Updated Date: 07/07/2026
System Settings
You can access system settings in the webUI.
You can view active system alarms and events in the webUI and CLI.
The Alarms & Events screen lists alert information for system components (such as PSU, firmware, and LCD) that have currently crossed a performance or health threshold. Use this screen to identify the specific component that is affected.
Log in to the webUI using an account with admin access.
On the left, click SYSTEM SETTINGS > Alarm & Events.
Choose from one of these actions:
- To refresh the alarms or events list, click the Refresh icon on the right of the screen.
- To display events result by time preference, click the down arrow next to the Refresh icon and select a value from the list. The default value is one hour. For example, select five minutes to display any event that occurred in the last five minutes.
- To display events by severity, select a value from the Severity list. The default value is WARNING.
Option Description Emergency Emergency system panic messages Alert Serious errors that require administrator intervention Critical Critical errors, including hardware and file system failures Error Non-critical, but possibly important, error messages Warning Warning messages that should be logged and reviewed Notice Messages that contain useful information, but might be ignored Informational Messages that contain useful information, but might be ignored Debug Detailed messages used for troubleshooting
You can view information about active system alarm conditions from the CLI.
Connect using SSH to the management IP address.
Log in to the command line interface (CLI) of the system using an account with admin access.
When you log in to the system, you are in user (operational) mode.
View a list of active system alarm conditions.
show system alarms | tabThis example shows a power supply unit (PSU) redundancy fault:
appliance-1# show system alarms | tab ID RESOURCE SEVERITY TEXT TIME CREATED –––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––- 65793 psu-1 ERROR PSU fault detected 2022-06-01-11:11:11.999825828 UTC
You can access management interface settings in the webUI.
You can view or change settings for the management interface from the webUI.
On the left, click SYSTEM SETTINGS > Management Interface.
For DHCP, select either Enabled or Disabled.
For Address, select either IPv4, IPv6, or IPv4 & IPv6.
Additional fields display, depending on which address type you selected.
Under IPv4 and IPv6, you can configure one or more management IP addresses for the system:
For IP Address, type an IPv4 or IPv6 address.
For Prefix Length, specify a number from 1-32.
For Gateway, type the gateway IP address.
Under Interface Settings, you can configure the management port:
For State, select either Enabled or Disabled.
For Auto-negotiation, select either Enabled or Disabled.
If you enable auto-negotiation, port speed and duplex mode are set automatically.
For Port Speed, select one of these options: SPEED_1GB, SPEED_10MB, or SPEED_100MB.
For Duplex Mode, select FULL or HALF.
Click Save.
You can configure the management port from the CLI.
Connect to the system using a management console or console server.
Note: The default baud rate and serial port configuration is 19200/8-N-1.
Change to config mode.
configThe CLI prompt changes to include
(config). -
Enable and set general properties for the management port.
interfaces interface mgmt config { disabled | enabled } description <*interface-description*>In this example, you enable the management port, add a description, and set the type:
appliance-1(config)# interfaces interface mgmt config enabled description "Mgmt Interface" -
Exit to the top level of the configuration hierarchy.
top -
Configure Ethernet properties for the management port.
interfaces interface mgmt config auto-negotiate { false | true } duplex-mode { FULL | HALF } port-speed { SPEED\_1GB | SPEED\_10MB | SPEED\_100MB }In this example, you enable the management port, add a description, and set the type:
appliance-1(config)# interfaces interface mgmt config auto-negotiate true duplex-mode FULL port-speed SPEED_1GB -
Commit the configuration changes.
commit -
Return to user (operational) mode.
end -
Verify that the management interface is configured.
show interfaces interface mgmtA summary similar to this example displays:
appliance-1# show interfaces interface mgmt interfaces interface mgmt state name mgmt state type ethernetCsmacd state enabled true state oper-status UP ethernet state auto-negotiate true ethernet state duplex-mode FULL ethernet state port-speed SPEED_1GB ethernet state hw-mac-address 00:12:a1:34:56:78 ethernet state negotiated-duplex-mode FULL ethernet state negotiated-port-speed SPEED_1GB
An allow list enables you to add either an IPv4 or IPv6 address as an accepted source that can access the system.
When the IP address is configured and saved to your allow list, only traffic coming from that IP address and port is accepted by the system’s management interface. You can also edit or delete entries in the allow list after you have configured them.
You can add, configure, or delete an IP address in the system allow list from the webUI.
On the left, click SYSTEM SETTINGS > Allow List.
The Allow List displays.
Add an IP address to the allow list:
Click Add.
For Name, enter a descriptive name for the IP address.
For IPv4/IPv6, select IPv4 or IPv6.
For Address, enter the IP address to be added to the allow list.
For Prefix Length, enter or select the prefix length.
The prefix length values must be between 1 and 32 for IPv4 and between 1 and 128 for IPv6.
For Port, select a port number for the IP address.
Available options are:
- 443 (HTTPS): Allow only HTTP with SSL traffic on this IP address.
- 80 (HTTP): Allow only HTTP traffic on this IP address.
- 8888 (RESTCONF): Allow only RESTCONF traffic on this IP address.
- 161 (SNMP): Allow only SNMP traffic on this IP address.
- 7001 (VCONSOLE): Allow only VCONSOLE traffic on this IP address.
- 22 (SSH): Allow only SSH traffic on this IP address.
Edit the allow list:
Select the IP address that you want to edit from the allow list.
The IP address details display. You cannot edit the designated name, but you can change all other fields.
Click Save & Close.
To delete an IP address, select it and click Delete.
When you are asked to confirm that you want to delete the IP address from the allow list, click OK.
You can configure your system to allow only specific IP addresses, ports, or a netmask from the CLI.
(config). -
Configure the system to allow traffic only from specified IP addresses.
system allowed-ips allowed-ip <*allowlist-profile-name*> config [ ipv4 | ipv6 ] address <*ip-address*> port <*port-number*>prefix-length <*subnet-prefix-length*>Important: This is applicable only for ports 161 (SNMP), 8888 (RESTCONF), 443 (HTTPS), 80 (HTTP), 7001 (VCONSOLE), and 22 (SSH).
This example adds a specified IPv4 address to the system allow list:
appliance-1(config)# system allowed-ips allowed-ip test config ipv4 address 192.0.2.33 port 161 prefix-length 32This example adds a netmask to the system allow list:
appliance-1(config)# system allowed-ips allowed-ip test config ipv4 address 192.0.2.0 port 161 prefix-length 24This example restricts access to the management interface (SSH) to only the specified IP address:
appliance-1(config)# system allowed-ips allowed-ip test config ipv4 address 192.0.2.33 port 22 prefix-length 32 -
commit
The Software Management screen on the webUI includes options for uploading, importing and updating Base OS software for the system.
