Manual Chapter : System Settings
Applies To:
  • F5OS-C
    1.8.3, 1.8.2, 1.8.1
System Settings
You can access system settings in the system controller webUI and chassis partition webUI. Each webUI provides different settings.
This table lists the available system settings in the system controller and chassis partition webUIs:
System controller webUI Chassis partition webUI
Alarms and Events Alarms and Events
Controller Management Cluster Details
System Inventory High Availability
Log Settings Log Settings
File Utilities File Utilities
Time Settings SNMP Configuration
SNMP Configuration Configuration Backup
Configuration Backup General
Licensing
Software Install Status
General
You can view active system alarms and events in the system controller webUI and CLI.
The Alarms & Events screen is available in both the system controller and chassis partition webUIs. This screen lists the alert information for all performance and network indicators that have currently crossed a performance or health threshold. Use this screen to identify the specific object that is affected.
  1. Log in to the VELOS system controller webUI or the chassis partition webUI using an account with admin access.
  2. On the left, click SYSTEM SETTINGS > Alarm & Events.
  3. Choose from one of these actions:
    • To refresh the alarms or events list, click the Refresh icon on the right of the screen.
    • To display events result by time preference, click the down arrow next to Refresh icon, select a value from the list. The default value is one hour. For example, select five minutes to display any event that occurred in the last five minutes.
    • To display events by severity, select a value from the Severity list. The default value is Informational.
      Option Description
      Emergency Emergency system panic messages
      Alert Serious errors that require administrator intervention
      Critical Critical errors, including hardware and file system failures
      Error Non-critical, but possibly important, error messages
      Warning Warning messages that should be logged and reviewed
      Notice Messages that contain useful information, but might be ignored
      Informational Messages that contain useful information, but might be ignored
      Debug Detailed messages used for troubleshooting
You can view information about active system alarm conditions from the system controller CLI.
  1. Connect using SSH to the system controller floating management IP address.
  2. Log in to the command line interface (CLI) of the system controller using an account with admin access.
    When you log in to the system, you are in user (operational) mode.
  3. View a list of active system alarm conditions.
    show system alarms | tab
    This example shows a power supply unit (PSU) redundancy fault:
    syscon-1-active# show system alarms
    ID     RESOURCE        SEVERITY  TEXT                           TIME CREATED
    65796  psu-controller  WARNING   PSU redundancy fault detected  2021-07-01-11:11:11.992270499 UTC
    65793  psu-2           ERROR     PSU fault detected             2021-07-01-11:11:11.999825828 UTC
You can configure system controller high availability (HA) from Controller Management screen on the system controller webUI. The system controllers work together as a redundant pair. The default mode for system controller HA is Auto, which automatically selects the system controller that is best suited at the time as the active controller and fails over only as needed.
The High Availability screen on the chassis partition webUI includes options for configuring chassis partition HA. High availability is already implemented for chassis partitions on the VELOS system.
You should not need to change system controller high availability (HA) to something other than the default configuration (Auto), but you can opt to change the configuration or initiate a failover from the active controller to the standby from the system controller webUI.
  1. Log in to the VELOS system controller webUI using an account with admin access.
  2. On the left, click SYSTEM SETTINGS > Controller Management.
  3. For the Preferred Node field, select System Controller 1 or System Controller 2 to act as an active system controller, or choose Auto (recommended).
    Note: Changing the Preferred Node configuration creates a failover event and ends the session if you select the system controller that is currently acting as the standby. Wait 30 seconds and then start a new session with either the floating IP address or the active system controller IP address after the change has completed.
    Hardware health conditions of the system controllers always take precedence. If one of the system controllers is not healthy, the chassis partition will ignore the preference and synchronize with the healthy system controller.
  4. To force a failover to occur immediately, click Failover.
    Note: The Failover button is available only when Preferred Node field is set to Auto.
    You would do this only if you want the current standby system controller to become the active system controller.
You can change the preferred system controller high availability (HA) mode from either the system controller or chassis partition CLI.
  1. Connect using SSH to the system controller floating management IP address or chassis partition management IP address.
  2. Log in to the command line interface (CLI) of the system controller or chassis partition using an account with admin access.
  3. Change to config mode.
    config
    The CLI prompt changes to include (config).
  4. Change system controller high availability/redundancy to a specified mode.
    system redundancy config mode [ auto | prefer-1 | prefer-2 }
    These redundancy modes are available:
    Option Description
    auto System chooses preferred mode automatically. This is the default value.
    prefer-1 Prefer controller-1 to be active.
    prefer-2 Prefer controller-2 to be active.
    This example shows configuring controller-1 as the preferred active system controller from the system controller CLI:
    syscon-1-active(config)# system redundancy config mode prefer-1
  5. Commit the configuration changes.
    commit
You can access settings for hardening the security of your system in the system controller or chassis partition webUI.
An allow list enables you to specify either specific IPv4 or IPv6 addresses, ports, or a netmask as an accepted source that can access the system.
When the IP address is configured and saved to the system allow list, only traffic coming from that IP address and port is accepted by the system’s management interface. You can also edit or delete entries in the allow list after you have configured them.
You can configure the system allow list from either the system controller or chassis partition webUI. To edit an existing allow list entry, select the IP address that you want to edit. You cannot change the designated name, but you can change all other fields.
  2. On the left, click SYSTEM SETTINGS > System Security.
  3. In the Allowed IP Addresses area, click Add to add an IP address to the allow list.
  4. For Name, enter a descriptive name for the IP address.
  5. For IPv4/IPv6, select IPv4 or IPv6.
  6. For Address, enter the IP address to be added to the allow list.
  7. For Prefix Length, enter or select the prefix length.
    The prefix length values must be between 1 and 32 for IPv4 and between 1 and 128 for IPv6.
  8. For Port, select a port number for the IP address.
    Available options are:
    • 443 (HTTPS): Allow only HTTP with SSL traffic on this IP address.
    • 80 (HTTP): Allow only HTTP traffic on this IP address.
    • 8888 (RESTCONF): Allow only RESTCONF traffic on this IP address.
    • 161 (SNMP): Allow only SNMP traffic on this IP address.
    • 7001 (VCONSOLE): Allow only VCONSOLE traffic on this IP address.
    • 22 (SSH): Allow only SSH traffic on this IP address.
  9. Click Save & Close.
You can configure the system allow list from either the system controller or chassis partition CLI.
  1. Log in to the command line interface (CLI) of the system controller or chassis partition using an account with admin access.
  2. Change to config mode.
    config
  3. Configure the system to allow traffic only from specified IP addresses.
    Note: This is applicable only for ports 22, 161, 8888, 443, 80, and 7001.
    system allowed-ips allowed-ip <*allowlist-profile-name*> config [ ipv4 | ipv6 ] address <*ip-address*> port <*port-number*> prefix-length <*subnet-prefix-length*>
    This example adds a specified IPv4 address to the system allow list:
    syscon-1-active(config)# system allowed-ips allowed-ip test config ipv4 address
    192.0.2.33 port 161 prefix-length 32
    This example adds a netmask to the system allow list:
    12.13.14.0 port 161 prefix-length 24
  4. Commit the configuration changes.
    commit
You can run the system in appliance mode. Appliance mode adds a layer of security removing user access to Root and Bash. Enabling appliance mode disables all Root and Bash shell access for the system.
You can enable appliance mode at each of these levels:
  • System
  • Tenant
Appliance mode is disabled at all levels, by default. You can enable it from the webUI or the CLI. The appliance mode option for the system is available to users with admin access under SYSTEM SETTINGS > General in the webUI. For tenants, it is available in the webUI under TENANT MANAGEMENT > Tenant Deployments.
These are the effects of enabling appliance mode at each of the different levels.
System-level appliance mode
  • Root or Bash access is disabled on the system.
  • Console access: Root or Bash access is disabled on the system. Users can log in to the system CLI from the console using an admin account.
Tenant appliance mode
  • Root access to the tenant is disabled by all means. Bash access is disabled for users (with a terminal shell flag enabled) inside the tenant.
  • Users can access the tenant only through the webUI or the CLI.
  • Tenant console access: Users can log in to the CLI from the virtual console using an admin account (with a terminal shell flag enabled).
You can enable appliance mode if you want to disable all root and Bash shell access.
Note: For greater security, it is highly recommended that you configure the system controllers and chassis partitions to run in appliance mode.
From the system controller webUI, appliance mode disables root and Bash access to the controllers. From the chassis partition webUI, appliance mode limits access to the specific chassis partition to which you are connected. You can enable or disable the appliance mode for system controllers and partitions from their respective webUIs.
Note: The appliance mode option for tenants is available in the chassis partition webUI under TENANT MANAGEMENT > Tenant Deployments.
  3. For Appliance Mode, in the Appliance Mode area, for Enable/Disable, select either Enabled or Disabled.
    The default value is Disabled.
  4. Click Save.
You can configure appliance mode from either the system controller or chassis partition CLI if you want to disable all root and Bash shell access.
From the system controller CLI, appliance mode disables root and Bash access to the controllers. From the chassis partition CLI, appliance mode limits access to the specific chassis partition to which you are connected.
Note: The appliance mode option for tenants is available in the chassis partition CLI using the tenants tenant <*tenant-name*> config appliance-mode command sequence.
    config
  4. Enable appliance mode.
    system appliance-mode config [ disabled | enabled ]
    In this example, you enable appliance mode on the system controllers:
    syscon-1-active(config)# system appliance-mode config enabled
    commit
With appliance mode disabled, enabling the deny root SSH option will restrict the root user from accessing the system through SSH. However, root users can still be able to access the system using the console. This provides a maintenance window for ‌system administrators without compromising on ‌system security through ‌SSH.
Note: All users excluding root users can access the system through SSH. If appliance mode is enabled, it overrides the deny root SSH option.
You can enable or disable root SSH from the webUI. Configuring deny root SSH to Enabled will disable the root SSH access but allows console root access.
