Manual Chapter : System Settings

Applies To:

  • F5OS-A

    1.7.0

System Settings

You can access system settings in the webUI.

You can view active system alarms and events in the webUI and CLI.

The Alarms & Events screen lists alert information for system components (such as PSU, firmware, and LCD) that have currently crossed a performance or health threshold. Use this screen to identify the specific component that is affected.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Alarm & Events.

  3. Choose from one of these actions:

    • To refresh the alarms or events list, click the Refresh icon on the right of the screen.
    • To display events result by time preference, click the down arrow next to the Refresh icon and select a value from the list. The default value is one hour. For example, select five minutes to display any event that occurred in the last five minutes.
    • To display events by severity, select a value from the Severity list. The default value is WARNING.
      Option Description
      Emergency Emergency system panic messages
      Alert Serious errors that require administrator intervention
      Critical Critical errors, including hardware and file system failures
      Error Non-critical, but possibly important, error messages
      Warning Warning messages that should be logged and reviewed
      Notice Messages that contain useful information, but might be ignored
      Informational Messages that contain useful information, but might be ignored
      Debug Detailed messages used for troubleshooting

You can view information about active system alarm conditions from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. View a list of active system alarm conditions.

    show system alarms | tab

    This example shows a power supply unit (PSU) redundancy fault:

    appliance-1# show system alarms | tab
    ID     RESOURCE        SEVERITY  TEXT                           TIME CREATED
    –––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––-          
    65793  psu-1           ERROR     PSU fault detected             2022-06-01-11:11:11.999825828 UTC

You can access management interface settings in the webUI.

You can view or change settings for the management interface from the webUI.

You can view or change settings for the management interface from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Management Interface.

  3. For DHCP, select either Enabled or Disabled.

  4. Under IPv4 and IPv6, you can configure either one management IP address type or both types for the system:

    1. For IP Address, enter IP addresses in the appropriate sections for IPv4 or IPv6, or in both sections, if using both.

      The supported IPv4 format is, for example, 192.0.2.101. The supported IPv6 format is, for example, 2001:DB80:3238:DFE1:63::FEFB

    2. For Prefix Length, specify a number from 1-32.

    3. For Gateway, enter the gateway IP address.

  5. Under Interface Settings, you can configure the management port:

    1. For State, select either Enabled or Disabled.

    2. For Auto-negotiation, select either Enabled or Disabled.

      If you enable auto-negotiation, port speed and duplex mode are set automatically.

    3. For Port Speed, select one of these options: SPEED_1GB, SPEED_10MB, or SPEED_100MB.

    4. For Duplex Mode, select FULL or HALF.

  6. Click Save.

You can configure the management interface from the CLI.

  1. Connect to the system using a management console or console server.

    Note: The default baud rate and serial port configuration is 19200/8-N-1.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Enable and set general properties for the management interface.

    interfaces interface mgmt config { disabled | enabled } description <*interface-description*>

    In this example, you enable the management interface, add a description, and set the type:

    appliance-1(config)# interfaces interface mgmt config enabled description 
      "Mgmt Interface"
  5. Exit to the top level of the configuration hierarchy.

    top

  6. Configure Ethernet properties for the management interface.

    interfaces interface mgmt config auto-negotiate { false | true } duplex-mode { FULL | HALF } port-speed { SPEED\_1GB | SPEED\_10MB | SPEED\_100MB }

    In this example, you enable the management interface, add a description, and set the type:

    appliance-1(config)# interfaces interface mgmt config auto-negotiate true 
      duplex-mode FULL port-speed SPEED_1GB
  7. Commit the configuration changes.

    commit

  8. Return to user (operational) mode.

    end

  9. Verify that the management interface is configured.

    show interfaces interface mgmt

    A summary similar to this example displays:

    appliance-1# show interfaces interface mgmt 
    interfaces interface mgmt
     state name  mgmt
     state type  ethernetCsmacd
     state enabled true
     state oper-status UP
     ethernet state auto-negotiate true
     ethernet state duplex-mode FULL
     ethernet state port-speed SPEED_1GB
     ethernet state hw-mac-address 00:12:a1:34:56:78
     ethernet state negotiated-duplex-mode FULL
     ethernet state negotiated-port-speed SPEED_1GB

You can access settings for hardening the security of your system in the webUI.

An allow list enables you to specify either specific IPv4 or IPv6 addresses, ports, or a netmask as an accepted source that can access the system.

When the IP address is configured and saved to the system allow list, only traffic coming from that IP address and port is accepted by the system’s management interface. You can also edit or delete entries in the allow list after you have configured them.

You can configure the system allow list from the webUI. To edit an existing allow list entry, select the IP address that you want to edit. You cannot change the designated name, but you can change all other fields.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > System Security.

  3. In the Allowed IP Addresses area, click Add to add an IP address to the allow list.

  4. For Name, enter a descriptive name for the IP address.

  5. For IPv4/IPv6, select IPv4 or IPv6.

  6. For Address, enter the IP address to be added to the allow list.

  7. For Prefix Length, enter or select the prefix length.

    The prefix length values must be between 1 and 32 for IPv4 and between 1 and 128 for IPv6.

  8. For Port, select a port number for the IP address.

    Available options are:

    • 443 (HTTPS): Allow only HTTP with SSL traffic on this IP address.
    • 80 (HTTP): Allow only HTTP traffic on this IP address.
    • 8888 (RESTCONF): Allow only RESTCONF traffic on this IP address.
    • 161 (SNMP): Allow only SNMP traffic on this IP address.
    • 7001 (VCONSOLE): Allow only VCONSOLE traffic on this IP address.
    • 22 (SSH): Allow only SSH traffic on this IP address.
  9. Click Save & Close.

You can configure the system allow list from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Configure the system to allow traffic only from specified IP addresses.

    system allowed-ips allowed-ip <*allowlist-profile-name*> config { ipv4 | ipv6 } address <*ip-address*> port <*port-number*> prefix-length <*subnet-prefix-length*>

    Important: This is applicable only for ports 161 (SNMP), 8888 (RESTCONF), 443 (HTTPS), 80 (HTTP), 7001 (VCONSOLE), and 22 (SSH).

    This example adds a specified IPv4 address to the system allow list:

    appliance-1(config)# system allowed-ips allowed-ip test config 
      ipv4 address 192.0.2.33 port 161 prefix-length 32

    This example adds a netmask to the system allow list:

    appliance-1(config)# system allowed-ips allowed-ip test config 
      ipv4 address 192.0.2.0 port 161 prefix-length 24

    This example restricts access to the management interface (SSH) to only the specified IP address:

    appliance-1(config)# system allowed-ips allowed-ip test config 
      ipv4 address 192.0.2.33 port 22 prefix-length 32
  4. Commit the configuration changes.

    commit

You can run the system in appliance mode. Appliance mode adds a layer of security removing user access to Root and Bash. Enabling appliance mode disables all Root and Bash shell access for the system.

You can enable appliance mode at each of these levels:

  • System
  • Tenant

Appliance mode is disabled at all levels, by default. You can enable it from the webUI or the CLI. The appliance mode option for the system is available to users with admin access under SYSTEM SETTINGS > General in the webUI. For tenants, it is available in the webUI under TENANT MANAGEMENT > Tenant Deployments.

These are the effects of enabling appliance mode at each of the different levels.

System-level appliance mode

  • Root or Bash access is disabled on the system.
  • Console access: Root or Bash access is disabled on the system. Users can log in to the system CLI from the console using an admin account.

Tenant appliance mode

  • Root access to the tenant is disabled by all means. Bash access is disabled for users (with a terminal shell flag enabled) inside the tenant.
  • Users can access the tenant only through the webUI or the CLI.
  • Tenant console access: Users can log in to the CLI from the virtual console using an admin account (with a terminal shell flag enabled).

You can enable or disable appliance mode from the webUI. Enable appliance mode to disable all root and Bash shell access.

Note: The appliance mode option for tenants is available in the webUI under TENANT MANAGEMENT > Tenant Deployments.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > System Security.

  3. , in the Appliance Mode area, for Enable/Disable, select either Enabled or Disabled.

    The default value is Disabled.

  4. Click Save.

You can configure appliance mode from the CLI if you want to disable all root and Bash shell access.

Note: For greater security, it is highly recommended that you configure the system to run in appliance mode.

Note: The appliance mode option for tenants is available in the CLI using the tenants tenant <*tenant-name*> config appliance-mode command sequence.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Enable appliance mode.

    system appliance-mode config [ disabled | enabled ]

    In this example, you enable appliance mode on the system controllers:

    appliance-1(config)# system appliance-mode config enabled
  5. Commit the configuration changes.

    commit

The LCD touchscreen enables you to view system status and manage the system without attaching a console or network cable. You can configure the LCD to meet security requirements by changing to a more restrictive operational mode.

The LCD touchscreen supports these modes:

Allows access to all options.

Allows access only to management and setup options. A padlock icon displays next to limited options.

Does not allow access to any options and displays only an image to indicate that the LCD touchscreen is disabled.

You can configure the operational mode of the touchscreen LCD from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > System Security.

  3. In the LCD area, for Mode, select one of these options:

    • Select Disabled to not allow access to any options; displays only an image to indicate that the LCD touchscreen is disabled.
    • Select Secure to allow access only to management and setup options; displays a padlock icon next to limited options.
    • Select Standard to allow access to all options.
  4. Click Save.

Cryptographic agility on F5 rSeries systems enables you to replace cryptographic implementations for the httpd and sshd services. This applies to the F5OS management interface.

You can configure the cryptographic implementations on the system for the httpd and sshd services from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > System Security.

  3. In the Services area, for httpd Cipher Suites, enter the SSL cipher suites used for the httpd service.

    You can specify more than one cipher suite by separating the cipher suite names with a colon.

  4. For sshd Ciphers, enter the ciphers to use for the sshd service.

    For example, aes128-cbc or aes128-ctr. The cipher string can take several additional forms. It can consist of a single cipher suite or a list of cipher suites containing a certain algorithm, or cipher suites of a certain type. You can combine lists of cipher suites into a single cipher string by enclosing them in square brackets and delimiting them with a space.

  5. For sshd KEX Algorithms, enter the key exchange algorithms used for the sshd service.

    For example, diffie-hellman-group14-sha1 or diffie-hellman-group14-sha256. You can combine lists of KEX algorithms into a single string by enclosing them in square brackets and delimiting them with a space.