You can manage software images from the webUI.
On the left, click SYSTEM SETTINGS > Software Management.
To import a Base OS image:
Click Import.
A popup opens.
For URL, enter the URL of the remote image server.
F5 recommends that the remote host be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate. You can opt to select the Ignore Certificate Warnings check box if you want to skip the certificate check.
For Username, type the user name for an account on the remote image server, if required.
For Password, type the password for the account, if required.
Select Ignore Certificate Warnings to skip the certificate check.
Click Add Image.
Note: Depending on the image file size and network availability, the import might take a few minutes. When the import is successful, the software image is listed in the webUI.
To upload a Base OS image that you have downloaded to your local workstation:
Click Upload.
Navigate to the image file and select it.
Click Open.
To delete a Base OS image, select the image and click Delete.
Software images that are in use cannot be deleted.
View the status of image imports under Image Import Status, which shows information about Remote Host, File, Status, and Time.
Before you begin, you must also have added or uploaded an updated software image before you can do the update.
You can update Base OS software while the system is up and running from the webUI.
Important: During a software update, there is an interruption to traffic, so F5 recommends that you perform the update during a maintenance window
In the Update Base OS Software section, for Update Software:
- To install a full F5OS-A version release, select Bundled.
- To install F5OS-A and service version releases independently, select Unbundled.
For ISO Image, select the full version release ISO image from the drop-down.
This field is available when Bundled is selected.
For Base OS Version, select the F5OS version from the drop-down.
This field is available when Unbundled is selected.
For Service Version, select the service version release from the drop-down.
You can configure DNS for the system from the webUI. This is used for name resolution such as when setting up the system.
On the left, click SYSTEM SETTINGS > DNS.
Under DNS Lookup Servers, specify the name servers that the system uses to validate DNS lookups, and resolve host names. For each name server you want to add:
Click Add.
For Lookup Server, type the IP address of the name server that you want to add to the list.
Click Save & Close.
Under DNS Search Domains, specify the domains that the system searches for local domain lookups and to resolve local host names. For each domain you want to add:
Click Add.
For Search Domain, type the domain name of the name server that you want to add to the list.
For example, DNSsearch.com.
Click Save & Close.
DNS lookup servers and search domains are now specified for the system.
The webUI includes options for configuring remote log servers and the log severity level for individual software components and services.
The webUI enable you to generate a system report, or QKView file, to collect configuration and diagnostic information from the rSeries system if you have any concerns about your system operation. The QKView file contains machine-readable (JSON) diagnostic data and combines the data into a single compressed tar.gz format file. You can upload the QKView file to F5 iHealth where you can get help to verify proper operation of the system and get help with troubleshooting and understanding any issues you might be having and ensure that the system is operating at its maximum efficiency.
You can add and display information about configured remote log servers from the webUI. You can also change the log severity level for individual software components and services.
On the left, click SYSTEM SETTINGS > Log Settings.
To add access to a Remote Log Server, click Add.
In the Server field, type the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the remote server.
In the Port field, type the port number of the remote server.
The default port value is 514.
For Protocol, select UDP or TCP to choose between TCP or UDP input.
From the Facility list, select LOCAL0.
F5OS supports only the LOCAL0 logging facility. All logs are directed to this facility, and it is the only one that you can use for remote logging.
From the Severity list, select the severity level of the messages to log.
Option Description Emergency Emergency system panic messages Alert Serious errors that require administrator intervention Critical Critical errors, including hardware and file system failures Error Non-critical, but possibly important, error messages Warning Warning messages that should be logged and reviewed Notice Messages that contain useful information, but might be ignored Informational Messages that contain useful information, but might be ignored Debug Verbose messages used for troubleshooting -
Click Save & Close.
On the Log Settings screen, review the software component log levels for individual software components and adjust them as needed. Click Save if you made changes.
The log levels determine at what level events (and all higher levels) are logged for each service. Informational is the default so all except debug-level events are logged.
To delete a remote log server, select the server and click Delete.
The system logs events to the appliance.log file located in the log/host directory. To list files and view the contents of log files, you use the file command from the CLI.
List all files in the log directory.
file list path [ log/confd/ | log/host/ | log/system/ }This example shows an excerpt of the contents of the
log/host/directory:appliance-1# file list path log/host entries { name anaconda/ date Thu May 12 17:01:36 UTC 2022 size 4.0KB } entries { name ansible.log date Fri Jun 17 16:18:02 UTC 2022 size 0B } entries { name appliance.log date Fri Jun 17 16:18:19 UTC 2022 size 9.8KB } entries { name audit/ date Fri Jun 17 14:59:04 UTC 2022 size 4.0KB } entries { name boot.log date Thu May 12 17:02:35 UTC 2022 size 105B } ... -
Show the contents of a log file.
file show [ log/confd/<*filename*> | log/host/<*filename*> | log/system/<*filename*> ]This example shows the contents of the
log/host/boot.logfile:appliance-1# file show log/host/boot.log May 12 10:02:35 localhost NET[1605]: /etc/sysconfig/network-scripts/ifup-post : updated /etc/resolv.conf -
Show only the most recent entries in a log file.
file tail [ log/confd/<*filename*> | log/host/<*filename*> | log/system/<*filename*> ]This example shows the last ten lines of the
appliance.logfile and uses the-foption to append output as the file grows:appliance-1# file tail -f log/host/appliance.log 2022-06-17 16:18:03.267761 - OMD log is initialized 2022-06-17 16:18:03.267761 - 8:-738199808 - applianceMainEventLoop::Orchestration manager startup. 2022-06-17 16:18:03.270244 - 8:-754985216 - Can now ping appliance-1.chassis.local (100.65.60.1). 2022-06-17 16:18:03.723485 - 8:-754985216 - Successfully ssh'd to appliance 127.0.0.1. 2022-06-17 16:18:14.399076 - 8:-738199808 - Appliance 1 is ready in k3s cluster. 2022-06-17 16:18:14.399095 - 8:-738199808 - K3S cluster is ready. appliance-flannel_image|localhost:2003/appliance-flannel:0.13.0 No Image Changes Found for normal reboot appliance-multus_image|localhost:2003/appliance-multus:3.6.3 No Image Changes Found for normal reboot _
You can import, export, download, or delete files asynchronously depending on which directory you select to work in. All file transfers are done using the HTTPS protocol.
You can import a file from an external server into the system from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.
Note: If you want to import the contents of a tar file, you need to extract the contents first before you can import them onto the F5 system.