  2. On the left navigation pane, click SYSTEM SETTINGS > System Security.
  3. In the Shell & LCD Access section, select either Enabled/Disabled from the Deny Root SSH field dropdown.
  4. Click Save.
You can configure deny root SSH mode from the CLI to disable the root SSH access. However, it allows console root access.
    config
  4. Disable appliance mode.
    In this example, you disable appliance mode on the system controllers:
    syscon-1-active(config)# system appliance-mode config disabled
  5. Enable deny root SSH mode.
    system security deny-root-ssh config [ disabled | enabled ]
    In this example, you enable deny SSH mode on the system controllers:
    syscon-1-active(config)# system security deny-root-ssh config enabled
  6. Commit the configuration changes.
    commit
Cryptographic agility on F5 VELOS systems enables you to replace cryptographic implementations for the httpd and sshd services. This applies to the F5OS management interface.
You can configure the sshd service from either the system controller or chassis partition CLI.
    config
  4. Configure the sshd service.
    system security services service sshd config ciphers [ <*string*> ] kexalgorithms [ <*string*> ] macs [ <*string*> ]
    These are the available configuration options:
Option
Description
ciphers
User-specified ciphers. For example, aes128-cbc or aes128-ctr.The cipher string can take several additional forms. It can consist of a single cipher suite or a list of cipher suites containing a certain algorithm, or cipher suites of a certain type. You can combine lists of cipher suites into a single cipher string using the + character as a logical AND operation.
kexalgorithms
User-specified key exchange algorithms. For example, diffie-hellman-group14-sha1 or diffie-hellman-group14-sha256.You can combine lists of KEX algorithms into a single string using the + character as a logical AND operation.
macs
User-specified MAC algorithms. For example, hmac-sha2-512 or AEAD_AES_128_GCM.You can combine lists of MAC algorithms into a single string using the + character as a logical AND operation.
This example shows configuring the sshd service:
syscon-1-active(config)# system security services service ssh config ciphers [ aes128-ctr aes256-cbc ]
  kexalgorithms [ ecdh-sha2-nistp521 echd-sha2-nistp384 ] macs [ hmac-sha1 ]
  1. Commit the configuration changes.
    commit
After you commit the change, you are prompted to confirm the change. The service will then restart.
You can configure the SSL cipher suites used for the httpd service from either the system controller or chassis partition CLI.
    config
  4. Configure one or more cipher suites for the httpd service.
    system security services service httpd config ssl-ciphersuite <*string*>
    In this example, you indicate that the system uses only the specified cipher suite:
    syscon-1-active(config)# system security services service httpd config
      ssl-ciphersuite ECDHE-RSA-AES256-GCM-SHA384
    In this example, you specify more than one cipher suite by separating the cipher suite names with a colon:
      ssl-ciphersuite ECDHE-RSA-AES128-SHA:ECDHE-RSA-AES256-SHA
    commit
When you configure ciphers for httpd, you can use multiple formats. You can specify a single cipher suite, such as RC4-SHA. You can also represent a list of cipher suites containing a certain algorithm or cipher suites of a certain type using a shortened name. For example, SHA1 represents all cipher suites using the digest algorithm SHA1, and SSLv3 represents all SSLv3 algorithms. You can combine lists of cipher suites into a single cipher string using the + character as a logical AND operation. For example, SHA1+DES represents all cipher suites containing the SHA1 and DES algorithms.
These are the allowed SSL cipher suites for general appliances:
  • ECDHE-RSA-AES256-GCM-SHA384
  • ECDHE-ECDSA-AES256-GCM-SHA384
  • ECDHE-RSA-AES256-SHA384
  • ECDHE-ECDSA-AES256-SHA384
  • DHE-DSS-AES256-GCM-SHA384
  • DHE-RSA-AES256-GCM-SHA384
  • DHE-RSA-AES256-SHA256
  • DHE-DSS-AES256-SHA256
  • DHE-RSA-CAMELLIA256-SHA
  • DHE-DSS-CAMELLIA256-SHA
  • ECDH-RSA-AES256-GCM-SHA384
  • ECDH-ECDSA-AES256-GCM-SHA384
  • ECDH-RSA-AES256-SHA384
  • ECDH-ECDSA-AES256-SHA384
  • AES256-GCM-SHA384
  • AES256-SHA256
  • AES256-SHA
  • CAMELLIA256-SHA
  • PSK-AES256-CBC-SHA
  • ECDHE-RSA-AES128-GCM-SHA256
  • ECDHE-ECDSA-AES128-GCM-SHA256
  • ECDHE-RSA-AES128-SHA256
  • ECDHE-ECDSA-AES128-SHA256
  • DHE-DSS-AES128-GCM-SHA256
  • DHE-RSA-AES128-GCM-SHA256
  • DHE-RSA-AES128-SHA256
  • DHE-DSS-AES128-SHA256
  • DHE-RSA-CAMELLIA128-SHA
  • DHE-DSS-CAMELLIA128-SHA
  • ECDH-RSA-AES128-GCM-SHA256
  • ECDH-ECDSA-AES128-GCM-SHA256
  • ECDH-RSA-AES128-SHA256
  • ECDH-ECDSA-AES128-SHA256
  • AES128-GCM-SHA256
  • AES128-SHA256
  • AES128-SHA
  • CAMELLIA128-SHA
  • PSK-AES128-CBC-SHA
These are the allowed SSL cipher suites for systems that have a FIPS software license applied. It does not apply to the F5 r5900-DF or r10900-DF platforms that have an embedded FIPS hardware security module (HSM).
When you configure ciphers for sshd, you enclose the cipher string in square brackets and include more than one by separating them with a space. These ciphers are allowed on the system.
  • ecdh-sha2-nistp256
  • ecdh-sha2-nistp384
  • ecdh-sha2-nistp521
  • diffie-hellman-group16-sha512
  • diffie-hellman-group14-sha256
  • diffie-hellman-group14-sha1
For security purposes, you can configure how long management sessions can remain idle before you are logged out of the system. If you are connected using an SSH connection, the system closes the SSH connection after this time expires.
You can configure how long management sessions can remain idle before you are logged out of the system from either the system controller or chassis partition webUI. If you are connected using an SSH connection, the system closes the SSH connection after this time expires.
  3. In the Services area, for CLI Idle Timeout, enter a time, in seconds, for how long management sessions can remain idle before they time out.
    A value of 0 (zero) sets the time to infinity, so the user is never logged out. The timeout can be a value from 0 through 8192 seconds. The default value is 1800 seconds (30 minutes).
  4. Click Save.
You can configure how long management sessions can remain idle before you are logged out of the system from the from either the system controller or chassis partition CLI. If you are connected using an SSH connection, the system closes the SSH connection after this time expires. You can also configure how long the system is inactive for a root user before the user is logged out of the system.
  3. Configure the CLI system idle timeout setting for an admin user connected to the system.
    system settings config idle-timeout <*time-in-seconds*>
    This example sets an idle timeout of 3600 seconds (one hour):
    syscon-1-active(config)# system settings config idle-timeout 3600
  4. Configure the SSH system idle timeout setting for a root user.
    system settings config sshd-idle-timeout <*time-in-seconds*>
    A value of 0 (zero) sets the time to infinity, so the user is never logged out. The timeout can be a value from 0 through 8192 seconds. The default value is 0 (zero).
    This example sets an SSH system idle timeout of 3600 seconds (one hour):
    syscon-1-active(config)# system settings config sshd-idle-timeout 3600
    commit
F5OS v1.8.3 includes the Linux Kernel Runtime Guard (LKRG) module to provide continuous runtime kernel integrity verification. LKRG monitors the running kernel for unauthorized modifications, rootkits, and privilege escalation attempts.
LKRG operates in observation mode in the current release — it detects and logs all security events without taking enforcement action. The system continues running normally, ensuring zero disruption from LKRG itself, while providing comprehensive observability through system logs (dmesg and /var/log/messages).
LKRG loads automatically at boot time after system network services are up, eliminating the need for manual configuration, and unloads cleanly before platform shutdown to avoid interference with legitimate kernel module operations. Designed to work at the F5OS platform level, LKRG does not impact tenant workloads.
LKRG is optimized for minimal performance impact, typically adding less than 1% overhead on standard workloads, ensuring efficient security monitoring.
You can verify its operational status by running the systemctl command in your terminal.
Deployment
LKRG is packaged as an RPM (lkrg.ko) built against kernel headers and included in the OS image.
Lifecycle Management
LKRG is loaded only after network services are up and is gracefully unloaded during shutdown.
Enforcement Parameters (Log-Only Mode)
Kernel Integrity (kint_enforce) and Process Credentials (pint_enforce) Violations: These are logged only, with no enforcement actions taken.
Example Commands to Validate LKRG Operations:
grep ‘^lkrg ’ /proc/modules — Validate module loading. sysctl -a | grep lkrg — Inspect LKRG configurations. systemctl is-active lkrg.service — Check LKRG service status.
Where LKRG logs events
LKRG logs all detected events to the following locations:
Log destination Description
dmesg (kernel ring buffer) Real-time kernel-level messages, including integrity violations and module lifecycle events
/var/log/messages Persistent log file. LKRG messages are forwarded from dmesg via rsyslog.
What LKRG monitors
Category What LKRG Checks
Kernel text integrity Detects unauthorized modifications to kernel code
Critical data structures Monitors kernel data structures for tampering
Process credentials Detects anomalous changes to process credentials that may indicate privilege escalation
Control flow integrity (CFI) Detects violations of expected kernel control flow
User mode helper (UMH) events Monitors kernel-initiated user space process execution
Interpret LKRG log messages
Log message Description and recommended action
“LKRG initialized successfully” LKRG loaded and is monitoring. No action required
“Kernel text integrity violation detected” Unauthorized modification to kernel code. Generate a QKView and contact F5 Support
“Process credentials anomaly detected” Potential privilege escalation. Generate a QKView and contact F5 Support
Note: If you see an LKRG alert, collect a qkview file and contact F5 Support.