  6. For sshd MAC Algorithms, enter the MAC algorithms used for the sshd service.

    For example, hmac-sha2-512 or AEAD_AES_128_GCM. You can combine lists of MAC algorithms into a single string by enclosing them in square brackets and delimiting them with a space.

  7. Click Save.

You can show the current crypto configuration on the system from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Show the current configuration.

    show system security services service state

    A summary similar to this example displays:

    appliance-1# show system security services service state
    system security services service httpd
     state ssl-ciphersuite ECDHE-RSA-AES256-GCM-SHA384:ECDHE-ECDSA-AES256-GCM-SHA384:
     ECDHE-RSA-AES256-SHA384:ECDHE-ECDSA-AES256-SHA384:ECDHE-RSA-AES256-SHA:ECDHE-ECDSA-AES256-SHA:
     DHE-DSS-AES256-GCM-SHA384:DHE-RSA-AES256-GCM-SHA384:DHE-RSA-AES256-SHA256:DHE-DSS-AES256-SHA256:DHE-RSA-AES256-SHA:DHE-DSS-AES256-SHA:DHE-RSA-CAMELLIA256-SHA:DHE-DSS-CAMELLIA256-SHA:ECDH-RSA-AES256-GCM-SHA384:ECDH-ECDSA-AES256-GCM-SHA384:ECDH-RSA-AES256-SHA384:ECDH-ECDSA-AES256-SHA384:ECDH-RSA-AES256-SHA:ECDH-ECDSA-AES256-SHA:AES256-GCM-SHA384:AES256-SHA256:AES256-SHA:CAMELLIA256-SHA:PSK-AES256-CBC-SHA:ECDHE-RSA-AES128-GCM-SHA256:ECDHE-ECDSA-AES128-GCM-SHA256:ECDHE-RSA-AES128-SHA256:ECDHE-ECDSA-AES128-SHA256:ECDHE-RSA-AES128-SHA:ECDHE-ECDSA-AES128-SHA:DHE-DSS-AES128-GCM-SHA256:DHE-RSA-AES128-GCM-SHA256:DHE-RSA-AES128-SHA256:DHE-DSS-AES128-SHA256:DHE-RSA-AES128-SHA:DHE-DSS-AES128-SHA:DHE-RSA-CAMELLIA128-SHA:DHE-DSS-CAMELLIA128-SHA:ECDH-RSA-AES128-GCM-SHA256:ECDH-ECDSA-AES128-GCM-SHA256:ECDH-RSA-AES128-SHA256:ECDH-ECDSA-AES128-SHA256:ECDH-RSA-AES128-SHA:ECDH-ECDSA-AES128-SHA:AES128-GCM-SHA256:AES128-SHA256:AES128-SHA:CAMELLIA128-SHA:PSK-AES128-CBC-SHA
    system security services service sshd
     state ciphers [ aes128-cbc aes128-ctr aes128-gcm@openssh.com aes256-cbc aes256-ctr 
      aes256-gcm@openssh.com ]
     state kexalgorithms [ diffie-hellman-group14-sha1 diffie-hellman-group14-sha256 
     diffie-hellman-group16-sha512 ecdh-sha2-nistp256 ecdh-sha2-nistp384 ecdh-sha2-nistp521 ]

You can configure the sshd service from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure the sshd service.

    system security services service sshd config ciphers [ <*string*> ] kexalgorithms [ <*string*> ] macs [ <*string*> ]

    These are the available configuration options:

    Option

    Description

    ciphers

    User-specified ciphers. For example, aes128-cbc or aes128-ctr.The cipher string can take several additional forms. It can consist of a single cipher suite or a list of cipher suites containing a certain algorithm, or cipher suites of a certain type. You can combine lists of cipher suites into a single cipher string using the + character as a logical AND operation.

    kexalgorithms

    User-specified key exchange algorithms. For example, diffie-hellman-group14-sha1 or diffie-hellman-group14-sha256.You can combine lists of KEX algorithms into a single string using the + character as a logical AND operation.

    macs

    User-specified MAC algorithms. For example, hmac-sha2-512 or AEAD_AES_128_GCM.You can combine lists of MAC algorithms into a single string using the + character as a logical AND operation.

    This example shows configuring the sshd service:

    appliance-1(config)# system security services service ssh config ciphers [ aes128-ctr aes256-cbc ] 
      kexalgorithms [ ecdh-sha2-nistp521 echd-sha2-nistp384 ] macs [ hmac-sha1 ]
  5. Commit the configuration changes.

    commit

After you commit the change, you are prompted to confirm the change. The service will then restart.

You can configure the SSL cipher suites used for the httpd service from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure one or more cipher suites for the httpd service.

    system security services service httpd config ssl-ciphersuite <*string*>

    In this example, you indicate that the system uses only the specified cipher suite:

    appliance-1(config)# system security services service httpd config 
      ssl-ciphersuite ECDHE-RSA-AES256-GCM-SHA384

    In this example, you specify more than one cipher suite by separating the cipher suite names with a colon:

    appliance-1(config)# system security services service httpd config 
      ssl-ciphersuite ECDHE-RSA-AES128-SHA:ECDHE-RSA-AES256-SHA
  5. Commit the configuration changes.

    commit

After you commit the change, you are prompted to confirm the change. The service will then restart.

When you configure ciphers for httpd, you can use multiple formats. You can specify a single cipher suite, such as RC4-SHA. You can also represent a list of cipher suites containing a certain algorithm or cipher suites of a certain type using a shortened name. For example, SHA1 represents all cipher suites using the digest algorithm SHA1, and SSLv3 represents all SSLv3 algorithms. You can combine lists of cipher suites into a single cipher string using the + character as a logical AND operation. For example, SHA1+DES represents all cipher suites containing the SHA1 and DES algorithms.

These are the allowed SSL cipher suites for general appliances:

  • ECDHE-RSA-AES256-GCM-SHA384
  • ECDHE-ECDSA-AES256-GCM-SHA384
  • ECDHE-RSA-AES256-SHA384
  • ECDHE-ECDSA-AES256-SHA384
  • ECDHE-RSA-AES256-SHA
  • ECDHE-ECDSA-AES256-SHA
  • DHE-DSS-AES256-GCM-SHA384
  • DHE-RSA-AES256-GCM-SHA384
  • DHE-RSA-AES256-SHA256
  • DHE-DSS-AES256-SHA256
  • DHE-RSA-AES256-SHA
  • DHE-DSS-AES256-SHA
  • DHE-RSA-CAMELLIA256-SHA
  • DHE-DSS-CAMELLIA256-SHA
  • ECDH-RSA-AES256-GCM-SHA384
  • ECDH-ECDSA-AES256-GCM-SHA384
  • ECDH-RSA-AES256-SHA384
  • ECDH-ECDSA-AES256-SHA384
  • ECDH-RSA-AES256-SHA
  • ECDH-ECDSA-AES256-SHA
  • AES256-GCM-SHA384
  • AES256-SHA256
  • AES256-SHA
  • CAMELLIA256-SHA
  • PSK-AES256-CBC-SHA
  • ECDHE-RSA-AES128-GCM-SHA256
  • ECDHE-ECDSA-AES128-GCM-SHA256
  • ECDHE-RSA-AES128-SHA256
  • ECDHE-ECDSA-AES128-SHA256
  • ECDHE-RSA-AES128-SHA
  • ECDHE-ECDSA-AES128-SHA
  • DHE-DSS-AES128-GCM-SHA256
  • DHE-RSA-AES128-GCM-SHA256
  • DHE-RSA-AES128-SHA256
  • DHE-DSS-AES128-SHA256
  • DHE-RSA-AES128-SHA
  • DHE-DSS-AES128-SHA
  • DHE-RSA-CAMELLIA128-SHA
  • DHE-DSS-CAMELLIA128-SHA
  • ECDH-RSA-AES128-GCM-SHA256
  • ECDH-ECDSA-AES128-GCM-SHA256
  • ECDH-RSA-AES128-SHA256
  • ECDH-ECDSA-AES128-SHA256
  • ECDH-RSA-AES128-SHA
  • ECDH-ECDSA-AES128-SHA
  • AES128-GCM-SHA256
  • AES128-SHA256
  • AES128-SHA
  • CAMELLIA128-SHA
  • PSK-AES128-CBC-SHA

These are the allowed SSL cipher suites for systems that have a FIPS software license applied. It does not apply to the F5 r5900-DF or r10900-DF platforms that have an embedded FIPS hardware security module (HSM).

  • ECDHE-RSA-AES128-GCM-SHA256
  • ECDHE-RSA-AES256-GCM-SHA384
  • ECDHE-RSA-AES128-SHA
  • ECDHE-RSA-AES256-SHA
  • ECDHE-RSA-AES128-SHA256
  • ECDHE-RSA-AES256-SHA384
  • ECDHE-ECDSA-AES128-GCM-SHA256
  • ECDHE-ECDSA-AES256-GCM-SHA384
  • ECDHE-ECDSA-AES128-SHA
  • ECDHE-ECDSA-AES256-SHA
  • ECDHE-ECDSA-AES128-SHA256
  • ECDHE-ECDSA-AES256-SHA384

When you configure ciphers for sshd, you enclose the cipher string in square brackets and include more than one by separating them with a space. These ciphers are allowed on the system.

  • ecdh-sha2-nistp256
  • ecdh-sha2-nistp384
  • ecdh-sha2-nistp521
  • diffie-hellman-group16-sha512
  • diffie-hellman-group14-sha256
  • diffie-hellman-group14-sha1

For security purposes, you can configure how long management sessions can remain idle before you are logged out of the system. If you are connected using an SSH connection, the system closes the SSH connection after this time expires.

You can configure how long management sessions can remain idle before you are logged out of the system from the webUI. If you are connected using an SSH connection, the system closes the SSH connection after this time expires.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > System Security.

  3. In the Services area, for CLI Idle Timeout, enter a time, in seconds, for how long management sessions can remain idle before they time out.

    A value of 0 (zero) sets the time to infinity, so the user is never logged out. The timeout can be a value from 0 through 8192 seconds. The default value is 1800 seconds (30 minutes).