You can import files into these directories on the system:
- configs/
- diags/shared
- images/import
- images/staging
- images/tenant
You can download files in these directories from the system to your local workstation from the webUI:
- configs
- diags/core
- diags/crash
- diags/shared
- log/confd
- log/system
You can upload files in these directories from your local workstation to the system from the webUI:
- configs
- images/staging
- images/tenant
You can export a file from the system to an external server from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.
You can export files into these directories from the system:
- configs
- log/
- log/confd
- log/controller
- log/host
- log/system
- diags/
- diags/core
- diags/crash
- diags/shared
- images/
- images/import
- images/staging
- images/tenant
You can delete files (to which you have file permissions) on the system only from the diags/shared or configs directories from either the webUI or the CLI.
File Utilities are available in the webUI. You can use File Utilities to upload, download, import, export, and/or delete files asynchronously depending on which directory you select to work in. All file transfers are done using HTTPS protocol.
On the left, click SYSTEM SETTINGS > File Utilities.
From the Base Directory list, browse the directories and click subfolders to view their contents and the commands that are available from each one.
From a subfolder, click the left arrow next to the path to navigate back to the main folder.
To import a file:
Click Import.
In the popup, type the URL of the file to import.
Provide the Username and Password only if required by the remote host.
Select Ignore Certificate Warnings if you want to skip warnings when importing files (such as if the remote host does not have a valid CA-signed certificate).
Click Import File to begin the import.
To export a file:
Select the file and click Export.
In the popup, type the Server URL for where to export the file.
Select Ignore Certificate Warnings if you want to skip warnings when importing files.
Click Export File to begin the export.
To upload or download a file:
Select the file and click Upload or Download.
The selected file will be uploaded or downloaded.
To delete a file, select the file and click Delete.
You can delete files only from the
diags/shareddirectory.
You can view the status of a file transfer operation to view its progress and see if it was successful. If an operation fails, hover over the warning icon to see the error that occurred.
Note: A runtime error displays in the File Transfer status area, if an invalid operation is performed.
You can import a file from an external server into the system or export a file to an external server from the system using the CLI.
Import a file.
file import remote-url <*ip-address-and-file-path*> local-file <*local-file-path*> username <*user*> password [ remote-port <*port-number*> } [ protocol [ https | scp | sftp ]] [insecure]Note: The insecure option ignores certificate warnings during the transfer.
This example shows how to import a Base OS ISO to the system:
appliance-1# file import remote-url https://files.company.com/images/F5OS-A-1.1.x-xxxxx.R5R10.iso local-file images/staging username admin password Enter the password at the prompt: Value for 'password' (<string>): ******** result File transfer is initiated.(images/staging/F5OS-A-1.1.x-xxxxx.R5R10.iso)Note: If the file import doesn’t work, you can alternatively use secure copy (SCP) to copy the image file to the
images/stagingdirectory of the system. -
Optionally, you can check the file transfer status.
appliance-1# file transfer-statusWhen the file transfer completes, the
StatusdisplaysComplete. -
Export a file.
file export remote-url <*ip-address-and-file-path*> local-file <*local-file-path*> username <*user*> password [ remote-port <*port-number*> } [ protocol [ https | scp | sftp ]] [insecure]This example shows how to import a Base OS ISO to the system:
appliance-1# file export local-file configs/backup1.xml remote-file /tmp/backup1.xml remote-host 192.51.100.75 username rootThe system requests the password for the remote account.
Value for 'password' (<string>): ******* result File transfer is initiated.(configs/backup1.xml) -
Delete a file.
file delete local-file diags/shared/<*file-name.xml*>This example shows how to delete a file:
appliance-1# file delete local-file diags/shared/backup1.xmlYou can only delete files from the
diags/sharedorconfigsdirectory.
You can configure Network Time Protocol (NTP) for the rSeries system. An NTP server ensures that the system clock is synchronized with Coordinated Universal Time (UTC). The system also provides authentication support for NTP, which can enhance security by ensuring that the system sends time-of-day requests only to trusted NTP servers. You can also configure the time zone and set the time and date manually, if NTP is disabled. You can use either the system controller CLI or webUI to configure time settings.
After the system license is activated, you can configure Network Time Protocol (NTP) servers, including authentication support for NTP, time zone, and manual configuration of date and time, if NTP is disabled. The NTP server ensures that the system clock is synchronized with Coordinated Universal Time (UTC). You can specify a list of servers that you want the system to use when updating the time on network systems. You can configure time settings for the system from the webUI.
On the left, click SYSTEM SETTINGS > Time Settings.
To synchronize the system clock with an NTP server, for NTP Service, click Enabled.
The NTP Service is set to Disabled, by default.
To manually set the time and date:
For NTP Service, select Disabled.
In the Manual Time & Date Settings area, click the calendar to set the date and time.
To use authentication support for NTP:
For NTP Authentication, select Enabled.
The NTP Authentication is set to Disabled by default.
For NTP Keys, click Add.
The Add NTP Key screen displays.
For Key ID, enter an identifier used by the client and server to designate a secret key.
The client and server must use the same key ID.
For Key Type, select the encryption type used for the NTP authentication key.
The default value is F5_NTP_AUTH_SHA256.
Select from these options:
- F5_NTP_AUTH_MD5
- F5_NTP_AUTH_SHA1
- F5_NTP_AUTH_SHA256
- F5_NTP_AUTH_SHA384
- F5_NTP_AUTH_SHA512
For Key Value, paste the text of the NTP authentication key.
Click Save & Close.
To specify an NTP server:
Click Add.
In the NTP Server field, type the IPv4 address, IPv6 address, or the fully qualified domain name (FQDN) of the NTP server.
Note: If specifying an FQDN, you must configure a resolvable DNS server for the system.
Click Save & Close.
To set the time zone, from Locations, select the time zone region.
Click Save & Close.
You can manually configure the date and time for your system from the CLI.
(config). -
Change the system date and/or time.
Note: You can opt to change only the time or only the date by including only the relevant option (either time or date).
system set-datetime date <*YYYY-MM-DD*> time <*HH:MM-SS*>In this example, you change the system date to 2022-01-01 and the system time to be 12:01:00:
appliance-1# system set-datetime date 2022-01-01 time 12:01:00
The system date and time are now updated.
You can configure Network Time Protocol (NTP) for your rSeries system from the CLI.
Note: If you want to enable NTP authentication, see Configure NTP authentication from the CLI.
