the platform.
The scope indicates which product the attribute applies to:
  • F5 - Applies to all metrics produced by F5
  • F5OS - Applies to all metrics produced by the F5OS product
Name
Value
Type
Scope
Description
host.name
<*name of host*>
string
F5
The host-name for F5OS, derived from ConfD system hostname.
f5.system.id
<*instance ID*>
string
F5
A unique instance ID per product.
f5.product.version
<*version string*>
string
F5
A version string, which represents the version of the product.
f5.product.name
<*product\_name*>
string
F5
The high-level F5 product generating the metric/log: - F5OS
  • BIGIP-Next
  • SPK
  • CNF
f5.product.type
<*v6h-hi*>
string
F5OS
The platform type.
f5.platform.serial_number
<*platform\_serial\_no*>
string
F5OS
Serial number of an appliance, blade, or controller.
f5.platform.role
<*platform\_role*>
string
F5OS
The appliance is straight-forward. However, for chassis products, the telemetry data can originate from multiple places. The role can help identify a location. - Blade - The data originated from a blade within a partition
  • Partition - The data originated from a partition-level service
  • Controller - The data originated from a system controller
f5.platform.pid
C137
string
F5OS
The platform ID
f5.platform.name
<*platform\_name*>
string
F5OS
The Platform Name - rSeries - The appliance products
  • VELOS - The chassis products
instrument.name
<*name*>
string
F5OS
F5OS Instrument name associated with the metric.
f5.data_type
<*f5os-analytics*>
string
F5
The attribute used by BIG-IP Central Manager to help direct F5OS specific metrics
f5.tenant.name
<*f5os\_tenant\_name*>
string
F5OS
The deployed tenant name
The following attributes apply for the tenant based metrics.
Name
Value
Type
Description
f5.tenant.name
<*tenant name*>
string
The name of the tenant which acts as a tenant ID
f5.tenant.image
<*image version*>
string
The tenant image version
f5.tenant.type
  • BIG-IP
  • BIG-IP Next
string
The tenant type name
Note: These metrics are relevant to Platforms.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.interface.packets
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
Counter
int64
direction="transmit"
{packets}
f5.interface.bytes
Counter
int64
direction="receive"
Bytes
f5.interface.bytes
Counter
int64
Bytes
f5.interface.errors
Counter
int64
direction="receive"
{packets}
f5.interface.errors
Counter
int64
{packets}
f5os.interface.dropped
Counter
int64
direction="receive"
{packets}
Counter
int64
{packets}
f5.interface.broadcast
Counter
int64
direction="receive"
{packets}
f5os.interface.broadcast
Counter
int64
{packets}
f5os.interface.multicast
Counter
int64
direction="receive"
{packets}
f5.interface.multicast
Counter
int64
{packets}
f5os.interface.ethernet
Counter
int64
name="1.0"
state=<field>
{packets}
Reports the front-panel Optic DDM metrics.
Common Attributes include:
  • The F5OS port group name associated with the Optic
port.group=<*string*>
  • The front-panel port number
port.name="1.0"..