  4. Click Save.

You can configure how long management sessions can remain idle before you are logged out of the system from the CLI. If you are connected using an SSH connection, the system closes the SSH connection after this time expires. You can also configure how long the system is inactive for a root user connected to the system or via SSH or console before the user is logged out of the system.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Configure the CLI session idle timeout setting for an admin user connected to the system.

    system settings config idle-timeout <*time-in-seconds*>

    A value of 0 (zero) sets the time to infinity, so the user is never logged out. The timeout can be a value from 0 through 8192 seconds. The default value is 1800 seconds (30 minutes).

    This example sets an idle timeout of 3600 seconds (one hour):

    appliance-1(config)# system settings config idle-timeout 3600
  4. Configure the CLI session idle timeout setting for an admin or a root user connected via either SSH or console.

    system settings config sshd-idle-timeout <*time-in-seconds*>

    A value of 0 (zero) sets the time to infinity, so the user is never logged out. The timeout can be a value from 0 through 8192 seconds. The default value is 0 (zero).

    This example sets an SSH system idle timeout of 3600 seconds (one hour):

    appliance-1(config)# system settings config sshd-idle-timeout 3600
  5. Commit the configuration changes.

    commit

The Software Management screen on the webUI includes options for uploading, importing and updating Base OS software for the system.

You can manage software images from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Software Management.

  3. To import a Base OS image:

    1. Click Import.

      A popup opens.

    2. For URL, enter the URL of the remote image server.

      F5 recommends that the remote host be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate. You can opt to select the Ignore Certificate Warnings check box if you want to skip the certificate check.

    3. For Username, type the user name for an account on the remote image server, if required.

    4. For Password, type the password for the account, if required.

    5. Select Ignore Certificate Warnings to skip the certificate check.

    6. Click Add Image.

    Note: Depending on the image file size and network availability, the import might take a few minutes. When the import is successful, the software image is listed in the webUI.

  4. To upload a Base OS image that you have downloaded to your local workstation:

    1. Click Upload.

    2. Navigate to the image file and select it.

    3. Click Open.

  5. To delete a Base OS image, select the image and click Delete.

    Software images that are in use cannot be deleted.

View the status of image imports under Image Import Status, which shows information about Remote Host, File, Status, and Time.

Before you begin, you must also have added or uploaded an updated software image before you can do the update.

You can update Base OS software while the system is up and running from the webUI.

Important: During a software update, there is an interruption to traffic, so F5 recommends that you perform the update during a maintenance window

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Software Management.

  3. In the Update Base OS Software section, for Update Software:

    • To install a full F5OS-A version release, select Bundled.
    • To install F5OS-A and service version releases independently, select Unbundled.
  4. For ISO Image, select the full version release ISO image from the drop-down.

    This field is available when Bundled is selected.

  5. For Base OS Version, select the F5OS version from the drop-down.

    This field is available when Unbundled is selected.

  6. For Service Version, select the service version release from the drop-down.

    This field is available when Unbundled is selected.

You can install independent system or service packages on the system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Verify the version compatibility of a package on the system.

    system packages package <*package-name*> check-version version <*version*>

    This example checks the version compatibility of a package:

    appliance-1(config)# system packages package optics-mgr-independent-pkg 
      check-version version 4.0.0.2022_08_02_16_17_05.s3a9dffb4      
    response Compatibility verification succeeded.
  4. Install a new version of a package.

    system packages package <*package-name*> set-version version <*version*> proceed { no | yes }

    This example sets a new version of a package:

    appliance-1(config)# system packages package optics-mgr-independent-pkg 
      set-version version 4.0.0.2022_08_02_16_17_05.s3a9dffb4 proceed
    Possible completions:
      no  yes
  5. Commit the configuration changes.

    commit

You can remove independent system or service packages from the system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Remove an independent package from the system.

    system packages package <*package-name*> remove version <*version*>

    This example removes a specified package version:

    appliance-1(config)# system packages package optics-mgr-independent-pkg 
      remove version 4.0.0.2022_08_02_16_17_05.s3a9dffb4
  4. Commit the configuration changes.

    commit

The DNS screen on the webUI includes options for configuring Domain Name System (DNS) lookup servers and search domains for use with the system.

You can configure DNS for the system from the webUI. This is used for name resolution such as when setting up the system.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > DNS.

  3. Under DNS Lookup Servers, specify the name servers that the system uses to validate DNS lookups, and resolve host names. For each name server you want to add:

    1. Click Add.

    2. For Lookup Server, enter the IP address of the name server that you want to add to the list.

    3. Click Save & Close.

  4. Under DNS Search Domains, specify the domains that the system searches for local domain lookups and to resolve local host names. For each domain you want to add:

    1. Click Add.

    2. For Search Domain, enter the domain name of the name server that you want to add to the list.

      For example, DNSsearch.com.

    3. Click Save & Close.

DNS lookup servers and search domains are now specified for the system.

You can configure DNS for the system from the CLI. This is used for name resolution such as when setting up the system.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure a DNS lookup server.

    system dns servers server <*ip-address*> port <*port*>

    This example configures a DNS server at 192.0.2.20:

    appliance-1(config)# system dns servers server 192.0.2.20
  5. Commit the configuration changes.

    commit

The webUI includes options for configuring remote log servers and the log severity level for individual software components and services.

From the webUI you can generate a system report, or QKView file, to collect configuration and diagnostic information from the rSeries system if you have any concerns about your system operation. The QKView file contains machine-readable (JSON) diagnostic data and combines the data into a single compressed tar.gz format file. You can upload the QKView file to F5 iHealth where you can get help to verify proper operation of the system and get help with troubleshooting and understanding any issues you might be having and ensure that the system is operating at its maximum efficiency.

You can view event logs and configure secure remote logging from the CLI. You can also send host log files, which are in the /var/log directory, as well as audit.log files to the remote server from the CLI.

You can add and display information about configured remote log servers from the webUI. You can also change the log severity level for individual software components and services.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Log Settings.

  3. To add access to a Remote Log Server, click Add.

  4. In the Server field, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the remote server. After the remote log server is saved, you cannot modify the server address.

  5. In the Port field, enter the port number of the remote server.

    The default port value is 514.

  6. For Protocol, select UDP or TCP to choose between TCP or UDP input. When the TCP protocol is selected, the Authentication field displays.

  7. From the Facility list, select LOCAL0.

    F5OS supports only the LOCAL0 logging facility. All logs are directed to this facility, and it is the only one that you can use for remote logging.

  8. From the Severity list, select the severity level of the messages to log.

    Option Description
    Emergency Emergency system panic messages
    Alert Serious errors that require administrator intervention
    Critical Critical errors, including hardware and file system failures
    Error Non-critical, but possibly important, error messages
    Warning Warning messages that should be logged and reviewed
    Notice Messages that contain useful information, but might be ignored
    Informational Messages that contain useful information, but might be ignored
    Debug Verbose messages used for troubleshooting
  9. For Authentication, select the enable or disable option from the list. The default value is Disabled. This option is visible when the TCP protocol is selected while configuring the remote log server. If the UDP protocol is selected, the authentication value is saved as N/A.

  10. Click Save & Close.

  11. To delete a remote log server, select the server and click Delete.

  12. To view the Host Log Settings, click Show.

  13. For Host Log Forwarding, select the enable or disable radio button for remote forwarding. The default value is Disabled. When host log forwarding is enabled, the Include Standby Controller field displays.

  14. For Selectors, select the required facility and severity options from the list. To add more selectors, click the add + icon. To remove the existing selectors, click the remove (X) icon.

  15. To add the required host log files to the Selected Files panel, at the chassis level, click the required host log files checkboxes.

    At the chassis partition level, you can only view the already selected and locked host files.

    The Selected Files option allows the host logs files to be forwarded from the directory and subdirectories.

  16. For Custom Log File, enter the log file in the text box and click Add to manually add host log file names to the Selected Files panel.

  17. For TLS Certificate & Key, click Show. It displays TLS Certificate and TLS Key options. If the authentication value is set as enabled for any of the remote log servers, you cannot be able to clear the TLS configuration fields.

  18. For CA Bundles, click Add to enter the name and TLS CA certificate. When any of the remote server authentication is enabled, you cannot delete the CA bundle.

  19. On the Log Settings screen, review the software component log levels for individual software components and adjust them as needed. Click Save if you made changes.

    The log levels determine at what level events (and all higher levels) are logged for each service. Informational is the default so all except debug-level events are logged.

  20. Click Save to save the log settings.

The system logs events to the appliance.log file located in the log/host directory. To list files and view the contents of log files, you use the file command from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. List all files in the log directory.

    file list path [ log/confd/ | log/host/ | log/system/ }

    This example shows an excerpt of the contents of the log/host/ directory:

    appliance-1# file list path log/host
    entries {
        name anaconda/
        date Thu May 12 17:01:36 UTC 2022
        size 4.0KB
    }
    entries {
        name ansible.log
        date Fri Jun 17 16:18:02 UTC 2022
        size 0B
    }
    entries {
        name appliance.log
        date Fri Jun 17 16:18:19 UTC 2022
        size 9.8KB
    }
    entries {
        name audit/
        date Fri Jun 17 14:59:04 UTC 2022
        size 4.0KB
    }
    entries {
        name boot.log
        date Thu May 12 17:02:35 UTC 2022
        size 105B
    }
    ...
  4. Show the contents of a log file.

    file show [ log/confd/<*filename*> | log/host/<*filename*> | log/system/<*filename*> ]

    This example shows the contents of the log/host/boot.log file:

    appliance-1# file show log/host/boot.log
    May 12 10:02:35 localhost NET[1605]: /etc/sysconfig/network-scripts/ifup-post : updated /etc/resolv.conf
  5. Show only the most recent entries in a log file.

    file tail [ log/confd/<*filename*> | log/host/<*filename*> | log/system/<*filename*> ]

    This example shows the last ten lines of the appliance.log file and uses the -f option to append output as the file grows:

    appliance-1# file tail -f log/host/appliance.log
    2022-06-17 16:18:03.267761 - OMD log is initialized
    2022-06-17 16:18:03.267761 - 8:-738199808 - applianceMainEventLoop::Orchestration manager startup.
    2022-06-17 16:18:03.270244 - 8:-754985216 - Can now ping appliance-1.chassis.local (100.65.60.1).
    2022-06-17 16:18:03.723485 - 8:-754985216 - Successfully ssh'd to appliance 127.0.0.1.
    2022-06-17 16:18:14.399076 - 8:-738199808 - Appliance 1 is ready in k3s cluster.
    2022-06-17 16:18:14.399095 - 8:-738199808 - K3S cluster is ready.
    appliance-flannel_image|localhost:2003/appliance-flannel:0.13.0
    No Image Changes Found for normal reboot
    appliance-multus_image|localhost:2003/appliance-multus:3.6.3
    No Image Changes Found for normal reboot
    _

The system logs events to the appliance.log file located in the var/log directory and enables you to send these logs to a remote server. By configuring secure remote logging from the CLI, you can send logs in audit.log to a remote server. Secure logging is disabled by default.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure secure remote logging. The default value is disabled.

    system logging remote-servers remote-server <*ip-address*> config proto { udp | tcp | remote-port <*port-number*> authentication { disabled | enabled }

    The default protocol is upd, and the default port number is 514.