(config). -
Enable NTP.
system ntp config enabled -
Add an NTP server.
system ntp servers server <*ip-address*>In this example, you configure an NTP server at pool.ntp.org:
appliance-1(config)# system ntp servers server pool.ntp.org -
commit -
end -
Verify that NTP is enabled and a server is configured.
appliance-1# show system ntp system ntp state enabled system ntp state enable-ntp-auth false system ntp servers server pool.ntp.org state address pool.ntp.org state port 123 state version 4 state association-type SERVER state iburst false state prefer false state stratum 4 state root-delay 34 state root-dispersion 36 state offset 244 state poll-interval 6 state authenticated false
You can configure Network Time Protocol (NTP) authentication for your rSeries system from the CLI. NTP authentication enhances security by ensuring that the system sends time-of-day requests only to trusted NTP servers.
(config). -
Enable NTP.
Enable NTP authentication.
system ntp config enable-ntp-auth true -
Add the key associated with your server to the system.
system ntp ntp-keys ntp-key <*public-key-id*> config key-id <*secret-key-id*> key-type [ F5_NTP_AUTH_MD5 | F5_NTP_AUTH_SHA1 | F5_NTP_AUTH_SHA256 | F5_NTP_AUTH_SHA384 | F5_NTP_AUTH_SHA512 ] key-value HEX:<*ntp-auth-key-value*>Important: The key ID, key type, and key value on this client system must match the server exactly.
appliance-1(config)# system ntp ntp-keys ntp-key 11 config key-id 11 key-type F5_NTP_AUTH_SHA1 key-value HEX:E27611234BB5E7CDFC8A8ACE55B567FC5CA7C890 -
Add an NTP server and associate the key ID you added with the server.
system ntp servers server <*ip-address*>In this example, you configure an NTP server at the IP address 192.0.2.118:
appliance-1(config)# system ntp servers server 192.0.2.118 appliance-1(config-server-192.0.2.118)# config key-id 11 -
commit -
end -
Verify that NTP with authentication is enabled and a server is configured.
appliance-1# show system ntp servers system ntp servers server 192.0.2.118 state address 192.0.2.118 state port 123 state version 4 state association-type SERVER state iburst false state prefer false state stratum 8 state root-delay 0 state root-dispersion 0 state offset 251333 state poll-interval 6 state key-id 11 state authenticated true
Simple Network Management Protocol (SNMP) is an industry-standard protocol that enables you to use a standard SNMP management system to remotely manage network devices. F5 rSeries systems support SNMPv1, SNMPv2c, and SNMPv3. You can configure the system from both the CLI and webUI.
SNMP support is available in different ways, depending on which F5OS software version you are using. On F5 rSeries systems, SNMP is available from both the CLI and webUI.
F5 recommends using the newer system snmp commands, which include support for SNMP versions 1, 2c, and 3. For more information on the older commands, see:
F5OS-A software version |
Older CLI (v1/v2c only) |
Newer CLI (v1/v2c/v3) |
1.2.0 |
SNMP-COMMUNITY-MIB SNMP-NOTIFICATION-MIB SNMP-TARGET-MIB SNMP-VIEW-BASED-ACM-MIB SNMPv2-MIB |
system snmp communities system snmp engine-id system snmp targets system snmp users |
Before you configure SNMP access for F5 rSeries systems:
- Add the SNMP manager IP address to the system allow list. For more information, see Configure an allow list from the webUI.
- Add descriptions to front-panel interfaces. For more information, see Configure an interface from the CLI.
- Add descriptions to management interfaces. For more information, see Configure management IP addresses from the CLI.
- Add descriptions to LAGs, if needed. For more information, see Configure a static LAG interface from the CLI.
- Download the F5 MIB files from File Utilities in the system controller or chassis partition webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select mibs, select a
.tar.gzfile, and click Download). - Configure a DNS name server if you would like to use a fully-qualified domain name (FQDN) instead of an IP address for the SNMP trap destination. For more information, see Configure DNS from the webUI.
You can view SNMP information in the /log/system/snmp.log file. You can download the log file to your local workstation from the File Utilities screen in the webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select log/system, select snmp.log, and click Download). For more information about managing files from the webUI or CLI, see File utilities overview.
SNMPWALK is an application on an SNMP management system that performs SNMP GETNEXT requests to query a network device for information. You can provide an object identifier (OID) to specify which portion of the object identifier space to search using GETNEXT requests. The SNMP management system queries all variables in the subtree below the specified OID, displays these values to the user, and stops when it returns results that are no longer inside the range of the specified OID.
These SNMP system object IDs (OIDs) are defined for each F5 rSeries system type:
- 1.3.6.1.4.1.12276.1.3.1.1 (f5OsAppR5x00)
- 1.3.6.1.4.1.12276.1.3.1.2 (f5OsAppR10x00)
- 1.3.6.1.4.1.12276.1.3.1.3 (f5OsAppR2x00)
- 1.3.6.1.4.1.12276.1.3.1.4 (f5OsAppR4x00)
The IDs display in text format when the corresponding MIB is loaded in your SNMP management system. If the MIB is not loaded, the walk displays in OID format.
To more accurately map these system OIDs, you must download the F5-OS-SYSTEM-MIB.mib file and load it into your SNMP management system. To download the F5 MIB files, use File Utilities in the webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select mibs, select a .tar.gz file, and click Download).
You can configure SNMP communities with either version 1, version 2c, or both security models from the CLI.
(config). -
Configure a community.
system snmp communities community <*community-name*> config security-model { v1 | v2c }This example creates a community that uses the v2c security model:
appliance-1(config)# system snmp communities community v2comm config security-model v2cThis example creates a community that uses both v1 and v2c community models:
appliance-1(config)# system snmp communities community v1v2c config security-model [ v1 v2c ] -
commit -
end -
Verify the community configuration.
show system snmp communitiesA summary similar to this example displays:
appliance-1# show system snmp communities SECURITY NAME NAME MODEL ---------------------------------- v1v2c v1v2c [ v1 v2c ]Note: This example shows both security models configured. If you configure only one security model, then only the configured model displays in the output.
You can configure SNMP version 3, which is a user-based security model, from the CLI. This model provides support for additional authentication and privacy protocols.
(config). -
Configure a user, including authentication and privacy protocols.
system snmp users user <*user-name*> config authentication-protocol { md5 | none | sha } privacy-protocol { aes | des | none } authentication-passwordThis example creates a user that uses MD5 authentication and AES for password authentication:
appliance-1(config)# system snmp users user jdoe config authentication-protocol md5 privacy-protocol aes authentication-passwordAfter you press Enter, you are prompted to enter the authentication password.
(<string, min: 8 chars, max: 32 chars>): ********After you press Enter, configure the privacy password.
appliance-1(config-user-v3-user)# config privacy-passwordAfter you press Enter, you are prompted to enter the privacy password.