In F5OS v1.8.3, Linux Kernel Runtime Guard (LKRG) is enabled by default to enhance system security by safeguarding kernel integrity. However, if LKRG causes boot failures or kernel panics due to incompatibilities, administrators can temporarily bypass LKRG by appending the nolkrg parameter to the kernel command line via the bootloader. This recovery-focused approach is intended for troubleshooting only, as real-time or manual configuration changes to LKRG are deliberately restricted to prevent potential weakening of system security controls.
  • LKRG operates in observation mode only. It does not block, prevent, or terminate processes or connections when a violation is detected. All events are logged for analysis.
  • LKRG is not a replacement for other security measures such as firewalls, access controls, or intrusion prevention systems. It provides an additional layer of kernel-level integrity monitoring. LKRG is not compatible with CrowdStrike Falcon. If Falcon is already running on the system, LKRG is automatically disabled.
  • LKRG log entries should be reviewed regularly as part of your security monitoring practices. Forward /var/log/messages to your Security Information and Event Management (SIEM) system for centralized monitoring.
  • If LKRG detects a kernel integrity violation, generate a QKView and contact F5 Support immediately.
The System Inventory screen on the system controller webUI enables you to see an inventory of all components on the VELOS system, including the system controllers, blades, power supply units (PSU), PSU controller, fan tray, and LCD. The inventory includes the component name, status, part number, and serial number.
You can view an inventory of all of the system components on the VELOS system, including the system controllers, blades, power supply units (PSU), PSU controller, fan tray, and LCD from the system controller webUI. The inventory includes the component name, status, part number, and serial number.
  2. On the left, click SYSTEM SETTINGS > System Inventory.
The system inventory displays, and you can review the information about the components on the VELOS system. An example is shown here.
You can view an inventory of all of the system components on the VELOS system, including the system controllers, blades, power supply units (PSU), PSU controller, fan tray, and LCD from the system controller CLI. The inventory includes the component name, status, part number, and serial number.
  3. View information about system components.
    Add a specific component to show information only about that component or omit it to show information about all components.
    show components component [ <*specific-component*> ]
    In this example, you view details only about the system storage:
    syscon-1-active# show components component storage
    components component controller-1
     storage state disks disk nvme0n1
      state model "SAMSUNG MZ1LB960HAJQ-00007"
      state vendor Samsung
      state version EDA7602Q
      state serial-no S123NA0NA04567
      state size 894.00GB
      state type nvme
     storage state disks disk sda
      state model DataTraveler
      state vendor Kingston
      state version 3.0
      state serial-no 0000000005??
      state size 28.00GB
      state type usb
    components component controller-2
      state serial-no S123NA0NA45678
      state size 894.00GB
      state type nvme
      state version 3.0
      state serial-no 000000000123
      state size 28.00GB
      state type usb
The webUI includessystem controller and chassis partition webUIs include options for configuring remote log servers and the log severity level for individual software components and services.
From the webUIwebUIs you can generate a system report, or QKView file, to collect configuration and diagnostic information from the VELOS system if you have any concerns about your system operation. The QKView file contains machine-readable (JSON) diagnostic data and combines the data into a single compressed tar.gz format file. You can upload the QKView file to F5 iHealth where you can get help to verify proper operation of the system and get help with troubleshooting and understanding any issues you might be having and ensure that the system is operating at its maximum efficiency.
You can view event logs and configure secure remote logging from the CLI. You can also send host log files, which are in the /var/log directory, as well as audit.log files to the remote server from the CLI.
You can add and display information about configured remote log servers from either the system controller webUIs. You can also change the log severity level for individual software components and services.
  1. Log in to the command line interface (CLI) of the system controller using an account with admin access.
  2. On the left, click SYSTEM SETTINGS > Log Settings.
  3. To include hostname configured for your system in the logs, select True from the Include Hostname field dropdown.
    Note: By default, the Include Hostname dropdown value is set to true.
  4. To add access to a Remote Log Server, click Add.
    1. In the Server field, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the remote server. After the remote log server is saved, you cannot modify the server address.
    2. In the Port field, enter the port number of the remote server.
      The default port value is 514.
    3. For Protocol, select UDP or TCP to choose between TCP or UDP input.
      Note: The Authenticationfield is displayed only when the TCP protocol is selected.
    4. From the Selectors field,
      • Select LOCAL0 or AUTHPRIV
      • From the Severity list, select the severity level of the messages to log
        Option Description
        Debug Verbose messages used for troubleshooting
      Note:
      To add more selectors, click the + button. To remove the existing selectors, select it and click the x button.
    5. For Authentication, select the enable or disable option from the list. The default value is Disabled. This option is visible when the TCP protocol is selected while configuring the remote log server. If the UDP protocol is selected, the authentication value is saved as N/A.
    6. Click Save & Close
  5. To delete a remote log server, select the server and click Delete.
  6. To view the Host Log Settings, click Show.
    1. For Host Log Forwarding, select the enable or disable radio button for remote forwarding. The default value is Disabled. When host log forwarding is enabled, the Include Standby Controller field displays.
    2. System Controller webUI: For Include Standby Controller, select true or false from the list to include the standby controllers and send the host log files to the active controller. The default value is False. This option is visible when the Host Log Forwarding option is enabled at the chassis level.
    3. Chassis Partition webUI: For Include Blades, select one or more blades from the list. This option is visible when the Host Log Forwarding option is enabled at the chassis partition level.
    4. For Selectors, select the required facility and severity options from the list. To add more selectors, click the add + icon. To remove the existing selectors, click the remove (X) icon.
    5. To add the required host log files to the Selected Files panel, click the required host log files checkboxes. Click on directories to view the files and sub-directories and select individual files within the directory.
      At the chassis partition level, you can only view the already selected and locked host files.
      The Selected Files option allows the host logs files to be forwarded from the directory and subdirectories.
    6. For Custom Log File, enter the log file in the text box and click Add to manually add host log file names to the Selected Files panel.
  7. For TLS Certificate & Key, click Show. It displays TLS Certificate and TLS Key options. If the authentication value is set as enabled for any of the remote log servers, you cannot be able to clear the TLS configuration fields.
  8. For CA Bundles, click Add to enter the name and TLS CA certificate. When any of the remote server authentication is enabled, you cannot delete the CA bundle.
  9. On the Log Settings screen, review the software component log levels for individual software components and adjust them as needed. Click Save if you made changes.
    The log levels determine at what level events (and all higher levels) are logged for each service. Informational is the default so all except debug-level events are logged.
Component
Description
alert-service
Software component that handles ‌alerts and events at the system level. These components use ConfD to process updates and manage the status of the Alarm LED depending on the severity of the alert.
api-svc-gateway
Software component that manages requests and subscriptions for Tenants on the appliance.
audit-service
Software component for capturing the system configuration related logs in audit log.
authd
Software component responsible for managing the configuration settings for various AAA (Authentication, Authorization, Accounting) mechanisms supported by the F5OS system.
dagd-service
Software component that manages the distribution of Tenant traffic.
datapath-cp-proxy
Software component that manages Tenant datapath setup requests and configuration.
diag-agent
The Diagnostic Agent is responsible for running various diagnostic profiles, gathering and exporting telemetry data and providing system health information and producing the hardware alerts.
diag-data
Software component for primarily tasked with collecting important information periodically from an F5OS device and sending that data back to F5 for analysis purposes.
disk-usage-statd
dma-agent
Software component for Core Offload feature that functions as a buffer broker, allowing multiple tenants to share access to the FPGA while remaining isolated from one another.
fips-service
Software component for System FIPS configuration and handles system integrity check requests.
firewall-manager
One software component that enables the setting up of a whitelist for designated source IP addresses and destination ports such as HTTP, HTTPS, RESTCONF, SNMP, and vConsole.
fpgamgr
Software component, which manages the datapath FPGAs. ‌This includes ‌front panel interfaces, L2 functionality, and other advanced FPGA features.
ihealth-upload-service
Software component for providing secure way of transporting support package to F5 to different target destination. This service offers historical track records of support package uploads with configurable data retention policy.
ihealthd
Software component responsible for handling ihealth configuration parameters and Start a qkview upload by sending a request to ihealth.
image-agent
A software module that manages the validation of imported tenant images and displays the current status of both tenant and platform images on the user interface.
kubehelper
Software component triggered during tenant deployment and runs as an assistant task before tenant container is created.
For BIG-IP
  • Covert qcow2 image to raw format for BIG_IP tenant only.
  • Reserves huge pages for the tenant.
  • Creates host-net interface for host and tenant communication purposes.
  • Creates a tenant management interface for BIG-IP NEXT tenants and includes route integration.
l2-agent
Software component responsible for managing the setup and status of physical connections (such as interfaces and portgroups) and the configuration and status of Layer-2 components (such as VLANs, LAGs, and FDB).
lacpd
Daemon responsible for negotiation of LACP over system interfaces.
license-service
Software component responsible for system licensing installation.
line-dma-agent
Software component which is an fundamental layer of tcpdump in the VELOS/rSeries family.
lldpd
Software component for LLDP configuration.
lopd
Software component to manage communication with the LOP (AOM).
network-manager
Software component responsible for managing datapath related resources, such as MAC Addresses. It also manages datapath tables that route traffic between Tenants and Interfaces.
node-agent
Software component triggered during tenant deployment and node reboots.
  • Adds water-marking rules for BIG-IP NEXT tenants.
  • In charge of allocating large pages for chassis during tenant deployments.
optics-mgr
Software component that is responsible for storing the tuning values for supported optics. When provided with an optic, returns the proper tuning.
orchestration-agent
Software component for Tenant Orchestration which includes tenant configuration and deployments.
partition-bladesd
Software component responsible for the peer enumerator service, creates a file containing a list of IP addresses for peers in a partition. Qkviewd uses the list of IP addresses for collecting peer qkviews. - The generated peer file is located in /var/F5/partitionX/qkviewd/peers, where X indicates the partition number.