    This example enables secure remote logging:

    appliance-1(config)# system logging remote-servers remote-server 
      192.0.2.58 config proto tcp remote-port 80 authentication enabled
  5. Add certificate or key details for secure remote logging.

    system logging tls { certificate | key } <*string*>

  6. Add CA bundle details for secure remote logging.

    system logging tls ca-bundles ca-bundle <*name*> config name <*name*> content <*ca-cert-contents*>

    Note: The certificate bundle that you specify must include the certificate chain of the certificate authority.

  7. Commit the configuration changes.

    commit

  8. Return to user (operational) mode.

    end

  9. Verify the authentication, certificate, key, and CA bundle configuration.

    show running-config system logging tls { certificate | key | ca-bundles } <*string*>

You can disable secure remote logging from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Disable secure remote logging.

    system logging remote-servers remote-server <*ip-address*> config proto { udp | tcp | remote-port <*port-number*> authentication { disabled | enabled }

    This example disables secure remote logging:

    appliance-1(config)# system logging remote-servers remote-server 
      192.0.2.58 config proto tcp remote-port 80 authentication disabled
  5. Remove authentication details from secure remote logging.

    no system logging remote-servers remote-server <*ip-address*> config authentication

  6. Remove certificate or key details from secure remote logging.

    no system logging tls { certificate | key } <*string*>

  7. Remove CA bundle details from secure remote logging.

    no system logging tls ca-bundles ca-bundle

  8. Commit the configuration changes.

    commit

  9. Return to user (operational) mode.

    end

  10. Veify the authentication, certificate, key, and CA bundle configuration.

    show running-config system logging tls { certificate | key | ca-bundles } <*string*>

You can import, export, download, or delete files asynchronously depending on which directory you select to work in. All file transfers are done using the HTTPS protocol.

You can import a file from an external server into the system from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.

Note: If you want to import the contents of a tar file, you need to extract the contents first before you can import them onto the F5 system.

You can import files into these directories on the system:

  • configs/
  • diags/shared
  • images/import
  • images/staging
  • images/tenant

You can download files in these directories from the system to your local workstation from the webUI:

  • configs
  • diags/core
  • diags/crash
  • diags/shared
  • log/confd
  • log/system

You can upload files in these directories from your local workstation to the system from the webUI:

  • configs
  • images/staging
  • images/tenant

You can export a file from the system to an external server from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.

You can export files into these directories from the system:

  • configs
  • log/
  • log/confd
  • log/controller
  • log/host
  • log/system
  • diags/
  • diags/core
  • diags/crash
  • diags/shared
  • images/
  • images/import
  • images/staging
  • images/tenant

You can delete files (to which you have file permissions) on the system only from the diags/shared or configs directories from either the webUI or the CLI.

File Utilities are available in the webUI. You can use File Utilities to upload, download, import, export, and/or delete files asynchronously depending on which directory you select to work in. All file transfers are done using HTTPS protocol.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > File Utilities.

  3. From the Base Directory list, browse the directories and click subfolders to view their contents and the commands that are available from each one.

    From a subfolder, click the left arrow next to the path to navigate back to the main folder.

  4. To import a file:

    1. Click Import.

    2. In the popup, enter the URL of the file to import.

    3. Provide the Username and Password only if required by the remote host.

    4. Select Ignore Certificate Warnings if you want to skip warnings when importing files (such as if the remote host does not have a valid CA-signed certificate).

    5. Click Import File to begin the import.

  5. To export a file:

    1. Select the file and click Export.

    2. In the popup, enter the Server URL for where to export the file.

    3. Provide the Username and Password only if required by the remote host.

    4. Select Ignore Certificate Warnings if you want to skip warnings when importing files.

    5. Click Export File to begin the export.

  6. To upload or download a file:

    1. Select the file and click Upload or Download.

      The selected file will be uploaded or downloaded.

  7. To delete a file, select the file and click Delete.

    You can delete files only from the diags/shared directory.

You can view the status of a file transfer operation to view its progress and see if it was successful. If an operation fails, hover over the warning icon to see the error that occurred.

Note: A runtime error displays in the File Transfer status area, if an invalid operation is performed.

You can view the contents of a file from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. View the contents of a file.

    file show <*local-file-path*>

    This example shows how to view the contents of the platform.log file:

    appliance-1# file show log/system/platform.log | until 5
    2022-12-27T21:34:24.718946+00:00 appliance-1 tmstat-agent[1]: priority="Info" version=1.0 msgid=0x1601000000000008 msg="TMSTAT directory set from command line." directory="cluster".
    2022-12-27T21:34:24.719592+00:00 appliance-1 ihealthd[8]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
    appliance-1# file show log/system/platform.log | until 15
    2022-12-27T21:34:24.718946+00:00 appliance-1 tmstat-agent[1]: priority="Info" version=1.0 msgid=0x1601000000000008 msg="TMSTAT directory set from command line." directory="cluster".
    2022-12-27T21:34:24.719592+00:00 appliance-1 ihealthd[8]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
    2022-12-27T21:34:24.720155+00:00 appliance-1 alert-service[9]: priority="Notice" version=1.0 msgid=0x2201000000000001 msg="Alert Service starting." version="3.11.7" date="Thu Nov  3 13:25:15 2022".
    ...

You can import a file from an external server onto your system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Import a file.

    file import remote-url <*ip-address-and-file-path*> local-file <*local-file-path*> username <*user*> password [ remote-port <*port-number*> } [ protocol [ https | scp | sftp ]] [insecure]

    Note: The insecure option ignores certificate warnings during the transfer.

    This example shows how to import a Base OS ISO to the system:

    appliance-1# file import remote-url https://files.company.com/images/F5OS-A-1.6.x-xxxxx.R5R10.iso 
      local-file images/staging username admin password
    Enter the password at the prompt:
         Value for 'password' (<string>): ******** 
    result File transfer is initiated.(images/staging/F5OS-A-1.6.x-xxxxx.R5R10.iso)

    Note:

    • If the file import doesn’t work, you can alternatively use secure copy (SCP) to copy the image file to the images/staging directory of the system.

    • When importing a file using the remote-url argument, you must wrap the URL in double quotes (""). This prevent special characters from being incorrectly interpreted as shell commands. For example: remote-url "https://example.com/file-path?params"

      Example: Transfer a file named {}myfile.iso{} from the remote URL https://files.example.com on port 443 to the images/staging directory on the system:

      file import local-file images/staging remote-url "https://files.example.com/images.myfile.iso" remote-port 443 protocol https
  3. Optionally, you can check the file transfer status.

    appliance-1# file transfer-status

    When the file transfer completes, the Status displays Complete.

  4. Export a file.

    file export remote-url <*ip-address-and-file-path*> local-file <*local-file-path*> username <*user*> password [ remote-port <*port-number*> } [ protocol [ https | scp | sftp ]] [insecure]

    This example shows how to import a Base OS ISO to the system:

    appliance-1# file export local-file configs/backup1.xml remote-file /tmp/backup1.xml 
      remote-host 192.51.100.75 username root

    The system requests the password for the remote account.

    Value for 'password' (<string>): *******
    result File transfer is initiated.(configs/backup1.xml)
  5. Delete a file.

    file delete local-file diags/shared/<*file-name.xml*>

    This example shows how to delete a file:

    appliance-1# file delete local-file diags/shared/backup1.xml

    You can only delete files from the diags/shared or configsdirectory.

You can cancel an in-progress file import onto your system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Get the operation identifier for the file transfer process.

    show file transfer-operations

    A summary similar to this example displays:

    appliance-1# show file transfer-operations
    file transfer-operations transfer-operation images/import/iso/F5OS-A-1.6.0-1234.iso 
      files/F5OS-A/images/F5OS-A-1.6.0-1234.iso "Import file" "HTTPS   "
     operation-id IMPORT-C16QYpun
     status       "In Progress (13.0%)"
     timestamp    "Fri Mar 24 23:05:54 2023"
  3. Cancel the specified file transfer.

    file abort-transfer operation-id <*id*>

    This example shows canceling a specified in-progress file transfer:

    appliance-1# file abort-transfer operation-id IMPORT-C16QYpun
    Aborting will stop the file transfer. Do you want to proceed? [yes/no] yes
    result File transfer abort operation initiated.

You can export a file to an external server from your system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Export a file.

    file export insecure local-file <*local-file-path*> protocol { https | scp | sftp } remote-file <*remote-file-path*> remote-host <*ip-address-or-fqdn*> remote-port <*port-number*> remote-url <*ip-address-or-fqdn*> username <*user*> web-token <*remote-system-token*>

You can delete files from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Delete a file.

    file delete local-file diags/shared/<*file-name.xml*>

    This example shows how to delete a file:

    appliance-1# file delete local-file diags/shared/backup1.xml

    You can delete files only from the diags/shared or configsdirectories.

You can configure Network Time Protocol (NTP) for the rSeries system. An NTP server ensures that the system clock is synchronized with Coordinated Universal Time (UTC). The system also provides authentication support for NTP, which can enhance security by ensuring that the system sends time-of-day requests only to trusted NTP servers. You can also configure the time zone and set the time and date manually, if NTP is disabled. You can use either the CLI or webUI to configure time settings.

After the system license is activated, you can configure Network Time Protocol (NTP) servers, including authentication support for NTP, time zone, and manual configuration of date and time, if NTP is disabled. The NTP server ensures that the system clock is synchronized with Coordinated Universal Time (UTC). You can specify a list of servers that you want the system to use when updating the time on network systems. You can configure time settings for the system from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Time Settings.