  • For metrics which are per-channel, identifies the individual channel number
channel=1..N
  • An indication of transmit or receive direction
direction="transmit" | "receive"
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.optic.temperature
Gauge
float
port.group=<string>
port.name="1.0"
C
f5.optic.voltage
Gauge
float
port.group=<string>
port.name="1.0"
V
f5.optic.power
Gauge
float
port.group=<string>
port.name="1.0"
channel=1..N
dbm
f5.optic.tx-bias
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
f5.optic.los
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
f5.optic.tx-fault
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
The schema of the CPU metrics is based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.cpu.time
Counter
int64
cpu=cpu0..cpuN
thread=0...N
state=<field>
Seconds
system.cpu.utilization
Gauge
float64
pu=cpu0...cpuN
thread=0..N
state=<field>
{percent}
The Disk IO Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.disk.io_time
Counter
float64
device=<name>
direction=total
Seconds
system.disk.operations
Counter
int64
device=<name>
direction=read
{operations}
Counter
int64
device=<name>
direction=write
{operations}
system.disk.io
Counter
int64
device=<name>
direction=read
Bytes
system.disk.io
Counter
int64
device=<name>
direction=write
Bytes
system.disk.merged
Counter
int64
device=<name>
direction=read
{operations}
system.disk.merged
Counter
int64
device=<name>
direction=write
{operations}
system.disk.operation_time
Counter
float64
device=<name>
direction=read
Seconds
Counter
float64
device=<name>
direction=write
Seconds
system.disk.usage
Counter
float64
device=<name>
Bytes
The Memory Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.memory.usage
Counter
int64
state="<*field*>"
Bytes
system.memory.utillization
Gauge
float64
state=used
{percent}
system.memory.utilization
Gauge
float64
state=platform
{percent}
Gauge
float64
state=available
{percent}
The File system Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.filesystem.usage
Gauge
int64
state = "free" || "total" || "used" system.device = </*dev/mapper/partition\_image-export\_chassis*> system.filesystem.mountpoint = <*/var/export/chassis*> system.filesystem.type = <*ext4*>
By
system.filesystem.utilization
Gauge
float64
state =used system.device = <*/dev/mapper/partition\_image-export\_chassis*> system.filesystem.mountpoint = <*/var/export/chassis*> system.filesystem.type = <*ext4*>
Percent
The Uptime Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.uptime
Counter
int64
S
The Raid Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Note: Applicable for F5 r10000/12000 platforms with only two hard disks.
Metric Name
Metric Type
Value Type
Attributes
Unit
system.raid.blocks
Gauge
int64
state= "blocksTotal" || "blocks-synced"
system.raid.devices = <*nvme0n1p1,nvme1n1p1*>
system.raid.name = <*md124*>
Blocks
system.raid.state
Gauge
int64
state = "disks-total" || "disks-active" || "disks-failed" || "disks-down" || "disks-spare"
Count
system.raid.status
Gauge
int64
state = “active” || “blocks-synced”
{status}
system.raid.sync.estimation
Gauge
float64
Seconds
system.raid.sync.percent
Gauge
float64
Percent
system.raid.sync.speed
Gauge
float64
KbPerSecInterface Counter Metrics
Note: Applicable for F5 r5000/r10000/12000 platforms only.
Note: This metric is the sum of all internal tenant interfaces and independent of the F5 platform front-panel interface.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.datapath.packets
Counter
int
direction="transmit | receive"
f5.datapath.area="dma"
{packet}
f5.datapath.bytes
Counter
int
By
This table lists the attributes that are associated with the tenant-based metrics.
Metric Name Metric Type Value Type Attributes Unit
f5.tenant.cpu.utilization Gauge float64 state="<field-name>" cpu=cpuN Percent
f5.tenant.cpu.time Counter int64 state="<field-name>" cpu=cpuN s
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tenant.memory.utilization
Gauge
float64
state="<*field*>"
Percent
f5.tenant.memory.usage
Gauge
int64
state="<*field*>"
Bytes
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tenant.disk.operations
Counter
int64
device=<*name*>
direction=total
operation
Counter
int64
device=<*name*>
direction=read
operation
Counter
int64
device=<*name*>
direction=write
operation
f5.tenant.disk.io
Counter
int64
device=<*name*>
direction=read
Bytes
f5.tenant.disk.io
Counter
int64
device=<*name*>
direction=write
Bytes
f5.tenant.disk.merged
Counter
int64
device=<*name*>
direction=read
operation
Counter
int64
device=<*name*>
direction=write
operation
f5.tenant.disk.operation_time
Counter
float64
device=<*name*>
direction=read
s
Counter
float64
device=<*name*>
direction=write
s
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tenant.interface.packets
Counter
float64
interface.name="<interface-name>"
direction="receive"
packets
Counter
int64
packets