  • This container is only relevant for partition qkviews. This container is not intended to be usable by you.
partition-common
Software component responsible for incorporating standard ConfD utility functions that enhance the CLI interface.
partition-ha
Systen partition software component responsible for Partition’s HA control framework.
partition-manager
System partition software component responsible for Partition’s instance of ConfD.
platform-diag
Software component for providing statistics reports and measurements on top of the low-level hardware.
platform-fwu
Software component responsible for updating and reporting firmware.
platform-hal
Software component that provides other services with access to platform/hardware data and configuration.
platform-mgr
This software component displays the versions of platform components, CPUs, memory, and firmware. It also automatically initiates firmware upgrades when upgrading or installing a new ISO and rebooting.
platform-monitor
Monitoring Agent is responsible for:
  • Creating telemetry pipelines that query data periodically.
  • Applying processors to the data.
  • Sending the data to various destinations.
platform-stats
Software component responsible for capturing the various utilization stats of the CPU, drives and memory and storing the data in TMSTAT stat tables.
platform-stats-bridge
Software components responsible for handling the platform statistics to display on user interfaces.
qat-confd-service
Service for communicating QAT device tenant assignments to ConfD tables.
qat-plugin
Kubernetes device plugin for reporting and managing QAT device resources and resource activities related to their respective tenant assignments.
qkviewd
Software component designed to create diagnostic snapshots in containerized systems, known as QKView. A QKView file is a compressed file with diagnostic info from containers, the host, and other systems.The main qkviewd service operates within a container, while qkviewd-host service collects data on the host. A peer system is another system running the qkviewd daemon.
rsyslog-configd
Software component for remote syslog configuration handling.
snmp-service
Software component used to configure system SNMP configuration such as community, target, and user.
snmp-trapd
Software component that process the system alerts/events as traps and sends it to SNMP manager.
sshd-crypto
Software component for handling sshd crypto agility configurations.
stpd
Software component for configuring STP L2 protocol in platform.
stream-generator
Software component provides the capability to produce independent streams of traffic, which can be directed anywhere in the chassis. This service can also connect to the dma-client unix pipes to manage ePVA information. Internally, the stream-generator can asynchronously read the FSC status messages and store the last value in a cache.
Key features of the stream generator:
  • The stream-generator utilizes the SEP Topology feature to connect to all 3 data-movers within the dma-agent. The stream can be configured to traverse a specific data-mover.
  • A stream can have a flexible transmit schedule.
  • The stream’s packet can be a generic MAC frame or it can also include IPv4 + UDP type traffic.
  • The stream’s packets can be a variable size.
  • The stream can be directed to any Destination ID in the chassis.
  • The stream-generator uses a fixed service-id == 6.
sw-rbcast
Software component that is responsible for forwarding broadcast traffic received on a shared VLAN to the tenants which share that VLAN. A secondary responsibility is to forward DLF (destination look-up failures) requests to the fpgamgr component, so that they can be resolved.
tcam-manager
tcpdumpd
Software component responsible for the tcpdump client daemon.
tcpdumpd-manager
Software component responsible for the tcpdump server daemon.
tmstat-agent
Software component for providing the framework which can be used to store the statistics data in centralized location on each host.
tmstat-merged
Software component for providing framework to integrate and divide statistics streams.
user-manager
Software component responsible for the management and configuration of local users on the system such as user accounts, groups/roles, and passwords.
utils-agent
Software component that manages file transfer operations such as import, export, delete, and download/upload.
vconsole
Software component for providing authenticated virtual console access to F5OS tenants.
  1. Click Save to save the log settings.
You can add and display information about configured remote log servers from chassis partition webUIs. You can also change the log severity level for individual software components and services.
  1. Log in to the command line interface (CLI) of the chassis partition using an account with admin access.
  5. In the Server field, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the remote server. After the remote log server is saved, you cannot modify the server address.
  6. In the Port field, enter the port number of the remote server.
  7. For Protocol, select UDP or TCP to choose between TCP or UDP input. When the TCP protocol is selected, the Authentication field displays.
  8. From the Facility list, select LOCAL0.
    F5OS supports only the LOCAL0 logging facility. All logs are directed to this facility, and it is the only one that you can use for remote logging.
  9. From the Severity list, select the severity level of the messages to log.
    Option Description
  10. For Authentication, select the enable or disable option from the list. The default value is Disabled. This option is visible when the TCP protocol is selected while configuring the remote log server. If the UDP protocol is selected, the authentication value is saved as N/A.
  11. Click Save & Close.
  12. To delete a remote log server, select the server and click Delete.
  13. To view the Host Log Settings, click Show.
  14. For Host Log Forwarding, select the enable or disable radio button for remote forwarding. The default value is Disabled. When host log forwarding is enabled, the Include Standby Controller field displays.
  15. System Controller webUI: For Include Standby Controller, select true or false from the list to include the standby controllers and send the host log files to the active controller. The default value is False. This option is visible when the Host Log Forwarding option is enabled at the chassis level.
  16. Chassis Partition webUI: For Include Blades, select one or more blades from the list. This option is visible when the Host Log Forwarding option is enabled at the chassis partition level.
  17. For Selectors, select the required facility and severity options from the list. To add more selectors, click the add + icon. To remove the existing selectors, click the remove (X) icon.
  18. To add the required host log files to the Selected Files panel, at the chassis level, click the required host log files checkboxes.
  19. For Custom Log File, enter the log file in the text box and click Add to manually add host log file names to the Selected Files panel.
  20. For TLS Certificate & Key, click Show. It displays TLS Certificate and TLS Key options. If the authentication value is set as enabled for any of the remote log servers, you cannot be able to clear the TLS configuration fields.
  21. For CA Bundles, click Add to enter the name and TLS CA certificate. When any of the remote server authentication is enabled, you cannot delete the CA bundle.
  22. On the Log Settings screen, review the software component log levels for individual software components and adjust them as needed. Click Save if you made changes.
Component
Description
alert-service
api-svc-gateway
audit-service
authd
dagd-service
datapath-cp-proxy
diag-agent
diag-data
disk-usage-statd
dma-agent
fips-service
firewall-manager
fpgamgr
ihealthd
image-agent
kubehelper
For BIG-IP
l2-agent
lacpd
license-service
line-dma-agent
lldpd
lopd
network-manager
node-agent
optics-mgr
orchestration-agent
partition-bladesd
Software component responsible for the peer enumerator service, creates a file containing a list of IP addresses for peers in a partition. Qkviewd uses the list of IP addresses for collecting peer qkviews.1. The generated peer file is located in /var/F5/partitionX/qkviewd/peers, where X indicates the partition number.2. This container is only relevant for partition qkviews.3. This container is not intended to be usable by customers.
partition-common
partition-ha
partition-manager
platform-diag
platform-fwu
platform-hal
platform-mgr
platform-monitor
platform-stats
qat-confd-service
qat-plugin
qkviewd
rsyslog-configd
snmp-service
snmp-trapd
sshd-crypto
stpd
stream-generator
sw-rbcast
tcam-manager
tcpdumpd
tcpdumpd-manager
tmstat-agent
tmstat-merged
user-manager
utils-agent
vconsole
The system logs events to the velos.log file located in the /var/log_controller directory. To list files and view the contents of log files, you use the file command from either the system controller or chassis partition CLI.
  3. List all files in the log directory.
    file list path [ log/confd/ | log/controller/ | log/host/ }
    This example shows an excerpt of the contents of the log/controller/ directory:
    syscon-1-active# file list path log/controller/
    entries {
        name afu-cookie
        date Wed Jun 15 19:52:37 UTC 2022
        size 33B
    entries {
        name cc-confd
        date Wed Jun 15 20:25:49 UTC 2022
        size 581KB
    entries {
        name cc-confd-hal
        date Wed Jun 15 19:52:10 UTC 2022
        size 0B
  4. Show the contents of a log file.
    file show [ log/confd/<*filename*> | log/controller/<*filename*> | log/host/<*filename*> ]
    This example shows the contents of the log/controller/velos.log file and uses the more option to paginate the output:
    syscon-1-active# file show log/controller/velos.log | more
    2022-04-21T08:18:28-07:00 localhost.localdomain notice boot_marker: ---===[ BOOT-MARKER ]===---
    2022-04-21T08:19:39-07:00 controller-1.chassis.local notice boot_marker: ---===[ BOOT-MARKER ]===---
    2022-04-21T15:27:39.925830+00:00 controller-1 alert-service[8]: priority="Notice" version=1.0 msgid=0x2201000000000001 msg="Alert Service Starting..." version="3.10.2" date="Fri Apr  8 09:42:10 2022".
    2022-04-21T15:27:39.926245+00:00 controller-1 alert-service[8]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
    2022-04-21T15:27:39.926264+00:00 controller-1 snmp-trapd[9]: priority="Notice" version=1.0 msgid=0x2101000000000007 msg="SNMP Trap Service Starting..." version="3.2.3" date="Fri Apr  8 09:43:28 2022".
    2022-04-21T15:27:39.926274+00:00 controller-1 alert-service[8]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
  5. Show only the most recent entries in a log file.
    file tail [ log/confd/<*filename*> | log/controller/<*filename*> | log/host/<*filename*> }
    This example shows the last ten lines of the velos.log file and uses the -f option to append output as the file grows:
    syscon-1-active# file tail -f log/controller/velos.log
    2022-06-16T23:24:36.170220+00:00 controller-1 switchd[8]: priority="Notice" version=1.0 container="VCC-SWITCHD" msgid=0x1001000000000485 msg="Linkstatus change" PORT="1/mgmt0" LINKSTAT="DOWN".
    2022-06-16T23:24:36.176481+00:00 controller-1 vcc-lacpd[82]: priority="Info" version=1.0 msgid=0x330100000000004e msg="" info_str="check_if_op_modify(): new oc_if_oper_status: 2 (1:UP  2:DOWN ... )".