  3. To synchronize the system clock with an NTP server, for NTP Service, click Enabled.

    The NTP Service is set to Disabled, by default.

  4. To manually set the time and date:

    1. For NTP Service, select Disabled.

    2. In the Manual Time & Date Settings area, click the calendar to set the date and time.

  5. To use authentication support for NTP:

    1. For NTP Authentication, select Enabled.

      The NTP Authentication is set to Disabled by default.

    2. For NTP Keys, click Add.

      The Add NTP Key screen displays.

    3. For Key ID, enter an identifier used by the client and server to designate a secret key.

      The client and server must use the same key ID.

    4. For Key Type, select the encryption type used for the NTP authentication key.

      The default value is F5_NTP_AUTH_SHA256.

      Select from these options:

      • F5_NTP_AUTH_MD5
      • F5_NTP_AUTH_SHA1
      • F5_NTP_AUTH_SHA256
      • F5_NTP_AUTH_SHA384
      • F5_NTP_AUTH_SHA512
    5. For Key Value, paste the text of the NTP authentication key.

    6. Click Save & Close.

  6. To specify an NTP server:

    1. Click Add.

    2. In the NTP Server field, enter the IPv4 address, IPv6 address, or the fully qualified domain name (FQDN) of the NTP server.

      Note: If specifying an FQDN, you must configure a resolvable DNS server for the system.

    3. Click Save & Close.

  7. To set the time zone, from Locations, select the time zone region.

  8. Click Save & Close.

You can manually configure the date and time for your system from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Change the system date and/or time.

    Note: You can opt to change only the time or only the date by including only the relevant option (either time or date).

    system set-datetime date <*YYYY-MM-DD*> time <*HH:MM-SS*>

    In this example, you change the system date to 2022-01-01 and the system time to be 12:01:00:

    appliance-1(config)# system set-datetime date 2022-01-01 time 12:01:00

The system date and time are now updated.

You can configure Network Time Protocol (NTP) for your rSeries system from the CLI.

Note: If you want to enable NTP authentication, see Configure NTP authentication from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Enable NTP.

    system ntp config enabled

  5. Add an NTP server.

    system ntp servers server <*ip-address*>

    In this example, you configure an NTP server at pool.ntp.org:

    appliance-1(config)# system ntp servers server pool.ntp.org
  6. Commit the configuration changes.

    commit

  7. Return to user (operational) mode.

    end

  8. Verify that NTP is enabled and a server is configured.

    appliance-1# show system ntp
    system ntp state enabled
    system ntp state enable-ntp-auth false
    system ntp servers server pool.ntp.org
     state address    pool.ntp.org
     state port       123
     state version    4
     state association-type SERVER
     state iburst     false
     state prefer     false
     state stratum    4
     state root-delay 34
     state root-dispersion 36
     state offset     244
     state poll-interval 6
     state authenticated false

You can configure Network Time Protocol (NTP) authentication for your rSeries system from the CLI. NTP authentication enhances security by ensuring that the system sends time-of-day requests only to trusted NTP servers.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Enable NTP.

    system ntp config enabled

  5. Enable NTP authentication.

    system ntp config enable-ntp-auth true

  6. Add the key associated with your server to the system.

    system ntp ntp-keys ntp-key <*public-key-id*> config key-id <*secret-key-id*> key-type [ F5_NTP_AUTH_MD5 | F5_NTP_AUTH_SHA1 | F5_NTP_AUTH_SHA256 | F5_NTP_AUTH_SHA384 | F5_NTP_AUTH_SHA512 ] key-value HEX:<*ntp-auth-key-value*>

    Important: The key ID, key type, and key value on this client system must match the server exactly.

    appliance-1(config)# system ntp ntp-keys ntp-key 11 
      config key-id 11 key-type F5_NTP_AUTH_SHA1 key-value 
      HEX:E27611234BB5E7CDFC8A8ACE55B567FC5CA7C890       
  7. Add an NTP server and associate the key ID you added with the server.

    system ntp servers server <*ip-address*>

    In this example, you configure an NTP server at the IP address 192.0.2.118:

    appliance-1(config)# system ntp servers server 192.0.2.118
    appliance-1(config-server-192.0.2.118)# config key-id 11
  8. Commit the configuration changes.

    commit

  9. Return to user (operational) mode.

    end

  10. Verify that NTP with authentication is enabled and a server is configured.

    appliance-1# show system ntp servers
    system ntp servers server 192.0.2.118
     state address    192.0.2.118
     state port       123
     state version    4
     state association-type SERVER
     state iburst     false
     state prefer     false
     state stratum    8
     state root-delay 0
     state root-dispersion 0
     state offset     251333
     state poll-interval 6
     state key-id     11
     state authenticated true

Simple Network Management Protocol (SNMP) is an industry-standard protocol that enables you to use a standard SNMP management system to remotely manage network devices. F5 rSeries systems support SNMPv1, SNMPv2c, and SNMPv3. You can configure the system from both the CLI and webUI.

SNMP support is available in different ways, depending on which F5OS software version you are using. On F5 rSeries systems, SNMP is available from both the CLI and webUI.

SNMP support is available in different ways, depending on which F5OS software version you are using. On F5 rSeries systems, SNMP is available from both the CLI and webUI.

F5 recommends using the newer system snmp commands, which include support for SNMP versions 1, 2c, and 3. For more information on the older commands, see:

F5OS-A software version

Older CLI (v1/v2c only)

Newer CLI (v1/v2c/v3)

1.2.0

SNMP-COMMUNITY-MIB

SNMP-NOTIFICATION-MIB

SNMP-TARGET-MIB

SNMP-VIEW-BASED-ACM-MIB

SNMPv2-MIB

system snmp communities system snmp engine-id

system snmp targets

system snmp users

Before you configure SNMP access for F5 rSeries systems:

You can view SNMP information in the /log/system/snmp.log file. You can download the log file to your local workstation from the File Utilities screen in the webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select log/system, select snmp.log, and click Download). For more information about managing files from the webUI or CLI, see File utilities overview.

SNMPWALK is an application on an SNMP management system that performs SNMP GETNEXT requests to query a network device for information. You can provide an object identifier (OID) to specify which portion of the object identifier space to search using GETNEXT requests. The SNMP management system queries all variables in the subtree below the specified OID, displays these values to the user, and stops when it returns results that are no longer inside the range of the specified OID.

These SNMP system object IDs (OIDs) are defined for each F5 rSeries system type:

  • 1.3.6.1.4.1.12276.1.3.1.1 (f5OsAppR5x00)
  • 1.3.6.1.4.1.12276.1.3.1.2 (f5OsAppR10x00)
  • 1.3.6.1.4.1.12276.1.3.1.3 (f5OsAppR2x00)
  • 1.3.6.1.4.1.12276.1.3.1.4 (f5OsAppR4x00)

The IDs display in text format when the corresponding MIB is loaded in your SNMP management system. If the MIB is not loaded, the walk displays in OID format.

To more accurately map these system OIDs, you must download the F5-OS-SYSTEM-MIB.mib file and load it into your SNMP management system. To download the F5 MIB files, use File Utilities in the webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select mibs, select a .tar.gz file, and click Download).

You can configure the SNMP port from the rSeries webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > SNMP Configuration.

  3. For Port, enter the required value. The allowed values for the Port are either 161 or in the ranges of [1024-7000, 7033-8887, 8889-65535]. To check whether a port is valid or not, we have inline validation.

    Note: The port configured in the SNMP Configuration area is reflected on the Allow List Entry screen of the Allowed IP Addresses section under System Security in the System Settings chapter. When an allowlist is created with an SNMP port, the user is not allowed to change the SNMP Port on the SNMP Configuration area, which can cause an error. For more information, see Configure the system allow list from the webUI.

  4. Click Save & Close.

You can configure SNMP communities with either version 1, version 2c, or both security models from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > SNMP Configuration.

  3. In the Communities area, click Add.

    The Add Community screen displays.

  4. For Community, enter a descriptive name.

  5. For Security Model, select from these security models: v1, v2c, and v1 and v2c.

  6. Click Save & Close.

You can configure SNMP version 3, which is a user-based security model, from the webUI. This model provides support for additional authentication and privacy protocols.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > SNMP Configuration.

  3. In the Users area, click Add.

    The Add v3 User screen displays.

  4. For User, enter the user name.

  5. For Authentication Protocol, select from these protocols: MD5, SHA, or None.

  6. For Authentication Password, enter the password for the specified user.

  7. For Privacy Protocol, select from these protocols: AES128, DES, or None.

  8. Click Save & Close.

Before you can add an SNMP target, you must have already configured either the SNMPv1/v2c community or SNMPv3 user.

You can configure SNMP targets from the webUI. These are required to send system-generated traps to a manager. You can choose either community (v1/v2c) or user-based (v3) security.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > SNMP Configuration.

  3. In the Targets area, click Add.

    The Add Target screen displays.

  4. For Name, enter a descriptive name.

  5. For Security Model, select from these security models: v1, v2c, or v3.

  6. Select one of these options, depending on the selected security model:

    • If you selected v1 or v2c, for Community, select the community that you created with that security model.
    • If you selected v3, for User, select the user that you created.
  7. For IPv4/IPv6, select either IPv4 or IPv6.

  8. For Address, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the target.

  9. For Port, enter the port number for the target.

    The default value is 162, and the range is from 1024 to 65535

  10. Click Save & Close.

You can configure SNMP communities with either version 1, version 2c, or both security models from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure a community.

    system snmp communities community <*community-name*> config security-model { v1 | v2c }

    This example creates a community that uses the v2c security model:

    appliance-1(config)# system snmp communities community v2comm config 
      security-model v2c

    This example creates a community that uses both v1 and v2c community models:

    appliance-1(config)# system snmp communities community v1v2c config 
      security-model [ v1 v2c ]
  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. Verify the community configuration.

    show system snmp communities

    A summary similar to this example displays:

    appliance-1# show system snmp communities
                          SECURITY   
    NAME       NAME       MODEL      
    ----------------------------------
    v1v2c      v1v2c     [ v1 v2c ]  

    Note: This example shows both security models configured. If you configure only one security model, then only the configured model displays in the output.