f5.tenant.interface.bytes
Counter
int64
direction="receive"
Bytes
Counter
int64
Bytes
Attributes
Metric value type
Description
container.name
string
The name of the container
container.image.name
string
The container image name
Metric Name
Metric Type
Value Type
Attributes
Unit
container.cpu.usage
Gauge
float
ns
container.memory.<*field-name*>
Gauge
float
By
container.memory.usage <*field-name*>
Gauge
float
By
container.memory.percent
Gauge
float
{percent}
container.blockio.io_service_bytes_recursive
Gauge
float
operation="read" | "write"
By
container.network.io.usage.<*field-name*>
Gauge
float
interface=<name>
By | {percent}
container.cpu.percent
Gauge
float
cpu=<name>
{percent}
  • f5os.sensor.name=<sensor name>
    Eamples:
    • Temperature:
      • Inlet
      • Outlet
      • Central
    • Voltage:
      • 12V
      • 3.3V BCM
    • Current:
      • 12V Main
      • Current In
    • Power:
      • Controller Power
      • Total Power Supply Unit (PSU) Power In
      • Total Power Supply Unit (PSU) Power Out
  • f5os.sensor.source=<component name>
    Eamples:
    • psu-[1..N]
    • fantray-[1..N]
    • psu-controller-[1..N]
    • blade-[1..N]
    • controller-[1..2]
    • platform
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.sensor.temperature
Gauge
float64
sensor.name="<name of sensor>"
sensor.source="?<component name>"
C
f5.sensor.voltage
Gauge
float64
V
f5.sensor.current
Gauge
float64
A
f5.sensor.power
Gauge
float64
W
f5.sensor.humidity
Gauge
float64
{percent}
f5.sensor.fan.speed
Gauge
float64
RPM
Note: When you select instrument type as “all” and/or “metrics”, the instrument type “tmstat” is set to off and cannot be selected. You have to manualy enable the instrument “tmstat”. Using this instrument is more tailored to internal ‌F5 use cases, such as deep diagnostics.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tmstat.<*table*>
Gauge
int
f5.tmstat.column=<*name*>
You can configure an exporter from the webUI.
  1. Log in to the webUI using an account with admin access.
  2. On the left, clickSystem Monitoring > Telemetry.
    The Telemetry screen displays.
  3. Under the Telemetry exporters area, click Add.
  4. Enter Name of the Exporter (up to 20 characters).
    The first character in the name cannot be a number. After that, only lowercase alphanumeric characters and hyphens are allowed.
  5. For Endpoint
    • For IP Address, enter the IPv4 address, IPv6 address, or Fully Qualified Domain Name (FQDN) for an exporter.
    • For Port, enter the port number of the Server.
  6. For Enable, select True if you want to enable and send the telemetry data to the exporter or False to disable it.
  7. For Instruments, select one or more instruments for an exporter.
    Option Description
    logs Reports all F5OS logs file through the OpenTelemetry ’log’ API
    platform-log Exports the F5OS platform log through the OpenTelemetry ’log’ API
    event-log Exports the F5OS confd event log through the OpenTelemetry ’log’ API
    platform F5OS platform metrics such as memory, disk, cpu, interface, file system, and RAID stats
    hardware F5OS hardware sensors such as voltage, current, temperature, power, fan-speeds
    optics F5OS front-panel Optic DDM metrics
    tenant Low level tenant reported metrics such as memory, disk, cpu, interface stats
    container F5OS Per-Container metrics such as cpu, block-io, network, memory
  8. For Compression, select the compression type. By default gzip will be selected.
  9. For Attributes, specify the attributes for the exporter.
    Click on Add to add another attribute. Select an attribute and click Delete button to delete it.
    Attributes are reference data which can be associated with the exporter. Attributes can be specified in the key & value format.
  10. For Secure input, select True to enable and configure the Transport Layer Security (TLS) to secure the connections. The default option is False.
    Note: Before you can enable TLS encryption, you must configure a key and certificate on the system.
  11. You can secure connections by using one of these methods:
    • Server Authentication only:
      • For TLS CA Certificate, paste the contents of the certificate (self-signed or from a CA) for server TLS authentication.
    • Both Server and Client Authentication
      1. For TLS CA Certificate, paste the contents of the certificate (self-signed or from a CA) for server TLS authentication.
      2. In the TLS Certificate field, paste the text of the local certificate for client TLS authentication.
      3. In the TLS Key field, paste the text of the private key for client TLS authentication.
  12. For Reload Interval, specify the duration to reload the certificate within the specified timeframe.
    Note: You can only specify the duration value in nanoseconds (ns), microseconds (us (or µs)), milliseconds (ms), seconds, minutes, and hours.