    2022-06-16T23:24:36.176820+00:00 controller-1 vcc-lacpd[82]: priority="Info" version=1.0 msgid=0x330100000000004e msg="" info_str="check_if_op_modify(): new oc_eth_port_speed: ns: 1857063266 id: 1980508219 ".
    2022-06-16T23:24:36.267589+00:00 controller-1 switchd[8]: priority="Notice" version=1.0 container="VCC-SWITCHD" msgid=0x1001000000000485 msg="Linkstatus change" PORT="1/mgmt0" LINKSTAT="DOWN".
    2022-06-16T23:24:36.425971+00:00 controller-1 vcc-lacpd[82]: priority="Info" version=1.0 msgid=0x330100000000004e msg="" info_str="CCLacpdWriteHdlr::delete_member(memberName=1/mgmt0) from ConfD".
    2022-06-16T23:24:36.434091+00:00 controller-1 vcc-lacpd[82]: priority="Info" version=1.0 msgid=0x330100000000004e msg="" info_str="InterfaceCmObj::modifyOp: if_name=1/mgmt0 mode=FULL DUPLEX status=DOWN speed=10000#012".
    2022-06-16T23:24:36.434371+00:00 controller-1 vcc-lacpd[82]: priority="Info" version=1.0 msgid=0x330100000000004e msg="" info_str="InterfaceCmObj::modifyOp: if_name=1/mgmt0 mode=FULL DUPLEX status=DOWN speed=0#012".
    2022-06-16T23:25:09.324530+00:00 controller-1 platform-hal[8]: priority="Info" msg="NEBS is assumed to be true as chassis SEEPROM NEBS option couldn't be read" interface="job-2648493" apogeeUuid="a519fa20-ece4-11ec-a487-024264410634" $parent.jobId=0 $parent.apogeeUuid="a519fa20-ece4-11ec-a487-024264410634" $parent.treeUuid="90151e75-edcb-11ec-a487-024264410634" $parent.appKey="hal" actionKey="GET:chassis/nebs-capable" jobId=2648493 jobTreeUuid="90151e75-edcb-11ec-a487-024264410634"
    2022-06-16T23:25:09.399391+00:00 controller-1 platform-hal[8]: priority="Info" msg="NEBS is assumed to be true as platform SEEPROM NEBS option couldn't be read" interface="job-2648493" actionKey="GET:chassis/nebs-capable" jobId=2648493 jobTreeUuid="90151e75-edcb-11ec-a487-024264410634" apogeeUuid="a519fa20-ece4-11ec-a487-024264410634" $parent.jobId=0 $parent.apogeeUuid="a519fa20-ece4-11ec-a487-024264410634" $parent.treeUuid="90151e75-edcb-11ec-a487-024264410634" $parent.appKey="hal"
    2022-06-16T23:25:09.429431+00:00 controller-1 platform-hal[8]: priority="Info" msg="NEBS is assumed to be true as platform SEEPROM NEBS option couldn't be read" interface="job-2648493" actionKey="GET:chassis/nebs-capable" jobId=2648493 jobTreeUuid="90151e75-edcb-11ec-a487-024264410634" apogeeUuid="a519fa20-ece4-11ec-a487-024264410634" $parent.jobId=0 $parent.apogeeUuid="a519fa20-ece4-11ec-a487-024264410634" $parent.treeUuid="90151e75-edcb-11ec-a487-024264410634" $parent.appKey="hal"
    _
The system logs events to the velos.log file located in the /var/log_controller directory. To list files and view the contents of log files, you use the file command from the CLI.
    config
  4. Configure secure remote logging. The default value is disabled.
    system logging remote-servers remote-server <*name*> config proto <*proto*> remote-port <*port*> authentication { disabled | enabled }
    This example enables secure remote logging:
    syscon-1-active(config)# system logging remote-servers remote-server
      test config proto test2 remote-port 80 authentication enabled
  5. Add authentication details for secure remote logging.
    system logging remote-servers remote-server <*server-IP*> config authentication
  6. Add certificate or key details for secure remote logging.
    system logging tls { certificate | key } <*string*>
  7. Add CA bundle details for secure remote logging.
    system logging tls ca-bundles ca-bundle <*name*> config name <*name*> content <*ca-cert-contents*>
    Note:
    • The certificate bundle that you specify must include the certificate chain of the certificate authority.
    • When an incorrect TLS certificate or CA bundle is added for while configuring the secure remote logging, it results in the following errors:
      • Failure of remote log forwarding
      • Failure of local log writing
      • Failure of F5OS Logging
      • Failure of Qkview generation
  8. Remove authentication details from secure remote logging.
    no system logging remote-servers remote-server <*server-IP*> config authentication
  9. Remove certificate or key details from secure remote logging.
    no system logging tls { certificate | key } <*string*>
  10. Remove CA bundle details from secure remote logging.
    no system logging tls ca-bundles ca-bundle
  11. Send log files to the remote server.
    You can send host log files, which are in the /var/log directory, or audit.log files to the remote server
    system logging host-logs config files file <file-name>
  12. Commit the configuration changes.
    commit
  13. Return to user (operational) mode.
    end
  14. Show authentication, certificate, key, and CA bundle details.
    show running-config system logging tls { certificate | key | ca-bundles } <*string*>
You can use File Utilities to import, export, download, or delete files asynchronously depending on which directory you select to work in. All file transfers are done using the HTTPS protocol.
You can import a file from an external server into the system controller or chassis partition from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.
Note: If you want to import the contents of a tar file, you need to extract the contents first before you can import them onto the F5 system.
You can import files into these directories on a system controller :
  • images/staging
  • configs
You can import files into these directories on a chassis partition:
  • configs
  • images/import
  • images/staging
  • images/tenant
You can export a file from a system controller or chassis partition to an external server from either the webUI or the CLI. HTTPS is the supported protocol. The remote host should be an HTTPS server with PUT/POST enabled and have a valid CA-signed certificate.
You can export files in these directories from a system controller:
  • configs
  • log/confd
  • log/controller
  • log/host
  • diags/core
  • diags/crash
  • diags/shared
  • images/import
  • images/staging
You can export files in these directories from the chassis partition:
  • configs
  • diags/core
  • diags/shared
  • images
  • log
You can download files in these directories from a system controller to your local workstation from the webUI:
  • configs
  • diags/core
  • diags/crash
  • diags/shared
  • log/confd
  • log/controller
  • mibs
You can download files in these directories from a chassis partition to your local workstation from the webUI:
  • configs
  • diags/core
  • diags/shared
  • log
  • mibs
You can upload files in these directories from your local workstation to a system controller from the webUI:
  • configs
  • images/staging
You can upload files in these directories from your local workstation to a chassis partition from the webUI:
  • configs
  • images
You can delete files (to which you have file permissions) on a system controller or a chassis partition only from the diags/shared or configs directories from either the webUI or the CLI.
File Utilities are available in both the system controller and chassis partition webUIs. You can use File Utilities to import, export, download, upload, or delete files asynchronously depending on which directory you select to work in. All file transfers are done using the HTTPS protocol.
  2. On the left, click SYSTEM SETTINGS > File Utilities.
  3. From the Base Directory list, browse the directories and click subfolders to view their contents and the commands that are available from each one.
    From a subfolder, click the left arrow next to the path to navigate back to the main folder.
  4. To import a file, click Import.
    1. In the popup, enter the URL of the file to import.
    2. Provide the Username and Password only if required by the remote host.
    3. Select Ignore Certificate Warnings if you want to skip warnings when importing files (such as if the remote host does not have a valid CA-signed certificate).
    4. Click Import File to begin the import.
  5. To export a file, select the file and click Export.
    1. In the popup, enter the Server URL for where to export the file.
    3. Select Ignore Certificate Warnings if you want to skip warnings when importing files.
    4. Click Export File to begin the export.
  6. To upload a file:
    Click Upload and select the file you want to upload. The selected file will be uploaded.
  7. To download a file:
    1. Select the file and click Download.
      The selected file will be downloaded.
      On the system controller and chassis partition, you can delete files from diags/shared.
You can view the status of a file transfer operation to view its progress and see if it was successful. If you want to cancel the in-progress file transfer operation, click Cancel. If an operation fails, hover over the warning icon to see the error that occurred.
Note: A runtime error displays in the File Transfer status area, if an invalid operation is performed.
MIB files can be managed from the File Utilities page in both the system controller and chassis partition webUIs. You can use File Utilities to export or download MIB files. File transfers are done using the HTTPS protocol.
  3. From the Base Directory list, select mibs.
  4. To export a MIB file, select the file and click Export.
  5. To download a file:
    1. Select the file and click or Download.
You can view the contents of a file from either the system controller or chassis partition CLI.
  2. View the contents of a file.
    file show <*local-file-path*>
    This example shows how to view the contents of the velos.log file:
    default-1# file show log/velos.log
    2022-02-26T18:23:05.160009+00:00 controller-1(p1) partition-bladesd[7]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
    2022-02-26T18:23:05.161038+00:00 controller-1(p1) tcpdumpd-master[10]: priority="Notice" version=1.0 msgid=0x5402000000000002 msg="tcpdumpd-master starting" VERSION="1.3.18" DATE="Wed Feb 10 17:04:45 2021".
    2022-02-26T18:23:05.161047+00:00 controller-1(p1) tcpdumpd-master[10]: priority="Notice" version=1.0 msgid=0x5402000000000004 msg="tcpdumpd-master args." ARGS="/usr/bin/tcpdumpd_master".
    2022-02-26T18:23:05.161053+00:00 controller-1(p1) tcpdumpd-master[10]: priority="Notice" version=1.0 msgid=0x5402000000000004 msg="tcpdumpd-master args." ARGS="-r".
    2022-02-26T18:23:05.161057+00:00 controller-1(p1) tcpdumpd-master[10]: priority="Notice" version=1.0 msgid=0x5402000000000004 msg="tcpdumpd-master args." ARGS="1".