You can configure SNMP version 3, which is a user-based security model, from the CLI. This model provides support for additional authentication and privacy protocols.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure a user, including authentication and privacy protocols.

    system snmp users user <*user-name*> config authentication-protocol { md5 | none | sha } privacy-protocol { aes | des | none } authentication-password

    This example creates a user that uses MD5 authentication and AES for password authentication:

    appliance-1(config)# system snmp users user jdoe config 
      authentication-protocol md5 privacy-protocol aes authentication-password

    After you press Enter, you are prompted to enter the authentication password.

    (<string, min: 8 chars, max: 32 chars>): ********

    After you press Enter, configure the privacy password.

    appliance-1(config-user-v3-user)# config privacy-password

    After you press Enter, you are prompted to enter the privacy password.

    (<string, min: 8 chars, max: 32 chars>): *********
  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. Verify the user configuration.

    show system snmp users

    A summary similar to this example displays:

    appliance-1# show system snmp users
                      AUTHENTICATION  PRIVACY  
    NAME     NAME     PROTOCOL        PROTOCOL 
    --------------------------------------------
    jdoe     jdoe     md5             aes

You can configure SNMP targets with community-based security (SNMPv1/SNMPv2c) from the CLI. These are required to send system-generated traps to an SNMP management system.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure a target with community-based security.

    system snmp targets target <*target-name*> config community <*community-name*> security-model { v1 | v2c } { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>

    This example creates a target with community-based security:

    appliance-1(config)# system snmp targets target v2c-target 
      config community v2c-comm security-model v2c ipv4 address 192.0.2.24 
      port 5001
  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. Verify the target configuration.

    show system snmp users

    A summary similar to this example displays:

    appliance-1# show system snmp targets
                                              SECURITY                                      
    NAME       NAME       USER     COMMUNITY  MODEL     ADDRESS         PORT  ADDRESS  PORT 
    -----------------------------------------------------------------------------------------
    v2c-target v2c-target jdoe     -          -         192.0.2.24      5001  -        -

You can configure SNMP targets with user-based security (SNMPv3) from the CLI. These are required to send system-generated traps to an SNMP management system.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure a target with user-based security.

    system snmp targets target <*target-name*> config user <*user-name*> { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>

    This example creates a target with user-based security:

    appliance-1(config)# system snmp targets target v3-target 
      config user jdoe ipv4 address 192.0.2.24 port 5001
  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. Verify the target configuration.

    show system snmp targets

    A summary similar to this example displays:

    appliance-1# show system snmp targets
                                              SECURITY                                      
    NAME       NAME       USER     COMMUNITY  MODEL     ADDRESS         PORT  ADDRESS  PORT 
    -----------------------------------------------------------------------------------------
    v3-target  v3-target  jdoe     -          -         192.0.2.24      5001  -        -

You can back up the system configuration from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Configuration Backup.

  3. Click Create.

    The Create Configuration Backup popup opens.

  4. In the Name field, enter a name for the backup (for example, system-12-21-21).

  5. Click Create.

    The backup is created and added to the list.

  6. To delete a backup file, select the file and click Delete.

System configuration backups are stored in configs/. Backups should be stored on off the system.

You can restore configurations from the CLI. For more information on saving and restoring the configuration, see Complete backup and restore overview.

You can activate a license for the rSeries system from either the CLI or webUI. There is one license per rSeries system, which is also used by any tenants.

There are two ways to license the system:

Automatically
If your system is connected to the internet, use the Automatic method to prompt the system to contact the F5 license server and activate the license.
Manually
If your system is not connected to the internet, use a management workstation that is connected to the internet to retrieve an activation key from F5 and then transfer it to the system.

Important:

Adding or reactivating a license on an active rSeries system might impact traffic on tenants. Traffic processing will stop briefly on the tenants, and then restart automatically. This occurs when the tenant receives a new or reactivated license causing a configuration reload on the tenants. For more information, see these other references:

You can license a system using the automatic method from the webUI, as long as the system has Internet access.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Licensing.

  3. For the Base Registration Key field, the registration key is auto-populated.

    You can choose to overwrite this field with a new registration key by clicking Reactivate and overwriting the field.

  4. For the Add-On Keys field, the associated add-on keys are auto-populated.

    You can choose to change these keys by clicking Reactivate and then click + or x to add or remove additional add-on keys.

  5. For the Activation Method, select Automatic.

  6. Click Activate.

    The End User License Agreement (EULA) displays.

  7. Click Agree to accept the EULA.

The system is now licensed. If a base registration key or add-on key fails to activate, try re-activating the license or contact F5 Support at support.f5.com.

You can license a system without access to the Internet using the manual activation method from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > Licensing.

  3. For the Base Registration Key field, the registration key is auto-populated.

    You can choose to overwrite this field with a new registration key by clicking Reactivate and overwriting the field.

  4. For the Add-On Keys field, the associated add-on keys are auto-populated.

    You can choose to change these keys by clicking Reactivate and then click + or x to add or remove additional add-on keys.

  5. For the Activation Method, select Manual.

  6. For the Device Dossier, click Get Dossier.

    The system refreshes and displays the dossier.

  7. Copy the dossier text in the Device Dossier field.

  8. Click Click here to access F5 Licensing Server.

    The Activate F5 Product page displays.

  9. Paste the dossier in the Enter Your Dossier field.

  10. Click Next.

    The license key text displays.

  11. Copy the license key text.

    Alternatively, you can use the F5 license activation portal at activate.f5.com/license.

  12. In the License Text field, paste the license key text.

  13. Click Activate.

    The End User License Agreement (EULA) displays.

  14. Click Agree to accept the EULA.

The system is now licensed. If a base registration key or add-on key fails to activate, try re-activating the license or contact F5 Support at support.f5.com.

You can activate the rSeries system license manually from the system CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Get the system dossier.

    system licensing get-dossier [registration-key XXXXX-XXXXX-XXXXX-XXXXX-XXXXXXX]

    The registration key is optional. If it is not included, the system uses the one already pre-installed. If no registration key is found, you receive an error.

    The dossier for the system displays.

  4. Get the license file using the dossier output you just received by going to the F5 siteactivate.f5.com/license/dossier.jsp.

  5. Copy the license file text.

  6. Install the license.

    system licensing manual-install license

    Press Enter to enable multi-line mode and paste the contents. Press Ctrl-D to exit multi-line mode.

    appliance-1(config)# system licensing manual-install license 
    Value for 'license' (<string>): 
    [Multiline mode, exit with ctrl-D.]
    >

The rSeries system is licensed. The license applies to the system and tenants.

For automatic rSeries system licensing, the system needs to be able to connect to the F5 licensing server either through the Internet or another means of networking. You need to have the Base Registration Key (five sets of characters separated by hyphens) provided by F5, and any add-on keys (two sets of 7 characters separated by a hyphen) that you have purchased. The Base Registration Key with associated add-on keys are pre-installed on a new rSeries system.

You can activate the rSeries system license automatically from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Apply a license to the system.

    system licensing install registration-key <*key*>

    The registration key is optional. If it is not included, the system uses the one that is already pre-installed. If no registration key is found, you receive an error.

    This example applies a specified base registration license to the system:

    appliance-1(config)# system licensing install registration-key 
     I1234-12345-12345-12345-1234567
    result License installed successfully. 
  4. Apply any add-on keys.

    system licensing install add-on-keys <*add-on-keys*>

    This example enables the additional features associated with the three specified add-on-keys, along with the entitlements of the base registration key:

    appliance-1(config)# system licensing install 
     add-on-keys [1234567-1234567 2345678-2345678 3456789-3456789]
    result License installed successfully.

The rSeries system is licensed. The license and any add-on keys apply to the system and all tenants.

You can display the license and associated information of an rSeries system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Display the system license.

    show system licensing

    A summary similar to this example displays:

    appliance-1# show system licensing
     system licensing license   Licensed version    1.1.0
           Registration Key    I1234-12345-12345-12345-1234567
           Licensed date       2022/02/08
           License start       2022/02/07
           License end         2022/03/11
           Service check date  2022/02/08
           Platform ID         C128
           Appliance SN        f5-nhlh-lule
    
           Active Modules
            Local Traffic Manager, r10900 (S680352-1548257)
              LTM to Best Upgrade, r109XX
              Rate Shaping
              DNSSEC
              Anti-Virus Checks
              Base Endpoint Security Checks
              Firewall Checks
              Machine Certificate Checks
              Network Access
              Protected Workspace
              Secure Virtual Keyboard
              APM, Web Application
              App Tunnel
              Remote Desktop
              DNS Rate Fallback, Unlimited
              DNS Licensed Objects, Unlimited
              DNS Rate Limit, Unlimited QPS
              GTM Rate Fallback, (UNLIMITED)
              GTM Licensed Objects, Unlimited
              GTM Rate, Unlimited
              Carrier Grade NAT (AFM ONLY)
              APM, Limited
              Routing Bundle
              Protocol Security Manager
              Access Policy Manager, Base, r109XX
              Advanced Web Application Firewall, r10XXX
              Max SSL, r10900
              Max Compression, r10900
              DNS Max, rSeries
              Advanced Firewall Manager, r10XXX
  3. Display the entire license file content received from the F5 license server.

    show running-config system licensing

The rSeries system is licensed. The license applies to the system and tenants.

F5 r10000 platforms include two storage drives that support drive mirroring using a redundant array of independent disks (RAID) by default. You can manage the software RAID array from either the CLI or the webUI.

Important: If you need to swap out a faulty drive, you must first remove the drive from the software RAID array before physically removing the drive from the platform.

You can configure a software RAID (redundant array of independent disks) for the system from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > RAID Configuration.

  3. To remove a drive from the software RAID array:

    1. Select the drive to remove.

    2. Click Remove.

      When prompted, click OK to confirm drive removal.

  4. To add a drive to the software RAID array:

    1. Select the drive to add.

    2. Click Add.

      When prompted, click OK to confirm drive addition.

You can configure a software RAID (redundant array of independent disks) for the system from the CLI.

  1. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Change to config mode.

    config

    The CLI prompt changes to include (config).