(<string, min: 8 chars, max: 32 chars>): ********* -
commit -
end -
Verify the user configuration.
show system snmp usersA summary similar to this example displays:
appliance-1# show system snmp users AUTHENTICATION PRIVACY NAME NAME PROTOCOL PROTOCOL -------------------------------------------- jdoe jdoe md5 aes
You can configure SNMP targets with community-based security (SNMPv1/SNMPv2c) from the CLI. These are required to send system-generated traps to an SNMP management system.
(config). -
Configure a target with community-based security.
system snmp targets target <*target-name*> config community <*community-name*> security-model { v1 | v2c } { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>This example creates a target with community-based security:
appliance-1(config)# system snmp targets target v2c-target config community v2c-comm security-model v2c ipv4 address 192.0.2.24 port 5001 -
commit -
end -
Verify the target configuration.
appliance-1# show system snmp targets SECURITY NAME NAME USER COMMUNITY MODEL ADDRESS PORT ADDRESS PORT ----------------------------------------------------------------------------------------- v2c-target v2c-target jdoe - - 192.0.2.24 5001 - -
You can configure SNMP targets with user-based security (SNMPv3) from the CLI. These are required to send system-generated traps to an SNMP management system.
(config). -
Configure a target with user-based security.
system snmp targets target <*target-name*> config user <*user-name*> { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>This example creates a target with user-based security:
appliance-1(config)# system snmp targets target v3-target config user jdoe ipv4 address 192.0.2.24 port 5001 -
commit -
end -
show system snmp targetsA summary similar to this example displays:
appliance-1# show system snmp targets SECURITY NAME NAME USER COMMUNITY MODEL ADDRESS PORT ADDRESS PORT ----------------------------------------------------------------------------------------- v3-target v3-target jdoe - - 192.0.2.24 5001 - -
Before rSeries systems can exchange data with one another, they must exchange device certificates, that is, digital certificates and keys used for secure communication.
If you are using LDAP with transport layer security (TLS) for user authentication, you can choose to require TLS Certificate Validation in the authentication settings. You can add a certificate and key into the system, and when you create a certificate signing request (CSR), it saves the generated key and certificate to these directories:
system/aaa/tls/config/keysystem/aaa/tls/config/certificate
When you install an SSL certificate, you also install a certificate authority (CA) bundle, which is a file that contains root and intermediate certificates. The CA bundle and server certificate complete the SSL chain of trust.
Before you can install device certificates, you must enable LDAP as an authentication method in the system (USER MANAGEMENT > Auth Settings).
You can view a certificate from the webUI.
On the left, click SYSTEM SETTINGS > Certificate Management.
To display a TLS Certificate, a TLS Key that was previously installed, or the TLS Details, click Show.
A text area opens and displays the certificate, key, or details.
You can create or view a self-signed certificate from the webUI.
Click Create Certificate.
A form appears to enter certificate information.
In the Name field, enter a name for the certificate. For example, the server’s hostname.
In the Email field, enter the email address for the certificate contact.
In the City field, enter the city or locality name.
In the State field, enter the state, county, or region.
In the Country field, enter the two-letter country code. For example, US for United States.
In the Organization field, enter the certificate originator name. For example, your company’s name.
In the Unit field, enter the organizational unit name. For example, IT.
In the Version field, specify the version number for the certificate.
In the Days Valid field, specify the number of days the certificate is valid.
In the Key Type field, choose ECDSA or RSA as your key type.
In the Store TLS field, choose whether to store your TLS information.
Click Save.
You can create and view certificate signing requests (CSRs) from the webUI.
To create a Certificate Signing Request, click Create CSR.
For example, IT.
Click Save.
You can add or delete a CA bundle from the webUI.
In the CA Bundles area, click Add.
For Name, type the bundle name.
For TLS CA Certificate, paste the certificate text.
Click Save.
To delete a CA bundle, in the CA Bundles area, click the name of the bundle in the table and click Delete.
Click Save.
You can create a private key and a self-signed certificate from the CLI.
(config). -
Create a private key and self-signed certificate.
system aaa tls create-self-signed-cert name <*name*> email <*email-address*> city <*city*> region <*region*> country <*country*> organization <*org-name*> unit <*org-unit*> version <*cert-version*> days-valid <*number*> key-type { *rsa* | *ecdsa* } store-tls { *true* | *false* }The store-tls option stores the private key and self-signed certificate in
system/aaa/tls/config/keyandsystem/aaa/tls/config/certificateinstead of returning in the CLI output.This example creates a private key and self-signed certificate with city, country, days valid, email, key type, name, organization, region, unit and version options specified, and with store TLS set to false:
appliance-1(config)# system aaa tls create-self-signed-cert city Seattle country US days-valid 365 email jdoe@company.com key-type ecdsa name Godzilla organization "Company" region Washington unit DEV version 1 curve-name prime239v2 store-tls false response -----BEGIN EC PRIVATE KEY----- MHECAQEEHiyJEVihDTnVi+v9RjfK3LhZ2PdSOXZFMJf3lyXaoaAKBggqhkjOPQMB BaFAAz4ABHFISUTEi8wEdG0iBF3iqTi5m5b62xUSbhOJrXR8d0S6h+anvpo9xrH3 QKbVuacF7ZSNMj2tX/wyqVNePg== -----END EC PRIVATE KEY----- -----BEGIN CERTIFICATE----- MIICAzCCAa4CCQCR5RKtuBFcxTAKBggqhkjOPQQDAjCBjTELMAkGA1UEBhMCVVMx EzARBgNVBAgMCldhc2hpbmd0b24xEDAOBgNVBAcMB1NlYXR0bGUxEzARBgNVBAoM CkY1IE5ldG9ya3MxEDAOBgNVBAsMB1NXRElBR1MxETAPBgNVBAMMCEdvZHppbGxh MR0wGwYJKoZIhvcNAQkBFg5qLm1vb3JlQGY1LmNvbTAeFw0yMTAzMjcwMjE2NTFa Fw0yMjAzMjcwMjE2NTFaMIGNMQswCQYDVQQGEwJVUzETMBEGA1UECAwKV2FzaGlu Z3RvbjEQMA4GA1UEBwwHU2VhdHRsZTET3hdhv1UECgwKRjUgTmV0b3JrczEQMA4G A1UECwwHU1dESUFHUzERMA8GA1UEAwwIR29kemlsbGExHTAbBgkqhkiG9w0BCQEW DmoubW9vcmVAZjUuY29tMFUwEwYHKoZIzj0CAQYIKoZIzj0DAQUDPgAEcUhJRMSL zAR0bSIEXeKpOLmblvrbF4jsv4mtdHx3RLqH5qe+mj3GsfdAptW5pwXtlI0yPa1f /DKpU14+MAoGCCqGSM49BAMCA0MAMEACHh38OAyBBjAsVRBklBXZUIuynHq3/tr4 3VUQsMtYHQIeeP3vCrRm2qjPtK62QwtbkqDA9h2qTvuDj6uYL8EI -----END CERTIFICATE----- -
commit
Before you can enable TLS encryption, you must have already configured a key and certificate on the system.