    2022-02-26T18:23:05.161062+00:00 controller-1(p1) tcpdumpd-master[10]: priority="Notice" version=1.0 msgid=0x5402000000000004 msg="tcpdumpd-master args." ARGS="-l".
    2022-02-26T18:23:05.161067+00:00 controller-1(p1) partition-bladesd[7]: priority="Info" version=1.0 msgid=0x6602000000000005 msg="DB is not ready".
You can import a file from an external serve onto your system from either the system controller or chassis partition CLI.
  2. Import a file.
    file import [ remote-port <*port-number*> } username <*user*> password <*password*> remote-host <*ip-address-or-fqdn*> remote-file <*remote-file-path*> remote-url <*full-remote-url*> local-file <*local-file-path*> [insecure] web-token <*remote-system-token*>
    Note: The insecure option ignores certificate warnings during the transfer.
    This example shows how to import a file to the system controller:
    file import username admin password remote-url
      https://files.company.com/images/BIGIP-1x.x.x.x-x.x.xxx.ALL-F5OS.qcow2.zip
      local-file images/staging
    This example shows how to import a file to the chassis partition:
      local-file images
    Note: When importing a file using the remote-url argument, you must wrap the URL in double quotes (""). This prevent special characters from being incorrectly interpreted as shell commands. For example: remote-url "https://example.com/file-path?params"
    Example: Transfer a file named {}myfile.iso{} from the remote URL https://files.example.com on port 443 to the images/staging directory on the system:
    file import local-file images/staging remote-url "https://files.example.com/images.myfile.iso" remote-port 443 protocol https
    end
  4. Optionally, you can check the file transfer status.
    file transfer-status file-name <*local-file-path*>
You can cancel an in-progress file import onto your system from either the system controller or chassis partition CLI.
  2. Get the operation identifier for the file transfer process.
    show file transfer-operations
    A summary similar to this example displays:
    syscon-1-active# show file transfer-operations
    file transfer-operations transfer-operation images/import/iso/F5OS-C-1.6.0-1234.CONTROLLER.iso
      files/F5OS-C/controller/images/F5OS-C-1.6.0-1234.CONTROLLER.iso "Import file" "HTTPS   "
     operation-id IMPORT-C16QYpun
     status       "In Progress (13.0%)"
     timestamp    "Fri Mar 24 23:05:54 2023"
  3. Cancel the specified file transfer.
    file abort-transfer operation-id <*id*>
    This example shows canceling a specified in-progress file transfer:
    syscon-1-active# file abort-transfer operation-id IMPORT-C16QYpun
    Aborting will stop the file transfer. Do you want to proceed? [yes/no] yes
    result File transfer abort operation initiated.
You can export files to an external server from your system from either the system controller or chassis partition CLI.
  2. Export a file.
    file export insecure local-file <*local-file-path*> protocol { https | scp | sftp } remote-file <*remote-file-path*> remote-host <*ip-address-or-fqdn*> remote-port <*port-number*> remote-url <*ip-address-or-fqdn*> username <*user*> web-token <*remote-system-token*>
You can delete files from either the system controller or chassis partition CLI.
  2. Delete a file.
    file delete file-name <*local-file-path*>
You can configure Network Time Protocol (NTP) for the VELOS system. An NTP server ensures that the system clock is synchronized with Coordinated Universal Time (UTC). The system also provides authentication support for NTP, which can enhance security by ensuring that the system sends time-of-day requests only to trusted NTP servers. You can also configure the time zone and set the time and date manually, if NTP is disabled. You can use either thesystem controller CLI or webUI to configure time settings.
After the VELOS system license is activated, you can configure Network Time Protocol (NTP) servers, including authentication support for NTP, time zone, and manual configuration of date and time, if NTP is disabled. The NTP server ensures that the system clock is synchronized with Coordinated Universal Time (UTC). You can specify a list of servers that you want the system to use when updating the time on network systems. You can configure time settings for the system from the system controller webUI.
  2. On the left, click SYSTEM SETTINGS > Time Settings.
  3. To synchronize the system clock with an NTP server, for NTP Service, select Enabled.
    The NTP Service is set to Disabled by default.
  4. To set the time and date manually:
    1. For NTP Service, select Disabled.
    2. In the Manual Time & Date Settings area, click the calendar to set the date and time.
  5. To use authentication support for NTP:
    1. For NTP Authentication, select Enabled.
      The NTP Authentication is set to Disabled by default.
    2. For NTP Keys, click Add.
      The Add NTP Key screen displays.
    3. For Key ID, type an identifier used by the client and server to designate a secret key.
      The client and server must use the same key ID.
    4. For Key Type, select the encryption type used for the NTP authentication key.
      The default value is F5_NTP_AUTH_SHA256.
      Select from these options:
      • F5_NTP_AUTH_MD5
      • F5_NTP_AUTH_SHA1
      • F5_NTP_AUTH_SHA256
      • F5_NTP_AUTH_SHA384
      • F5_NTP_AUTH_SHA512
    5. For Key Value, paste the text of the NTP authentication key.
    6. Click Save & Close.
  6. To specify an NTP server, from NTP Servers:
    1. Click Add.
    2. For NTP Server, type the IPv4 address, IPv6 address, or Fully Qualified Domain Name (FQDN) of the NTP server. This information will be displayed in the Name column of the table on the Time Settings screen.
      Note: If specifying an FQDN, you must configure a resolvable DNS server for the system. The resolved IP address will display in the NTP Server column of the table on the Time Settings screen. If the FQDN is unresolvable, this will be indicated in the NTP Server column, although this could be a transitional state.
      Note: If specifying an IPv4 or IPv6 address, the address will display in both the Name and the NTP Server columns.
    3. Set iburst Mode to True if necessary. By default, it is set to False.
    4. Select a Key ID, if you have defined an NTP key, select it from the list.
    5. Click Save & Close.
  7. To set the time zone, from Locations, select the time zone region.
  8. Click Save & Close.
You can manually configure the date and time for your system from the CLI.
  1. Connect using SSH to the system controller floating management IP address.
  2. Log in to the command line interface (CLI) of the system controller using an account with admin access.
    When you log in to the system, you are in user (operational) mode.
    config
  4. Change the system date and/or time.
    Note: You can opt to change only the time or only the date by including only the relevant option (either time or date).
    system set-datetime date <*YYYY-MM-DD*> time <*HH:MM-SS*>
    In this example, you change the system date to 2022-01-01 and the system time to be 12:01:00:
    syscon-1-active# system set-datetime date 2022-01-01 time 12:01:00
The system date and time are now updated.
You can configure Network Time Protocol (NTP) for your VELOS system from the system controller CLI.
Note: If you want to enable NTP authentication, see Configure NTP authentication from the CLI.
    config
  4. Enable NTP.
    system ntp config enabled
  5. Add an NTP server.
    system ntp servers server <*ip-address*>
    In this example, you configure an NTP server at pool.ntp.org:
    syscon-1-active(config)# system ntp servers server pool.ntp.org
    commit
  7. Return to user (operational) mode.
    end
  8. Verify that NTP is enabled and a server is configured.
    syscon-1-active# show system ntp
     system ntp state enabled
     system ntp state enable-ntp-auth false
     state address    pool.ntp.org
     state port       123
     state version    4
     state association-type SERVER
     state iburst     false
     state prefer     false
     state stratum    4
     state root-delay 32
     state root-dispersion 45
     state offset     0
     state poll-interval 8
     state authenticated false
You can configure Network Time Protocol (NTP) authentication for your VELOS system from the system controller CLI. NTP authentication enhances security by ensuring that the system sends time-of-day requests only to trusted NTP servers.
    config
  4. Enable NTP.
  5. Enable NTP authentication.
    system ntp config enable-ntp-auth true
  6. Add the key associated with your server to the system.
    system ntp ntp-keys ntp-key <*public-key-id*> config key-id <*secret-key-id*> key-type [ F5_NTP_AUTH_MD5 | F5_NTP_AUTH_SHA1 | F5_NTP_AUTH_SHA256 | F5_NTP_AUTH_SHA384 | F5_NTP_AUTH_SHA512 ] key-value HEX:<*ntp-auth-key-value*>
    Important: The ID, key type, and key value on this client system must match the server exactly.
    syscon-1-active(config)# system ntp ntp-keys ntp-key 11
      config key-id 11 key-type F5_NTP_AUTH_SHA1 key-value
      HEX:E27611234BB5E7CDFC8A8ACE55B567FC5CA7C890
  7. Add an NTP server and associate the key ID you added with the server.
    In this example, you configure an NTP server at the IP address pool.ntp.org:
    syscon-1-active(config-server-pool.ntp.org)# config key-id 11
  8. Commit the configuration changes.
    commit
  9. Return to user (operational) mode.
    end
  10. Verify that NTP with authentication is enabled and a server is configured.
    syscon-1-active# show system ntp servers
     state port       123
     state version    4
     state iburst     false
     state prefer     false
     state stratum    8
     state root-delay 0
     state root-dispersion 0
     state offset     251333
     state poll-interval 6
     state key-id     11
     state authenticated true
Simple Network Management Protocol (SNMP) is an industry-standard protocol that enables you to use a standard SNMP management system to remotely manage network devices. F5 VELOS systems support SNMPv1, SNMPv2c, and SNMPv3. You can configure the system from both the CLI and webUI.
You can use SNMP to monitor VELOS systems at both the system controller and chassis partition levels. For more comprehensive monitoring, configure your system at both levels from the CLI or webUI. SNMP traps always send from the active system controller’s fixed management IP address as the source IP address.
SNMP support is available in different ways, depending on which F5OS software version you are using. On VELOS systems, SNMP is available from both the system controller and chassis partition CLIs and webUIs.