  3. Remove a drive from the software RAID array.

    system raid remove drive ssd2

    A summary similar to this example displays:

    appliance-1(config)# system raid remove drive ssd2
    status Remove of RAID SSD2 initiated.
    [11084.434517] md/raid1:md121: Disk failure on nvme1n1p3, disabling device.
    [11084.434517] md/raid1:md121: Operation continuing on 1 devices.
    [11084.449528] md/raid1:md122: Disk failure on nvme1n1p4, disabling device.
    [11084.449528] md/raid1:md122: Operation continuing on 1 devices.
    [11084.464098] md/raid1:md123: Disk failure on nvme1n1p5, disabling device.
    [11084.464098] md/raid1:md123: Operation continuing on 1 devices.
    [11084.478342] md/raid1:md124: Disk failure on nvme1n1p1, disabling device.
    [11084.478342] md/raid1:md124: Operation continuing on 1 devices.
    [11084.492509] md/raid1:md127: Disk failure on nvme1n1p2, disabling device.
    [11084.492509] md/raid1:md127: Operation continuing on 1 devices.
    status Remove of RAID SSD2 initiated.					
  4. Add the replacement drive to the array.

    system raid add drive ssd2

    A summary similar to this example displays:

    appliance-1(config)# system raid add drive ssd2   
    status Add RAID SSD2 initiated.

    The array status for the new drive should change to replicating, and the STAT LED should change to solid green. The replication process typically takes between 15 and 45 minutes.

You can configure general system settings for the rSeries system, such as system hostname, login banner, and message of the day (MOTD) banner. Depending on which setting you want to configure, you can use either the CLI or the webUI.

You can configure the hostname, login banner, message of the day (MOTD) banner, and an advisory banner for the system from the webUI. When enabled and configured, the advisory banner will display at the top of the webUI after authentication.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > General.

  3. For Hostname, enter a custom hostname for the system.

  4. For Login Banner, enter any text to be shown when users log in to the system.

  5. For MOTD Banner, enter any text to be used as a MOTD when users log in to the system.

  6. For Advisory Banner, select Enabled or Disabled.

  7. For Advisory Banner Color, select the color for the banner.

  8. For Advisory Banner Text, enter the text for the banner. The maximum number of characters is 80.

  9. Click Save.

You can manually configure the hostname for your system from the CLI. F5 recommends you to configure a Fully Qualified Domain Name (FQDN) hostname.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Change the hostname.

    system config hostname <*hostname*>

    The minimum length is 1 character, and the maximum length is 253 characters.

    In this example, you change the hostname for the system to test.company.com:

    appliance-1(config)# system config hostname test.company.com

The system hostname is now updated.

You can configure the login banner for your system manually from the CLI. The login banner displays before users log in to each respective system.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Change the login banner text.

    system config login-banner

    Press Enter to enable multi-line mode and paste the contents. Press Ctrl-D to exit multi-line mode.

    In this example, you change the login banner text to indicate that unauthorized access is prohibited:

    appliance-1(config)# system config login-banner
    (<string>):
    [Multiline mode, exit with ctrl-D.]
    UNAUTHORIZED ACCESS TO THIS DEVICE IS PROHIBITED
  5. Commit the configuration changes.

    commit

The login banner is now updated.

You can configure the message-of-the-day (MOTD) banner for your system manually from the CLI. The MOTD banner displays after users log in to each respective system.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Change the MOTD banner text.

    system config motd-banner

    Press Enter to enable multi-line mode and paste the contents. Press Ctrl-D to exit multi-line mode.

    In this example, you change the login banner text to notify users of upcoming system maintenance:

    appliance-1(config)# system config motd-banner
    (<string>):
    [Multiline mode, exit with ctrl-D.]
    ATTENTION!
    This system is scheduled for maintenance in two days.
  5. Commit the configuration changes.

    commit

The MOTD banner is now updated.

You can verify the current MAC allocation data from the system controller CLI.

  1. Log in to the command line interface (CLI) of the system controller using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  2. Display the current MAC allocation data.

    show system mac-allocation

    A summary similar to this example displays:

    appliance-1# show system mac-allocation
    system mac-allocation state free-single-macs 17
    system mac-allocation state allocated-single-macs 3
    system mac-allocation state free-large-blocks 3
    system mac-allocation state allocated-large-blocks 0
    system mac-allocation state free-medium-blocks 0
    system mac-allocation state allocated-medium-blocks 0
    system mac-allocation state free-small-blocks 0
    system mac-allocation state allocated-small-blocks 0
    system mac-allocation state total-free-mac-count 113
    system mac-allocation state total-allocated-mac-count 3
    system mac-allocation state total-mac-count 116

If you are having an issue with the system (such as unusually high CPU or memory usage or lockup), it is possible that rebooting might help to resolve the issue.

When there is a problem, the system sends alerts that you would see on the dashboard or on the Alarms & Events screen. You should rarely have to reboot the system, however, because typically if the system needs to reboot, it will do so automatically without administrator intervention. F5 recommends working with customer support if you think a system reboot is necessary.

You can manually reboot the system from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Reboot the system.

    system reboot

    In this example, you reboot the system:

    appliance-1# system reboot
    The reboot of the system results in data plane and management connectivity 
    to be disrupted. Proceed? [no,yes]

It takes a few minutes for the system to reboot, and you will be logged out from the SSH session.

You can reboot the system from the webUI.

  1. Log in to the webUI using an account with admin access.

  2. On the left, click SYSTEM SETTINGS > General.

  3. Review the system status.

    The Reboot button will not be available if the system is currently being rebooted.

  4. If you decide that a reboot is necessary, in the System Operations & Status area, click Reboot.

    A popup displays asking you to confirm the reboot operation.

    It takes a few minutes for the system to reboot, and you will be logged out from the webUI.

OpenTelemetry streamlines observability in distributed systems through standardized APIs, libraries, and tools for collecting telemetry data, including traces, metrics, and logs.

F5OS OpenTelemetry enables the efficient collection of streaming metrics and logs in a structured format from the F5OS product to display in your observability platform. All the metrics and logs will be exported through a gRPC connection. The F5OS supports gRPC endpoints and each OpenTelemetry Line Protocol (OTLP) endpoint is provided with the ability to toggle instrument based filtering.

Telemetry subsystem within the F5OS platform layer generates common attributes and different metrics to display in your observability platform.

An instrument is an area of metrics, which contain multiple metrics and can be enabled selectively. F5OS Resource includes instruments.

The following tenant metrics are currently reported by the BIG-IP tenant into the F5OS platform layer. The metrics visible at the platform layer are only a limited subset of the total number of metrics available to the tenant. You can view the full tenant metrics by using the BIG-IP metric reporting capability.

F5OS OpenTelemetry exporter will only report the metrics that are associated with the Docker containers managed by the platform layer. For more information about the docker container metrics, see Docker stats documentation.

The platform hardware sensors represent physical sensors associated with the hardware which measure: temperature, current, power, voltage, RPM and percent humidity.

An instrument is an area of metrics, which contain multiple metrics and can be enabled selectively. F5OS Resource includes instruments.

Instument name Description
platform Standard platform stats such as memory, disk, CPU, and interface
tenant Tenant-initiated stats such as memory, disk, CPU, and interface
optics The front-panel optic DDM metrics
hardware The low-level platform hardware sensors
container Docker container stats for F5OS services
logs Export the platform log file

Note: Support for the intrument “tenant” is provided only for BIG-IP tenants.

This image provides a representation how the F5OS Resource includes instruments with multiple metrics:

The table lists the set of attributes that can be applied to all metrics produced by the platform.

The scope indicates which product the attribute applies to:

  • F5 - Applies to all metrics produced by F5
  • F5OS - Applies to all metrics produced by the F5OS product

Name

Value

Type

Scope

Description

dataType
f5os-analytics

string

F5

Attribute used by BIG-IP Central Manager to help direct F5OS specific metrics

f5.product
F5OS

string

F5

High level F5 product generating the metric/log

host.name
appliance-1

string

F5

otel.library.name
platform

string

F5

platform.serial_number
bldXXXXXXs

f5-AAAA-BBBB

string

F5

Serial number of an appliance, blade, or controller

platform.pid
C137

string

F5OS

The platform ID

platform.role
appliance

string

Role of the platform

instrument.name
<name>

string

F5OS

F5OS Instrument name associated with the metric

Metric Name

Metric Type

Value Type

Attributes

Unit

f5os.interface.packets
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
f5os.interface.packets
Counter
int64
interface.name="1.0"
direction="transmit"
{packets}
f5os.interface.bytes
Counter
int64
interface.name="1.0"
direction="receive"
Bytes
f5os.interface.bytes
Counter
int64
interface.name="1.0"
direction="transmit"
Bytes
f5os.interface.errors
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
f5os.interface.errors
Counter
int64
interface.name="1.0"
direction="transmit"
{packets}
f5os.interface.dropped
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
f5os.interface.dropped
Counter
int64
interface.name="1.0"
direction="transmit"
{packets}
f5os.interface.broadcast
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
f5os.interface.broadcast
Counter
int64
interface.name="1.0"
direction="transmit"
{packets}
f5os.interface.multicast
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
f5os.interface.multicast
Counter
int64
interface.name="1.0"
direction="transmit"
{packets}
f5os.interface.ethernet
Counter
int64
name="1.0"
direction="receive" 
state=<field>
{packets}
f5os.interface.ethernet
Counter
int64
name="1.0"
direction="transmit" 
state=<field>
{packets}

Reports the front-panel Optic DDM metrics.