You can configure a TLS key and certificate from the CLI.
Configure a certificate.
system aaa tls config certificate- Press Enter to enable multi-line mode and press ctrl-D to exit multi-line mode.
(<string>): [Multiline mode, exit with ctrl-D.] > ...- Enter the certificate value.
commit -
Configure a key.
system aaa tls config key- Press Enter to enable multi-line mode and press ctrl-D to exit multi-line mode.
(<string>): [Multiline mode, exit with ctrl-D.] > ...- Enter the key value.
commit -
end -
Verify that the certificate is configured.
show system aaa tls state certificateappliance-1# show system aaa tls state certificate response Certificate: Data: Version: 3 (0x2) Serial Number: 123434828 (0x1334e9cc) Signature Algorithm: sha256WithRSAEncryption Issuer: C=US, ST=WA, L=Seattle, O=MyCompany, OU=IT, CN=localhost.localdomain/emailAddress=root@localhost.localdomain Validity Not Before: Mar 18 21:40:28 2020 GMT Not After : Mar 16 21:40:28 2030 GMT Subject: C=US, ST=WA, L=Seattle, O=MyCompany, OU=IT, CN=localhost.localdomain/emailAddress=root@localhost.localdomain Subject Public Key Info: Public Key Algorithm: rsaEncryption Public-Key: (2048 bit) Modulus: 00:bc:ba:b9:8d:51:c7:c9:fe:81:86:52:ea:ef:08: ab:af:68:df:dc:22:6d:a3:23:fa:a5:5b:cd:89:3e: be:fb:cb:92:c4:bc:d7:a6:a5:f3:8b:6b:84:fa:b4: 31:39:88:8b:9a:96:2a:35:1c:3f:ee:23:4a:25:8f: cd:ca:ae:fa:e2:38:5d:9f:43:9d:18:c2:8f:1f:f7: 27:a7:75:a1:12:71:2f:ec:8f:37:e2:a6:74:cc:59: d4:c4:68:26:0c:0d:b6:b0:92:76:38:59:86:e1:54: 40:0e:0e:5d:6e:d6:e7:21:07:94:9e:43:6d:f0:50: 25:5a:68:64:39:fe:a6:df:6d:3f:f8:3c:69:9b:68: 5d:e7:36:88:5c:67:5a:02:01:99:e3:2c:d9:08:cc: d5:9e:1c:cd:46:28:3a:85:76:59:fb:b3:f1:61:bc: ef:03:57:2c:20:5d:6c:1d:11:1e:56:30:b2:91:67: 99:32:3f:d3:08:6d:4f:cd:a3:8d:f6:e6:34:9c:87: 04:8e:f2:79:f2:8c:1f:cc:1a:8b:2c:25:cf:b4:0c: ab:73:93:e4:49:d5:03:00:eb:1f:90:3c:04:c3:59: 10:90:c9:dd:29:32:cb:27:9f:04:37:f5:05:20:f9: 79:32:c1:50:66:76:1d:6d:2d:78:95:16:d2:65:7b: 4c:f1 Exponent: 65530 (x10001) Signature Algorithm: sha256WithRSAEncryption 12:21:0e:06:80:ab:df:05:9f:04:80:9f:d6:db:b9:2e:c8:d7: 39:8b:ac:6a:cf:cc:7b:5b:64:5c:59:2c:72:fe:57:d5:46:91: 0a:d4:40:0d:42:c1:95:a6:69:d9:1e:36:ac:d1:dd:f4:a1:b0: 34:3c:71:09:31:57:1a:0b:33:83:13:17:99:84:e4:70:82:85: f3:72:c7:fa:ba:0e:1a:fe:55:a1:ce:f7:96:2b:39:ef:4d:7a: 7a:23:71:44:01:c1:6c:10:58:e8:5f:6b:a8:b6:70:cc:8f:65: c8:cd:7b:aa:4b:e2:6a:bc:1c:fe:59:8f:c8:85:08:f0:46:67: 8d:15:a6:01:d0:a3:a2:fd:9c:db:c5:5b:51:07:6f:db:59:f8: bc:ba:9d:4a:30:ea:a7:7c:0c:fb:bb:9a:ea:c9:c2:a4:c1:82: e3:b8:2e:57:cd:32:6a:b1:a8:95:75:e3:82:8a:ea:c2:f8:37: c4:6f:a2:b4:e5:82:6c:3a:5d:c1:1f:a7:8e:da:7d:4c:51:d1: 45:36:da:97:31:4a:64:92:bf:bb:85:e3:bd:67:16:79:fe:53: 92:df:a8:3f:dc:8c:4e:e4:7c:b9:5e:ba:d6:ab:3d:7d:29:59: 01:27:d9:ca:52:10:58:60:00:02:19:f9:1d:74:07:5c:0d:f7: 5e:c2:d6:82
You can create a text-based certificate signing request (CSR) from the CLI.
(config). -
Create a CSR.