F5 recommends using the newer system snmp commands, which include support for SNMP versions 1, 2c, and 3. For more information on the older commands, see:
F5OS-C software version
Older CLI (v1/v2c only)
Newer CLI (v1/v2c/v3)
webUI
1.5.0
SNMP-COMMUNITY-MIB
SNMP-NOTIFICATION-MIB
SNMP-TARGET-MIB
SNMP-VIEW-BASED-ACM-MIB
SNMPv2-MIB
system snmp communities system snmp engine-id
system snmp targets
system snmp users
SYSTEM SETTINGS > SNMP Configuration
Before you configure SNMP access for VELOS systems:
  • Add the SNMP manager IP address to the system allow list. For more information, see Allow list overview.
  • Add descriptions to front-panel interfaces. For more information, see Configure an interface from the CLI.
  • Add descriptions to management interfaces. For more information, see Configure management IP addresses from the CLI.
  • Add descriptions to LAGs, if needed. For more information, see Configure a static LAG interface from the CLI.
  • Download the F5 MIB files from File Utilities in the system controller or chassis partition webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select mibs, select a .tar.gz file, and click Download).
  • Configure a DNS name server if you would like to use a fully-qualified domain name (FQDN) instead of an IP address for the SNMP trap destination. For more information, see Configure DNS from the webUI.
You can view SNMP information in the /log/system/snmp.log file. You can download the log file to your local workstation from the File Utilities screen in the system controller or chassis partition webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select log/system, select snmp.log, and click Download).
For more information about managing files from the system controller or chassis partition webUI or CLI, see File utilities overview.
SNMPWALK is an application on an SNMP management system that performs SNMP GETNEXT requests to query a network device for information. You can provide an object identifier (OID) to specify which portion of the object identifier space to search using GETNEXT requests. The SNMP management system queries all variables in the subtree below the specified OID, displays these values to the user, and stops when it returns results that are no longer inside the range of the specified OID.
These SNMP system object IDs (OIDs) are defined for each F5 VELOS system type:
  • 1.3.6.1.4.1.12276.1.3.1.1 (f5OsAppR5x00)
  • 1.3.6.1.4.1.12276.1.3.1.2 (f5OsAppR10x00)
  • 1.3.6.1.4.1.12276.1.3.1.3 (f5OsAppR2x00)
  • 1.3.6.1.4.1.12276.1.3.1.4 (f5OsAppR4x00)
The IDs display in text format when the corresponding MIB is loaded in your SNMP management system. If the MIB is not loaded, the walk displays in OID format.
To more accurately map these system OIDs, you must download the F5-OS-SYSTEM-MIB.mib file and load it into your SNMP management system. To download the F5 MIB files, use File Utilities in the system controller or chassis partition webUI (on the left, click SYSTEM SETTINGS > File Utilities, and then from Base Directory, select mibs, select a .tar.gz file, and click Download).
You can configure the SNMP port from the webUI.
  1. Log in to the VELOS system controller webUI or the chassis partition webUI using an account with admin access.
  2. On the left, click SYSTEM SETTINGS > SNMP Configuration.
  3. For Port, enter the required value. The allowed values for the Port are either 161 or in the ranges of [1024-7000, 7033-8887, 8889-65535]. To check whether a port is valid or not, we have inline validation.
    Note: The port configured in the SNMP Configuration area is reflected on the Allow List Entry screen of the Allowed IP Addresses section under System Security in the System Settings chapter. When an allowlist is created with an SNMP port, the user is not allowed to change the SNMP Port on the SNMP Configuration area, which can cause an error. For more information, see Configure the system allow list from the webUI.
  4. Click Save & Close.
You can configure the SNMP properties from the webUI.
  3. Under the Properties area, enter values in the required fields.
    • System Contact
    • System Location
    • System Name Note: The maximum number characters limit is 255.
You can configure SNMP communities with either version 1, version 2c, or both security models from either the system controller or chassis partition webUI.
  3. In the Communities area, click Add.
    The Add Community screen displays.
  4. For Community, enter a descriptive name.
  5. For Security Model, select from these security models: v1, v2c, and v1 and v2c.
You can configure SNMP version 3, which is a user-based security model, from either the system controller or chassis partition webUI. This model provides support for additional authentication and privacy protocols.
  3. In the Users area, click Add.
    The Add V3 User screen displays.
  4. For User, enter the user name.
  5. For Authentication Protocol, select from these protocols: MD5, SHA, or None.
  6. For Authentication Password, enter the password for the specified user.
  7. For Privacy Protocol, select from these protocols: AES128, DES, or None.
Before you can add an SNMP target, you must have already configured either the SNMPv1/v2c community or SNMPv3 user.
You can configure SNMP targets from either the system controller or chassis partition webUI. These are required to send system-generated traps to a manager. You can choose either community (v1/v2c) or user-based (v3) security.
  3. In the Targets area, click Add.
    The Add Target screen displays.
  4. For Name, enter a descriptive name.
  5. For Security Model, select from these security models: v1, v2c, or v3.
  6. Select one of these options, depending on the selected security model:
    • If you select v1 or v2, for Community, select the community that you created.
    • If you select v3, for User, select the user that you created.
  7. For IPv4/IPv6, select either IPv4 or IPv6.
  8. For Name, enter the IPv4 address, IPv6 address, or fully qualified domain name (FQDN) of the target.
  9. For Port, enter the port number for the target.
    The default value is 162, and the range is from 1024 to 65535
  10. Click Save & Close.
You can configure the SNMP port from the CLI.
  1. Connect using SSH to the system controller floating management IP address or chassis partition management IP address.
  2. Log in to the command line interface (CLI) of the system controller or chassis partition using an account with admin access.
  3. Change to config mode.
    config
    The CLI prompt changes to include (config).
  4. Configure SNMP port
    system snmp config port <*value*>
    The following example configures SNMP port ‘5000’:
    syscon-1-active(config)# system snmp config port 5000
    Note: The allowed values for the Port are either 161 or in the ranges of [1024-7000, 7033-8887, 8889-65535]. The port configured in the SNMP Configuration area is reflected on the Allow List Entry screen of the Allowed IP Addresses section under System Security in the System Settings chapter. When an allowlist is created with an SNMP port, the user is not allowed to change the SNMP Port in the SNMP Configuration area, which can cause an error. For more information, see Configure the system allow list from the webUI
  5. Commit the configuration changes.
    commit
You can configure the SNMP properties from the CLI.
  1. Log in to the command line interface (CLI) of the system controller or chassis partition using an account with admin access.
  2. Change to config mode.
    config
  3. Configure SNMP properties
    SNMPv2-MIB system sysName <*system name*> sysLocation <*location name*> sysContact <*contact details*>
    A summary of this example displays:
    syscon-1-active(config)# SNMPv2-MIB system sysName f5System sysLocation boston sysContact support@f5.com
  4. Commit the configuration changes.
    commit
You can configure SNMP communities with either version 1, version 2c, or both security models from either the system controller or chassis partition CLI.
    config
  4. Configure a community.
    system snmp communities community <*community-name*> | config security-model { v1 | v2c }
    This example creates a community that uses the v2c security model:
    syscon-1-active(config)# system snmp communities community v2comm config
      security-model v2c
    This example creates a community that uses both v1 and v2c community models:
    syscon-1-active(config)# system snmp communities community v1v2c config
      security-model [ v1 v2c ]
    commit
  6. Return to user (operational) mode.
    end
  7. Verify the community configuration.
    show system snmp communities
    syscon-1-active# show system snmp communities
                          SECURITY
    NAME       NAME       MODEL
    v1v2c      v1v2c     [ v1 v2c ]
    Note: This example shows both security models configured. If you configure only one security model, then only the configured model displays in the output.
You can configure SNMP version 3, which is a user-based security model, from either the system controller or chassis partition CLI. This model provides support for additional authentication and privacy protocols.
    config
  4. Configure a user, including authentication and privacy protocols.
    system snmp users user <*user-name*> config authentication-protocol config { md5 | none | sha } privacy-protocol { aes | des | none }
    This example creates a user that uses MD5 authentication and AES for password authentication:
    syscon-1-active(config)# system snmp users user jdoe config
      authentication-protocol md5 privacy-protocol aes authentication-password
    After you press Enter, you are prompted to enter the authentication password.
    (<string, min: 8 chars, max: 32 chars>): ********
    After you press Enter, configure the privacy password.
    syscon-1-active(config-user-v3-user)# config privacy-password
    After you press Enter, you are prompted to enter the privacy password.
    (<string, min: 8 chars, max: 32 chars>): *********
    commit
    end
  7. Verify the user configuration.
    show system snmp users
    syscon-1-active# show system snmp users
                      AUTHENTICATION  PRIVACY
    NAME     NAME     PROTOCOL        PROTOCOL
    jdoe     jdoe     md5             aes
You can configure SNMP targets with community-based security (SNMPv1/SNMPv2c) from either the system controller or chassis partition CLI. These are required to send system-generated traps to a manager.
    config
  4. Configure a target with community-based security.
    system snmp targets target <*target-name*> config community <*community-name*> security-model { v1 | v2c } { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>
    This example creates a target with community-based security:
    syscon-1-active(config)# system snmp targets target v2c-target config community v2c-comm
      security-model v2c ipv4 address 192.0.2.24 port 5001
    commit
    end
  7. Verify the target configuration.
    syscon-1-active# show system snmp targets
                                              SECURITY
    NAME       NAME       USER     COMMUNITY  MODEL     ADDRESS         PORT  ADDRESS  PORT
    v2c-target v2c-target jdoe     -          -         192.0.2.24      5001  -        -
You can configure SNMP targets with user-based security (SNMPv3) from either the system controller or chassis partition CLI. These are required to send system-generated traps to an SNMP management system.
    config
  4. Configure a target with user-based security.
    system snmp targets target <*target-name*> config user <*user-name*> { ipv4 | ipv6 } address <*ip-address*> port <*port-number*>
    This example creates a target with user-based security:
    syscon-1-active(config)# system snmp targets target v3-target
      config user jdoe ipv4 address 192.0.2.24 port 5001
    commit
    end
                                              SECURITY
    v3-target  v3-target  jdoe     -          -         192.0.2.24      5001  -        -
You can back up the configurations of the system controller or chassis partition in which you are working from the webUI.