Common Attributes include:

port.group=


    -   The F5OS port group name associated with the Optic
-   ``` {#codeblock_cld_wtz_z1c}
 port.name="1.0"..
-   The front-panel port number

channel=1..N


    -   For metrics which are per-channel, identifies the individual channel number
-   ``` {#codeblock_zkj_wtz_z1c}
direction="transmit" | "receive"
-   An indication of transmit or receive direction

Metric Name

Metric Type

Value Type

Attributes

Unit

f5os.optic.temperature
Gauge
float
port.group=<string>
port.name="1.0"
C
f5os.optic.voltage
Gauge
float
port.group=<string>
port.name="1.0"
V
f5os.optic.power
Gauge
float
port.group=<string>
port.name="1.0"
channel=1..N
direction="transmit" |  "receive"
dbm
f5os.optic.tx-bias
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
?
f5os.optic.los
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
direction="transmit" | "receive"
f5os.optic.tx-fault
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
direction="transmit" | "receive"

The schema of the CPU metrics is based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions

Metric Name

Metric Type

Value Type

Attributes

Unit

system.cpu.time
Counter
int64
cpu=cpu0..cpuN
thread=0...N
state=<field>
Seconds
system.cpu.utilization
Gauge
float64
pu=cpu0...cpuN
thread=0..N
state=<field>
{percent}

The Disk IO Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions

Metric Name

Metric Type

Value Type

Attributes

Unit

system.disk.io_time
Counter
float64
device=<name>
direction=total
Seconds
system.disk.operations
Counter
int64
device=<name>
direction=read
{operations}
system.disk.operations
Counter
int64
device=<name>
direction=write
{operations}
system.disk.io
Counter
int64
device=<name>
direction=read
Bytes
system.disk.io
Counter
int64
device=<name>
direction=write
Bytes
system.disk.merged
Counter
int64
device=<name>
direction=read
{operations}
system.disk.merged
Counter
int64
device=<name>
direction=write
{operations}
system.disk.operation_time
Counter
float64
device=<name>
direction=read
Seconds
system.disk.operation_time
Counter
float64
device=<name>
direction=write
Seconds
system.disk.usage
Counter
float64
device=<name>
Bytes

The Memory Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions

Metric Name

Metric Type

Value Type

Attributes

Unit

system.disk.usage
Counter
int64
state="<field>"
Bytes
system.disk.utillization
Gauge
float64
state=used
{percent}
system.disk.utillization
Gauge
float64
state=platform
{percent}
system.disk.utillization
Gauge
float64
state=available
{percent}

The following tenant metrics are currently reported by the BIG-IP tenant into the F5OS platform layer. The metrics visible at the platform layer are only a limited subset of the total number of metrics available to the tenant. You can view the full tenant metrics by using the BIG-IP metric reporting capability.

This table lists the attributes that are associated with the tenant-based metrics.

Metric Name

Metric Type

Value Type

Attributes

Unit

f5os.tenant.cpu.utilization
Gauge
float64
state="<field-name>"
cpu = cpuN
Percent
f5os.tenant.cpu.time
Couner
int64
state= "<field-name>"
cpi = cpuN
s

Metric Name

Metric Type

Value Type

Attributes

Unit

system.disk.utillization
Gauge
float64
state="<field>"
Percent
system.disk.usage
Gauge
int64
state="<field>"
Bytes

Metric Name

Metric Type

Value Type

Attributes

Unit

f5os.tenant.disk.operations
Counter
int64
device=<name>
direction=total
operation
f5os.tenant.disk.operations
Counter
int64
device=<name>
direction=read
operation
f5os.tenant.disk.operations
Counter
int64
device=<name>
direction=write
operation
f5os.tenant.disk.io
Counter
int64
device=<name>
direction=read
Bytes
f5os.tenant.disk.io
Counter
int64
device=<name>
direction=write
Bytes
f5os.tenant.disk.merged
Counter
int64
device=<name>
direction=read
operation
f5os.tenant.disk.merged
Counter
int64
device=<name>
direction=write
operation
f5os.tenant.disk.operation_time
Counter
float64
s
f5os.tenant.disk.operation_time
Counter
float64
s

Metric Name

Metric Type

Value Type

Attributes

Unit

f5os.tenant.interface.packets
Counter
float64
interface.name="<interface-name>"
direction="receive"
packets
f5os.tenant.interface.packets
Counter
int64
interface.name="<interface-name>"
direction="transmit"
packets
f5os.tenant.interface.bytes
Counter
int64
interface.name="<interface-name>"
direction="receive"
Bytes
f5os.tenant.interface.bytes
Counter
int64
interface.name="<interface-name>"
direction="transmit"
Bytes

F5OS OpenTelemetry exporter will only report the metrics that are associated with the Docker containers managed by the platform layer. For more information about the docker container metrics, see Docker stats documentation.

Attributes

Metric value type

Description

container.name
string

The name of the container

container.image.name
string

The container image name

Metric Name

Metric Type

Value Type

Attributes

Unit

container.cpu.usage
Gauge
float

s

ns
container.memory.<field-name>
Gauge
float
By
container.memory.<field-name>
Gauge
float
operation="read" | "write"
By
container.memory.percent
Gauge
float
interface=<name>
{percent}
container.blockio.io_service_bytes_recursive
Gauge
float
cpu=<name>
By
container.network.io.usage.<field-name>
Gauge
float
By | {percent}
container.cpu.percent
Gauge
float
{percent}

The platform hardware sensors represent physical sensors associated with the hardware which measure: temperature, current, power, voltage, RPM and percent humidity.

f5os.sensor.name=


    Eamples:

    -   Temperature:
        -   Inlet
        -   Outlet
        -   Central
    -   Voltage:
        -   12V
        -   3.3V BCM
    -   Current:
        -   12V Main
        -   Current In
    -   Power:
        -   Controller Power
        -   Total Power Supply Unit \(PSU\) Power In
        -   Total Power Supply Unit \(PSU\) Power Out
-   ``` {#codeblock_onv_mj1_1bc}
f5os.sensor.source=<component name>
Eamples:

-   psu-\[1..N\]
-   fantray-\[1..N\]
-   psu-controller-\[1..N\]
-   blade-\[1..N\]
-   controller-\[1..2\]
-   platform

Metric Name

Metric Type

Value Type

Attributes

Unit

f5os.sensor.temperature
Gauge
float64
f5os.sensor.name="<name of sensor>"
sensor.source="?<component name>"
C
f5os.sensor.voltage
Gauge
float64
f5os.sensor.name="<name of sensor>"
sensor.source="?<component name>"
V
f5os.sensor.current
Gauge
float64
f5os.sensor.name="<name of sensor>"
sensor.source="?<component name>"
A
f5os.sensor.power
Gauge
float64
f5os.sensor.name="<name of sensor>"
sensor.source="?<component name>"
W
f5os.sensor.humidity
Gauge
float64
f5os.sensor.name="<name of sensor>"
sensor.source="?<component name>"
{percent}
f5os.sensor.fan.speed
Gauge
float64
f5os.sensor.name="<name of sensor>"
sensor.source="?<component name>"
RPM

An instrument is an area of metrics, which contain multiple metrics and can be enabled selectively.

Before configuring an exporter, you can display supported instruments from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Show the total and available instruments:

    show system telemetry instruments

    This example displays the available instruments:

    appliance-1# show system telemetry instruments
    NAME           DESCRIPTION   
    -------------------------------------------------------------------------------------
    all            Report all logs and metrics produced by the F5OS platform layer
    logs           F5OS platform log file through the OpenTelemetry 'log' API
    platform       F5OS platform metrics such as: memory, disk, cpu, interface stats
    hardware       F5OS hardware sensors such as: voltage, current, temperature, power, fan-speeds
    optics         F5OS front-panel Optic DDM metrics
    tenant         Low level tenant reported metrics such as: memory, disk, cpu interface stats
    container      F5os Per-Container metrics such as: cpu, block-io, network, memory

An exporter defines an OpenTelemetry gRPC endpoint to which the F5OS Platform will push metrics/logs.

You can configure the exporter from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Configure the exporter.

    You must specify the IPv4 address or DNS name of the server and the port number of the server on which OpenTelemetry (OTEL) is running

    system telemetry exporters exporter <*server name*> config endpoint address <*address*> port <*port number*> instruments <*instrument name*>

    A summary similar to this example displays:

    appliance-1(config)# system telemetry exporters exporter server1 config endpoint address 10.144.74.171 port 4317 instruments platform
  5. Commit the configuration changes.

    commit

After you configure the exporter, you can display the state of the exporter from the CLI.

You can configure the exporter from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Display the state of a specific exporter:

    show system telemetry exporters exporter

    When you specify an exporter, a summary to this example displays:

    appliance-1# show system telemetry exporters
    system telemetry exporters exporter server1
    state enabled
    state endpoint address 10.144.74.171
    state endpoint port 4317
    state instruments [platform]
    state options retry-enabled true
    state options timeout 5
    state options compression gzip

You can modify the configuration of an exporter from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. You can use the following commands to modify the exporter configuration:

    • Disable the exporter

      system telemetry exporters exporter <*server name*> config disabled

      When you specify an exporter, a summary to this example displays:

      appliance-1(config)# system telemetry exporters exporter server1 config disabled
    • Modify option retry-enabled

      system telemetry exporters exporter <*server name*> config retry-enabled

      A summary to this example displays:

      appliance-1(config-exporter-server1)# system telemetry exporters exporter server1 config options retry-enabled
      Possible completions:
        false  true
      appliance-1(config)# system telemetry exporters exporter server1 config options retry-enabled false
    • Modify option timeout

      system telemetry exporters exporter server1 config options timeout <*new value*> 

      A summary to this example displays:

      appliance-1(config)# system telemetry exporters exporter server1 config options timeout 10
    • Modify option compression

      system telemetry exporters exporter server1 config options compression <*new value*>

      A summary to this example displays:

      appliance-1(config)# system telemetry exporters exporter server1 config options compression zstd
  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. You can verify the state of the exporter. see Display exporter state from the CLI.

You can add, modify, or delete the instruments that are configured for an exporter from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. You can use the following commands to modify the exporter configuration:

    • Add a new instrument

      system telemetry exporters exporter <*server name*> config instruments <*instrument name*>

      A summary to this example displays:

      appliance-1(config)# system telemetry exporters exporter server1 config instruments hardware
    • Modify the instrument

      system telemetry exporters exporter <*server name*> config instruments [<*instrument name*>]

      A summary to this example displays:

      appliance-1(config)# system telemetry exporters exporter server1 config instruments [ optics ]
    • Delete the instrument

      no system telemetry exporters exporter <*server name*> config instruments <*instrument name*>

      A summary to this example displays:

      appliance-1(config)# no system telemetry exporters exporter server1 config instruments platform
  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. You can verify the state of the exporter. see Display exporter state from the CLI.

  1. Connect using SSH to the management IP address.

  2. Log in to the command line interface (CLI) of the system using an account with admin access.

    When you log in to the system, you are in user (operational) mode.

  3. Change to config mode.

    config

    The CLI prompt changes to include (config).

  4. Delete the exporter:

    no system telemetry exporters exporter <*server name*>

    A summary similar to this example displays:appliance-1(config)# no system telemetry exporters exporter server1

  5. Commit the configuration changes.

    commit

  6. Return to user (operational) mode.

    end

  7. You can verify the state of the exporter. see Display exporter state from the CLI.