  13. Click Save.
You can delete an exporter from the webUI.
  2. On the left, click System Monitoring > Telemetry.
    The Telemetry screen displays the existing exporter and associated details.
  3. To delete an exporter, in the Telemetry exporters area, select the exporter from the list and then click Delete.
Attributes are reference data which can be associated with the exporter. Attributes can be specified in the key:value format. Spaces must be included between each entry. You can add attributes to all the configured exporters from the webUI.
  3. Under Telemetry Attributes, click on Add Attributes.
    Click on Add to add another attribute. Select an attribute and click Delete to delete it.
  4. Click on Save
Before configuring an exporter, you can display supported instruments from the CLI.
  1. Connect using SSH to the management IP address.
  2. Log in to the command line interface (CLI) of the system using an account with admin access.
    When you log in to the system, you are in user (operational) mode.
  3. Show the total and available instruments:
    show system telemetry instruments
    This example displays the available instruments:
    appliance-1# show system telemetry instruments
    NAME           DESCRIPTION
    all           Report all logs and metrics produced by the F5OS platform layer
    logs          Report all F5OS logs file through the OpenTelemetry 'log' API
    platform-log  Export the F5OS platform log through the OpenTelemetry 'log' API
    event-log     Export the F5OS confd event log through the OpenTelemetry 'log' API
    metrics       Report all F5OS metrics through the OpenTelemetry 'metric' API
    platform      F5OS platform metrics such as: memory, disk, cpu, interface, file system, and RAID stats
    hardware      F5OS hardware sensors such as: voltage, current, temperature, power, fan-speeds
    tenant        Low level tenant reported metrics such as: memory, disk, cpu, interface stats
    container     F5OS Per-Container metrics such as: cpu, block-io, network, memory
An exporter defines an OpenTelemetry gRPC endpoint to which the F5OS Platform will push metrics/logs.
Note: You can enable ‌Transport Layer Security (TLS) and secure the connections for telemetry streaming. Before you can enable TLS encryption, you must generate a private key and self-signed certificate.
You can configure the exporter from the CLI.
    config
  4. Configure the exporter.
    You must specify the IP address or DNS name of the server and the port number of the server on which OpenTelemetry (OTEL) is running
    system telemetry exporters exporter <*server name*> config endpoint address <*address*> port <*port number*> instruments <*instrument name*> tls sercure { false | true }
    A summary similar to this example displays:
    appliance-1(config)# system telemetry exporters exporter test1 config endpoint address 10.144.74.171 port 4317 instruments [all] tls secure true
    Possible completions:
      ca-certificate    Specifies the CA Certificate content.
      certificate       Specifies the PEM-encoded telemetry client certificate (Configure for mTLS).
      key               Specifies the PEM-encoded telemetry client private key (Configure for mTLS)
      reload-interval   Specifies reload-interval in duration strings.
      <cr>
  5. You can secure the connections by using one of these methods:
    • To authenticate the server, add the certificate:
      system telemetry exporters exporter <*server name*> config ca-certificate
      Press Enter to enable multi-line mode and then paste the contents. Press Ctrl-D to exit multi-line mode.
      system telemetry exporters exporter test1 config ca-certificate
      (<string>):
      [Multiline mode, exit with ctrl-D.]