system aaa tls create-csr``name <*name*> email <*email-address*> city <*city*> region <*region*> country <*country*> organization <*org-name*> unit <*org-unit*> version <*cert-version*>This example creates a CSR with name, email, organization, and unit options specified:
appliance-1# (config): system aaa tls create-csr name company.com email dev@company.com organization "Company" unit engineering response -----BEGIN CERTIFICATE REQUEST----- MIIC0zCCAbsCAQEwgY0xCzAJBgNVBAYTAlVTMRMwEQYDVQQIEwpXYXNoaW5ndG9u MRAwDgYDVQQHEwdTZWF0dGxlMRQwEgYDVQQKFAtGNV9OZXR3b3JrczEUMBIGA1UE CxMLZGV2ZWxvcG1lbnQxGTAXBgkqhkiG9w0BCQEWCmRldkBmNS5jb20xEDAOBgNV BAMTB3Rlc3Rjc3IwggEiMA0GCSqGSIb3DQEBAQUAA4IBDwAwggEKAoIBAQCinnAV Dv/G6+qbiBVO7zIPmFFatYcrzdUnvpTGXf30vhBRqcW90jJy12FwtYOL8P6mED+ gfjpxRWe+vjnztjZSIDpyh7Dn+F3MRF3zkgnSKlYKI9qqzlRHRAwi2U7GfujeR5H CXrJ4uxYK2Wp8WVSa7TWwj6Bnps8Uldnj0kenBJ1eUVUXoQAbUmZQg6l+qhKRiDh 3E/xMOtaGWg0SjD7dEQij5l+8FBEHVhQKEr52d4OifR62/MZSnPw2MY5OJ69p2Wn k7Fr7m4I5z9lxJduYDNmiddVilpWdqRaCB2j29XCmpVJduF2v6EsMx693K18IJ1h iRice6oKL7eoI/NdAgMBAAGgADANBgkqhkiG9w0BAQUFAAOCAQEAGjWSAqKUPqMY eLlSDs8fhj+ckia5r/TITqamMN+m8TqQI8Pk0tAnwHCl8HHS+4cI8QuupgS/3aU ls7OtxceoQZ1VFX2sQFkrDJFe0ewZQLm5diip5kxFrnap0oA0wRy84ks0wxeiCWD New3hgSXfzyXI0g0auT6KNwsGaO8ZuhOX3ICNnSLbfb00aYbhfI9jKopXQgZG/LO pOct33fdpf/U6kQA9Rw/nzs3Hz/nsVleOrl3TH1+9veMMF+6eq8KKPpbYKh9bhA+ pYI3TtbZHuyRyQbq/r4gf4JkIu/PGszzy/rsDWy+b9g9nXMh1oFj+xhTrBjBk8a2 0ov+Osy2iA== -----END CERTIFICATE REQUEST----- -
commit
You can configure a Certificate Revocation List (CRL) entry from the CLI.
(config). -
To configure a CRL entry.
system aaa tls crls crl <*crl-name*>In this example, you configure a CRL named “bbb”:
appliance-1(config)# system aaa tls crls crl bbb- Press Enter to enable multi-line mode and press ctrl-D to exit multi-line mode.
Value for 'config revocation-key'(<string>): [Multiline mode, exit with ctrl-D.] > ...- Enter the key value.
commit -
To delete a CRL entry.
no system aaa tls crls crl <*crl-name*>In this example, you delete a CRL entry named “bbb”:
appliance-1(config)# no system aaa tls crls crl bbb -
commit -
end -
View the CRLs currently on the system.
show system aaa tls crls crlThis example shows the CRLs currently on the system:
appliance-1# show system aaa tls crls crl DATE NAME ADDED -------------------- *name* 3/11/2021
When you install an SSL certificate, you add a certificate authority (CA) bundle, which is a file that contains root and intermediate certificates, in addition to the certificate. You can add or delete a CA bundle from the CLI.
Note: The default login credentials are admin/admin. When logging in as admin for the first time, the system prompts you to change the password.
(config). -
To add a CA bundle.
system aaa tls ca-bundles ca-bundle <*ca-bundle-name*> config name <*ca-bundle-name*> content- Press Enter to enable multi-line mode and press ctrl-D to exit multi-line mode.
In this example, you add a CA bundle named “test_caaaa”:
appliance-1(config)# system aaa tls ca-bundles ca-bundle test_caaaa config name test_caaaa content -
commit -
To delete a CA bundle.
no system aaa tls ca-bundles ca-bundle <*ca-bundle-name*>In this example, you delete a CA bundle named “test_caaaa”:
appliance-1(config)# no system aaa tls ca-bundles ca-bundle test_caaaa -
commit
You can back up the system configuration from the webUI.
On the left, click SYSTEM SETTINGS > Configuration Backup.
Click Create.
The Create Configuration Backup popup opens.
In the Name field, type a name for the backup (for example, system-12-21-21).
Click Create.
The backup is created and added to the list.
To delete a backup file, select the file and click Delete.
System configuration backups are stored in configs/. Backups should be stored on off the system.
You can restore configurations from the CLI. For more information on saving and restoring the configuration, see the Complete backup and restore overview section.
You can activate a license for the rSeries system from either the CLI or webUI. There is one license per rSeries system, which is also used by any tenants.
There are two ways to license the system:
- Automatically
- If your system is connected to the internet, use the Automatic method to prompt the system to contact the F5 license server and activate the license.
- Manually
- If your system is not connected to the internet, use a management workstation that is connected to the internet to retrieve an activation key from F5 and then transfer it to the system.
Important:
Adding or reactivating a license on an active rSeries system might impact traffic on tenants. Traffic processing will stop briefly on the tenants, and then restart automatically. This occurs when the tenant receives a new or reactivated license causing a configuration reload on the tenants. For more information, see these other references:
- F5 rSeries Systems: Installation and Upgrade at Documentation - F5OS-A and F5 rSeries.
- K7752: Licensing the BIG-IP system
- Additional information about BIG-IP Next licensing may be available on the F5 beta portal.
You can license a system using the automatic method from the webUI, as long as the system has Internet access.
On the left, click SYSTEM SETTINGS > Licensing.
For the Base Registration Key field, the registration key is auto-populated.
You can choose to overwrite this field with a new registration key by clicking Reactivate and overwriting the field.
For the Add-On Keys field, the associated add-on keys are auto-populated.
You can choose to change these keys by clicking Reactivate and then click + or x to add or remove additional add-on keys.
For the Activation Method, select Automatic.
Click Activate.
The End User License Agreement (EULA) displays.
Click Agree to accept the EULA.
The system is now licensed. If a base registration key or add-on key fails to activate, try re-activating the license or contact F5 Support at my.f5.com.
You can license a system without access to the Internet using the manual activation method from the webUI.
For the Activation Method, select Manual.
For the Device Dossier, click Get Dossier.
The system refreshes and displays the dossier.
Copy the dossier text in the Device Dossier field.
Click Click here to access F5 Licensing Server.
The Activate F5 Product page displays.
Paste the dossier in the Enter Your Dossier field.
Click Next.
The license key text displays.
Copy the license key text.
Alternatively, you can use the F5 license activation portal at activate.f5.com/license.
In the License Text field, paste the license key text.
Click Activate.
You can activate the rSeries system license manually from the system CLI.
(config). -
Get the system dossier.
system licensing get-dossier [registration-key XXXXX-XXXXX-XXXXX-XXXXX-XXXXXXX]The registration key is optional. If it is not included, the system uses the one already pre-installed. If no registration key is found, you receive an error.
The dossier for the system displays.
Get the license file using the dossier output you just received by going to the F5 siteactivate.f5.com/license/dossier.jsp.
Copy the license file text.
Install the license.
system licensing manual-install license -
Paste the license file content in multiline mode, then press Ctrl+D.
appliance-1(config)# system licensing manual-install license Value for 'license' (<string>): [Multiline mode, exit with ctrl-D.] >
The rSeries system is licensed. The license applies to the system and tenants.