      appliance-1(config)# system telemetry exporters exporter test1 config endpoint address 10.144.74.171 port 4317 instruments [ all ] tls secure true ca-certificate
      (<string, min: 1 chars>):
      > -----BEGIN CERTIFICATE-----
      > MIIFmzCCA4OgAwIBAgIJAIQRlRZvPsmXMA0GCSqGSIb3DQEBCwUAMGQxCzAJBgNV
      > BAYTAlVTMRMwEQYDVQQIDApXYXNoaW5ndG9uMRAwDgYDVQQHDAdTZWF0dGxlMRQw
      > EgYDVQQKDAtGNSBOZXR3b3JrczELMAkGA1UECwwCUEQxCzAJBgNVBAMMAmNhMB4X
      > DTIzMTExMzA3NTUzNFoXDTI0MTExMjA3NTUzNFowZDELMAkGA1UEBhMCVVMxEzAR
      > BgNVBAgMCldhc2hpbmd0b24xEDAOBgNVBAcMB1NlYXR0bGUxFDASBgNVBAoMC0Y1
      > IE5ldHdvcmtzMQswCQYDVQQLDAJQRDELMAkGA1UEAwwCY2EwggIiMA0GCSqGSIb3
      > DQEBAQUAA4ICDwAwggIKAoICAQC4NiPFaDvwfajK1pLaisHrWFnji0GAiM4Dyn8C
      > ndJW5AptRr8xOPfESMvhkMq1MTp9lQCDNKVgfJuJe3xNWugVFvAMPMuTeMnjv+Xm
      > /9jzYFBCJ2ddof/8Uwd6/0X2nmAwfO+gGZZv6rviwtxt6YCPuxUWM48Mqdq5BjSQ
      > 5eSepXtMXhtubXr8VCjh1aFxAqnadOm8pykumcTUq7vnPElv/4DG5M6WL+vCpDes
      > XEjqhAp3wyOzCglew026xUBYvy3WAIxHVttd0VWP+7KNl2QlYXpJewZcUpHM917i
      > Uoui3+h66w1YrfoZTBBcdL7Lnb8v78Jg/6tBAjEcxIXRPQbM+qm1l0e6rCy0NMKP
      > i+v0wq9EUOfc4z+nMtF+ggyZlHUo6lJLr3+ZMtkBticvNpRpOZ2XjxsvjjoymZ0a
      > 7QBDeSbYtOam+UT2h1UiN4RJsQbtyUAgz9zMTyc82B2TonztVm12MrW2GuDD2+Nv
      > KdCi5trmgpmWagSFsi8dWK1qFpXUB34+83geAhp5sz5ngsQtiAWHcYbL67M86fKs
      > L9GP91p8LZm09LVzekwxbe6Bq/FM7SCHVMcK+lCLA3hTdX3PCuvjkjrXOH7zy8M7
      > R7RCmPj5hdPXxTYomGkwY1IW8JkurwukYvnfzn6pwNkRX6/1B5GZHMIi98nkA3lJ
      > /eUtKQIDAQABo1AwTjAdBgNVHQ4EFgQUTYPD7uZ2NLCxdyMdxeVQnTONkl4wHwYD
      > VR0jBBgwFoAUTYPD7uZ2NLCxdyMdxeVQnTONkl4wDAYDVR0TBAUwAwEB/zANBgkq
      > hkiG9w0BAQsFAAOCAgEARpehpSFWyKw0sPeZYk8LsiTiMhS5BX+WBIaZzGrQXW4p
      > lU9rOBtunhzjbH5Vf6bzJVL5Zi7kFIUa+8RrnY0+0+CVxRiFE3k1rOFZ7YsS1ILl
      > vQ7tVBTCRHJ6VAThlVlagYntfEI+bxTJQ3nnRzRe+znh5uqANEChZUoXX2lmDmhU
      > D+2lyzuZ9t6C8xcB2jfe0yUJeUQAdQh1x4k5Y2ssjnS4tLOa2Ly3xj3WudFHoA2D
      > kwu9myRKkJ1ruCO6DSRxi1BnfKISUOQtZ1DWaNpN/2fEzqtiW7klO9G2gwL6O/8J
      > 9cYn4HRTbA9DKITzPYs854TJnaOimn7US5hZkb1n9uy1c9cN1XfNxenHziEdG1BM
      > U7EsAmHYtf7k8N3XisKTfLEZ6AeAsqOp16Fi/ecp467DZtMnY4NXcadnj+IpIPeh
      > k6VkkayjrEZgWfcVHZ8L1vpVNTLnRuc0a3V4ioFoOGAKvoBVruQZWt0Sgtg/V/UH
      > i/otMqWYV5q366R4St55ZYfu8mdqhZljSU3Zrneco7DqTttFbWeWa3SaWhvP96VF
      > 4FTrgLyq4D6OlURqWMRbh98TxAzSbYw6cWoevRUpae5Eo0ST/c6dqjTlbq1YHr1H
      > MAhq2UPmh3/Uuc3a0dUWQ8gas0SEPFOHbnY5a/ae2cSdUV5uLR/dNsRWflZQaj4=
      > -----END CERTIFICATE-----
    • To authenticate the server and client, add the certificates and key.
      system telemetry exporters exporter <*server name*> config tls certificate
      system telemetry exporters exporter server1 config tls certificate (<string>): [Multiline mode, exit with ctrl-D.] > ... appliance-1(config-exporter-test)# config tls key (<string>): [Multiline mode, exit with ctrl-D.] > appliance-1(config-exporter-test)# config tls certificate (<string>): [Multiline mode, exit with ctrl-D.] >
      A summary to this example displays:
      appliance-1(config)# system telemetry exporters exporter test2 config endpoint address 10.144.74.171 port 4317 instruments [ all ] tls secure true ca-certificate
      (<AES encrypted string>):
      (<string>):
      > MIIFajCCA1KgAwIBAgIJAN5Vgnsykm2mMA0GCSqGSIb3DQEBCwUAMGQxCzAJBgNV
      > DTIzMTExMzEwNTgyOFoXDTI0MTExMjEwNTgyOFowcDELMAkGA1UEBhMCVVMxEzAR
      > IE5ldHdvcmtzMQswCQYDVQQLDAJQRDEXMBUGA1UEAwwOMTAuMjM4LjE1Ny4yMzcw
      > ggIiMA0GCSqGSIb3DQEBAQUAA4ICDwAwggIKAoICAQCiQiZZbGgioRHXDOw6slU8
      > 9lzikxOFmkpcr0EonT3f1o+n46oNU4PmZ7saTDp3dffU3gflLIh0eseUCJosFd8H
      > iF/OZdq38YPDCmAI4GD341Gs959qIpRYiuXzv5+11H7bUewS4Uj0ZP7ByuV+PFYS
      > +mHjRjcDXDV2kNVPwiEz/wxsuX5QP2rLH/Kepknj+ldkE9/khy2/aaWtmlVy5VaO
      > L1PRUAJh1lbT95GGpAYcCdbzay17GV0FN7uSl2/pMv74ygIvQNcs4av4l7bAvVdF
      > sGNJm/AdvruOhw2y87KKPGjgrS072c8aYkri/jJh6IW1DJ9HS+4vU7RtB9JKcbw5
      > O01gZXKWRal5VUHRg/BBiYGwRqJg2fmcKzt9YHqOTzFPvudc5S8ij4CgVmXH5lHI
      > bPQjc8dn8CE0upwDAIUKOS2tPz5PcgBCqbCG1d5NtCSbZSa8udDCQmRXZ0mwPdn9
      > wLNymUBAnZvFuzaU0Q99P1WwPK4wJrCHUdF+ETK3VY+U4pwYeyNLt82cVSeuAZD+
      > 4hBXNPHDKrsylhRn5QqhORfs+XNaUjp94zs4Uth2dxCREG3yb/AsW3q+ddjfCk51
      > 2kSy73dUudtxbErbivHSuuvmOm4flzBTgQF8C8aP1P9AEj60lyNOPY72dRMdWf2y
      > hpfogHMaqkHRNxcazhZ7GQIDAQABoxMwETAPBgNVHREECDAGhwQK7p3tMA0GCSqG
      > SIb3DQEBCwUAA4ICAQAb85rbxzosNnG+OucXVD3Cxt0VKH816ZnEvCtz9DVZfMqj
      > IpLOmIpFr5MJp4bz3459BRRsJf/TvhQaofPoxUCf1mm8Vf889mJFBFQ4eUmqpv35
      > FDZfe8cNmTsJwebHr7ubSxytJR+IMwAwirbuW656oSMX3r0ERNYxdC2VYf7rWG2a
      > EiF2zMlTAsyjfToMIIpWncata3tGxJHXMDYrl8Y4tXl20PlRR3x/2QBj/Ghud9+E
      > JYIFsdFeIMDiPyu2S3saYZS5dwb+0Fmn/0qgzut3eZuYn0TiTpPj9i0c4Zmza0aK
      > uHjI7N/lzkReAfh4KT/o3uqxLMn+6eUwc2ai8EfQ7Jw+geL0N4JDrhW7Z9Qsp+yS
      > 9Gl3qGNAyU+7kZqixcLde2+aLFZoq169Ayo7IXx/wFSBW/Lif0ZoMLKZ7OVOeawb
      > Ct1tnQ3bQZwmWa7MFdF3aaATXBy6jKfcEH0vTIa2FiCxhEbynMzw5zIcFX1GLL4l
      > SBzPKkNz7sA6EzuKJNL8LwjOndAKHGAB2EkGy4/3PKmM5yF//shRneXrJx1xd1nI
      > 9ipFxZ1e6YwxJ4K6tIiZMineKK/csA7z6tLaImQ/ldFz0S0Qws+1csgfp9VIrxtG
      > ZwIVHO/QCZe7gB6XQESbBpW6M8eKj5zqk5ZTMAGihtE7nDEe3ZXWvzV0Vr0MPQ==
  6. Commit the configuration changes.
    commit
After you configure the exporter, you can display the state of the exporter from the CLI.
  1. Log in to the command line interface (CLI) of the system using an account with admin access.
  2. Display the state of a specific exporter
    show system telemetry exporters exporter <*server name*>
    When you specify an exporter, a summary to this example displays:
    appliance-1# show system telemetry exporters exporter test-tls
    state enabled