For automatic rSeries system licensing, the system needs to be able to connect to the F5 licensing server either through the Internet or another means of networking. You need to have the Base Registration Key (five sets of characters separated by hyphens) provided by F5, and any add-on keys (two sets of 7 characters separated by a hyphen) that you have purchased. The Base Registration Key with associated add-on keys are pre-installed on a new rSeries system.
You can activate the rSeries system license automatically from the CLI.
(config). -
Apply a license to the system.
system licensing install registration-key <*key*>The registration key is optional. If it is not included, the system uses the one that is already pre-installed. If no registration key is found, you receive an error.
This example applies a specified base registration license to the system:
appliance-1(config)# system licensing install registration-key I1234-12345-12345-12345-1234567 result License installed successfully. -
Apply any add-on keys.
system licensing install add-on-keys <*add-on-keys*>This example enables the additional features associated with the three specified add-on-keys, along with the entitlements of the base registration key:
appliance-1(config)# system licensing install add-on-keys [1234567-1234567 2345678-2345678 3456789-3456789] result License installed successfully.
The rSeries system is licensed. The license and any add-on keys apply to the system and all tenants.
You can display the license and associated information of an rSeries system from the CLI.
Display the system license.
show system licensingA summary similar to this example displays:
appliance-1# show system licensing system licensing license Licensed version 1.1.0 Registration Key I1234-12345-12345-12345-1234567 Licensed date 2022/02/08 License start 2022/02/07 License end 2022/03/11 Service check date 2022/02/08 Platform ID C128 Appliance SN f5-nhlh-lule Active Modules Local Traffic Manager, r10900 (S680352-1548257) LTM to Best Upgrade, r109XX Rate Shaping DNSSEC Anti-Virus Checks Base Endpoint Security Checks Firewall Checks Machine Certificate Checks Network Access Protected Workspace Secure Virtual Keyboard APM, Web Application App Tunnel Remote Desktop DNS Rate Fallback, Unlimited DNS Licensed Objects, Unlimited DNS Rate Limit, Unlimited QPS GTM Rate Fallback, (UNLIMITED) GTM Licensed Objects, Unlimited GTM Rate, Unlimited Carrier Grade NAT (AFM ONLY) APM, Limited Routing Bundle Protocol Security Manager Access Policy Manager, Base, r109XX Advanced Web Application Firewall, r10XXX Max SSL, r10900 Max Compression, r10900 DNS Max, rSeries Advanced Firewall Manager, r10XXX -
Display the entire license file content received from the F5 license server.
show running-config system licensing
F5 r10000 platforms include two storage drives that support drive mirroring using a redundant array of independent disks (RAID) by default. You can manage the software RAID array from either the CLI or the webUI.
Important: If you need to swap out a faulty drive, you must first remove the drive from the software RAID array before physically removing the drive from the platform.
You can configure a software RAID (redundant array of independent disks) for the system from the webUI.
On the left, click SYSTEM SETTINGS > RAID Configuration.
To remove a drive from the software RAID array:
Select the drive to remove.
Click Remove.
When prompted, click OK to confirm drive removal.
To add a drive to the software RAID array:
Select the drive to add.
Click Add.
When prompted, click OK to confirm drive addition.
You can configure a software RAID (redundant array of independent disks) for the system from the CLI.
(config). -
Remove a drive from the software RAID array.
system raid remove drive ssd2A summary similar to this example displays:
appliance-1(config)# system raid remove drive ssd2 status Remove of RAID SSD2 initiated. [11084.434517] md/raid1:md121: Disk failure on nvme1n1p3, disabling device. [11084.434517] md/raid1:md121: Operation continuing on 1 devices. [11084.449528] md/raid1:md122: Disk failure on nvme1n1p4, disabling device. [11084.449528] md/raid1:md122: Operation continuing on 1 devices. [11084.464098] md/raid1:md123: Disk failure on nvme1n1p5, disabling device. [11084.464098] md/raid1:md123: Operation continuing on 1 devices. [11084.478342] md/raid1:md124: Disk failure on nvme1n1p1, disabling device. [11084.478342] md/raid1:md124: Operation continuing on 1 devices. [11084.492509] md/raid1:md127: Disk failure on nvme1n1p2, disabling device. [11084.492509] md/raid1:md127: Operation continuing on 1 devices. status Remove of RAID SSD2 initiated. -
Add the replacement drive to the array.
system raid add drive ssd2A summary similar to this example displays:
appliance-1(config)# system raid add drive ssd2 status Add RAID SSD2 initiated.The array status for the new drive should change to
replicating, and the STAT LED should change to solid green. The replication process typically takes between 15 and 45 minutes.
You can configure general system settings for the rSeries system, such as system hostname, login banner, and message of the day (MOTD) banner. Depending on which setting you want to configure, you can use either the CLI or the webUI.
You can configure the hostname, login banner, and a message of the day (MOTD) banner for the system from the webUI.
On the left, click SYSTEM SETTINGS > General.
For Hostname, enter a custom hostname for the system.
For Login Banner, enter any text to be shown when users log in to the system.
For MOTD Banner, enter any text to be used as a MOTD when users log in to the system.
Click Save.
You can run the system in appliance mode. Appliance mode adds a layer of security removing user access to Root and Bash. Enabling appliance mode disables all Root and Bash shell access for the system.
You can enable appliance mode at each of these levels:
- System
- Tenant
Appliance mode is disabled at all levels, by default. You can enable it from the webUI or the CLI. The appliance mode option for the system is available to users with admin access under SYSTEM SETTINGS > General in the webUI. For tenants, it is available in the webUI under TENANT MANAGEMENT > Tenant Deployments.
These are the effects of enabling appliance mode at each of the different levels.
System-level appliance mode
- Root or Bash access is disabled on the system.
- Console access: Root or Bash access is disabled on the system. Users can log in to the system CLI from the console using an admin account.
Tenant appliance mode
- Root access to the tenant is disabled by all means. Bash access is disabled for users (with a terminal shell flag enabled) inside the tenant.
- Users can access the tenant only through the webUI or the CLI.
- Tenant console access: Users can log in to the CLI from the virtual console using an admin account (with a terminal shell flag enabled).
You can enable or disable appliance mode from the webUI. Enable appliance mode to disable all root and Bash shell access.
Note: The appliance mode option for tenants is available in the webUI under TENANT MANAGEMENT > Tenant Deployments.
For Appliance Mode, select Enabled to enable it, or Disabled to disable it.
The default value is Disabled.
Click Save.