    state endpoint address 10.144.74.171
    state endpoint port 4317
    state instruments [ all ]
    state tls secure true
    state tls ca-certificate "
    state options compression gzip
You can modify the configuration of an exporter from the CLI.
    config
    The CLI prompt changes to include (config).
  4. You can use the following commands to modify the exporter configuration:
    • Disable the exporter
      system telemetry exporters exporter <*server name*> config disabled
      appliance-1(config)# system telemetry exporters exporter server1 config disabled
    • Modify option retry-enabled
      system telemetry exporters exporter <*server name*> config retry-enabled
      appliance-1(config-exporter-server1)# system telemetry exporters exporter server1 config options retry-enabled
        false  true
      appliance-1(config)# system telemetry exporters exporter server1 config options retry-enabled false
    • Modify option timeout
      system telemetry exporters exporter server1 config options timeout <*new value*>
      appliance-1(config)# system telemetry exporters exporter server1 config options timeout 10
    • Modify option compression
      system telemetry exporters exporter server1 config options compression <*new value*>
      appliance-1(config)# system telemetry exporters exporter server1 config options compression zstd
    commit
    end
  7. You can verify the state of the exporter. see Display exporter state from the CLI.
You can add, modify, or delete the instruments that are configured for an exporter from the CLI.
    config
    • Add a new instrument
      system telemetry exporters exporter <*server name*> config instruments <*instrument name*>
      appliance-1(config)# system telemetry exporters exporter server1 config instruments hardware
    • Modify the instrument
      system telemetry exporters exporter <*server name*> config instruments [<*instrument name*>]
      appliance-1(config)# system telemetry exporters exporter server1 config instruments [ optics ]
    • Delete the instrument
      no system telemetry exporters exporter <*server name*> config instruments <*instrument name*>
      appliance-1(config)# no system telemetry exporters exporter server1 config instruments platform
    commit
    end
You can add attributes to all the configured exporters from the CLI
  2. Change to config mode.
    config
  3. You can add attributes to all the configures exporters:
    system telemetry attributes attribute <*attribute name*> <*attribute value*>
    appliance-1(config)# system telemetry attributes attribute test.key config key test.key value test.vale
    appliance-1(config-attribute-test.key)# commit
    Commit complete.
    appliance-1(config-attribute-test.key)# exit
    appliance-1(config)# exit
    appliance-1# show system telemetry attributes
    KEY       KEY       VALUE
    test.key  test.key  test.vale
    commit
    config
  4. Delete the exporter:
    A summary similar to this example displays:appliance-1(config)# no system telemetry exporters exporter server1
    commit
    end