  2. On the left, click SYSTEM SETTINGS > Configuration Backup.
  3. Click Create.
    The Create Configuration Backup popup opens.
  4. In the Name field, enter a name for the backup (for example, system-controller-12-21-21 or partition1-6-14-21).
  5. Click Create.
    The backup is created and added to the list.
  6. To delete a backup file, select the file and click Delete.
System controller and chassis partition configuration backups are stored in configs/. Backups should be stored off the system.
You can restore configurations from the CLI. For more information on saving and restoring the configuration, see the Complete backup and restore overview section.
You can activate a license for the VELOS system from either the system controller CLI or webUI. There is one license per VELOS system, which is used by the chassis partitions and any tenants.
You can activate a license for the VELOS system from either the CLI or webUI. There is one license per VELOS system, which is also used by any tenants.
There are two ways to license the system:
If your system is connected to the internet, use the Automatic method to prompt the system to contact the F5 license server and activate the license.
If your system is not connected to the internet, use a management workstation that is connected to the internet to retrieve an activation key from F5 and then transfer it to the system.
Important:
Adding or reactivating a license on an active VELOS system might impact traffic on tenantsrunning on chassis partitions. Traffic processing will stop briefly on the tenants, and then restart automatically. This occurs when the tenant receives a new or reactivated license causing a configuration reload on the tenants. For more information, see these other references:
You can license the system automatically from the webUI, as long as the system has internet access.
  1. Log in to the VELOS system controller webUI using an account with admin access.
  2. On the left, click SYSTEM SETTINGS > Licensing.
  3. For the Base Registration Key field, the registration key is auto-populated.
    You can choose to overwrite this field with a new registration key.
  4. For the Add-On Keys field, the associated add-on keys are auto-populated.
    You can click + or x to add or remove additional add-on keys.
    Note: To add add-on keys to a licensed system, enter the keys in the Add-On Keys field and click Reactivate.
  5. For the Activation Method, select Automatic.
  6. Click Activate.
    The End User License Agreement (EULA) displays.
  7. Click Agree to accept the EULA, .
The system is now licensed. If a base registration key or add-on key fails to activate, try re-activating the license or contact support.f5.com.
You can use the system controller webUI to manually license the VELOS system for systems without access to the internet.
  5. For the Activation Method, select Manual.
  6. For the Device Dossier, click Get Dossier.
    The VELOS system refreshes and displays the dossier.
  7. Copy the dossier text into the Device Dossier field.
  8. Click Click here to access F5 Licensing Server.
    The Activate F5 Product page displays.
  9. Paste the dossier in the Enter Your Dossier field.
  10. Click Next.
    The license key text displays.
  11. Copy the license key text.
    Alternatively, you can use the F5 license activation portal at activate.f5.com/license.
  12. In the License Text field, paste the license key text.
  13. Click Activate.
  14. Click Agree to accept the EULA.
You can view information about the software license activated on your system, including license activation and expiration dates, service check date, and licensed modules, from either the system controller or chassis partition webUIs.
  3. View the license information for the system.
For automatic VELOS system licensing, the system needs to be able to connect to the F5 licensing server either through the internet or another means of networking. You need to have the Base Registration Key (five sets of characters separated by hyphens) provided by F5, and any add-on keys (two sets of 7 characters separated by a hyphen) that you have purchased. The Base Registration Key with associated add-on keys are pre-installed on a new VELOS system.
You can activate the VELOS system license automatically from the system controller CLI.
    config
  4. Apply a license to the chassis.
    system licensing install registration-key <*key*>
    The registration key is optional. If it is not included, the system uses the one that is already pre-installed. If no registration key is found, you receive an error.
    This example applies a specified base registration license to the system:
    syscon-1-active(config)# system licensing install registration-key
     I1234-12345-12345-12345-1234567
    result License installed successfully.
  5. Apply any add-on keys.
    system licensing install add-on-keys <*add-on-keys*>
    This example enables the additional features associated with the three specified add-on-keys, along with the entitlements of the base registration key:
     add-on-keys [1234567-1234567 2345678-2345678 3456789-3456789]
The VELOS system is licensed. The license and any add-on keys apply to all partitions and tenants.
You can activate the VELOS system license manually from the system controller CLI.
    config
  4. Get the system dossier.
    system licensing get-dossier [registration-key XXXXX-XXXXX-XXXXX-XXXXX-XXXXXXX]
    The registration key is optional. If it is not included, the system uses the one already pre-installed. If no registration key is found, you receive an error.
    The dossier for the system displays.
  5. Get the license file using the dossier output you just received by going to the F5 siteactivate.f5.com/license/dossier.jsp.
  6. Install the license.
    1. Copy the license file text.
    2. Run the manual install command and press Enter:
      system licensing manual-install license
    3. Paste the license file content in multiline mode, then press Ctrl+D.
    syscon-1-active(config)# system licensing manual-install license
    Value for 'license' (<string>):
    [Multiline mode, exit with ctrl-D.]
The VELOS system is licensed. The license applies to all of the chassis partitions and tenants.
For automatic VELOS system licensing, the system needs to be able to connect to the F5 licensing server either through the Internet or another means of networking. You need to have the Base Registration Key (five sets of characters separated by hyphens) provided by F5, and any add-on keys (two sets of 7 characters separated by a hyphen) that you have purchased. The Base Registration Key with associated add-on keys are pre-installed on a new VELOS system.
You can activate the VELOS system license automatically from the CLI.
    config
  4. Apply a license to the system.
    system licensing install registration-key <*key*> proxy-server <*protocol://domain name:port*> proxy-username <*name*> proxy-password <*input*>
    syscon-1-active(config)# system licensing install registration-key Y0922-72141-80658-12653-0642460 proxy-server http://192.0.2.20:3128 proxy-username root proxy-password
    Value for 'proxy-password' (<AES encrypted string>): *******
The VELOS system is licensed with proxy server. The license and any add-on keys apply to the system and all tenants.
You can display the license of a VELOS system from the system controller CLI.
  3. Display the system license in a simple form.
    show system licensing
    syscon-1-active# show system licensing
     system licensing license
            Licensed version    7.4.0
            Registration Key    Gxxxx-xxxxx-xxxxx-xxxxx-xxxxxxxx
            Licensed date       2021/01/01
            License start       2021/04/16
            License end         2022/01/01
            Service check date  2021/12/02
            Platform ID         F101
            Appliance SN        chs600144s
            Active Modules
            Local Traffic Manager, CX410 (Exxxxxx-xxxxxx)
            Best Bundle, CX410
            APM-Lite
            Carrier Grade NAT (AFM ONLY)
            Max Compression, CX410
            Rate Shaping
            Max SSL, CX410
            Advanced Firewall Manager, CX410
            Access Policy Manager, Base, CX410
            Anti-Virus Checks
            Base Endpoint Security Checks
            Firewall Checks
            Machine Certificate Checks
            Network Access
            Protected Workspace
            Secure Virtual Keyboard
            APM, Web Application
            App Tunnel
            Remote Desktop
            Advanced Routing, CX410
            Advanced Web Application Firewall, CX410
            DNS, Max QPS, CX410
  4. Display the raw license file content that was received from the F5 license server.
    show running-config system licensing
A cluster on a VELOS system is group of blades or nodes working together as a logical unit. The Cluster Details screen on the chassis partition webUI provides detailed information about clusters that might be useful when a chassis partition is made up of more than one slot/blade.
You can view detailed information about clusters from the chassis partition webUI.
  1. Log in to the VELOS chassis partition webUI using an account with admin access.
  2. On the left, click SYSTEM SETTINGS > Cluster Details.
  3. Set the Auto Refresh interval for refreshing the data displayed or click the refresh icon to update the data immediately.
  4. View the cluster detail information.
You can view detailed information about clusters from the chassis partition CLI.
  2. Show all cluster details.
    show cluster
    A summary similar to this excerpt displays:
    default-1# show cluster
    cluster state
    cluster disk-usage-threshold state warning-limit 85
    cluster disk-usage-threshold state error-limit 90
    cluster disk-usage-threshold state critical-limit 97
    cluster disk-usage-threshold state growth-rate-limit 10
    cluster disk-usage-threshold state interval 60
    cluster nodes node blade-1
     state enabled      true
     state assigned     true
     state node-running-state running
     state present      single
     state platform-id  B60100
     state slots        [ 1 ]
     state platform fpga-state FPGA_RDY
     state platform dma-agent-state DMA_AGENT_RDY
     state slot-number  1
     state node-info creation-time 2023-01-06T02:11:09Z
     state node-info cpu 28
     state node-info pods 250
     state node-info memory 131576224Ki
     state ready-info ready true
This procedure outlines the steps to completely remove a blade from the cluster.
  • If the blade is removed and then reinserted into the original slot, no additional steps are required because the system automatically re-integrates the blade into the cluster.
  • If a blade is removed from the chassis and not inserted back into the original slot, the blade must be removed from the cluster. Follow the below procedure to remove blade from cluster.
  1. Connect using SSH to the system controller management IP address.
    config
  4. Move the slot to the none partition.
    slots slot <slot_number> partition none
    A summary of the example displays:
    syscon-2-active(config)# slots slot 3 partition none
    commit
  6. Physically Remove the Blade.
    For more details on physically removing a blade, see Remove a blade.
  7. Remove the node from the cluster.
    cluster nodes node <node_name> set-extracted
    This example shows removing node 5 from the cluster:
    syscon-2-active(config)# cluster nodes node blade-5 set-extracted
    result Node was successfully removed from cluster.
    If you attempt the set-extractedcommand while the blade is still inserted, you will encounter the following error.
    syscon-2-active(config)# cluster nodes node <node_name> set-extracted
    result Blade is inserted. Node cannot be removed from cluster.
You can configure general system settings for the VELOS system, such as system hostname, login banner, and message of the day (MOTD) banner. Depending on which setting you want to configure, you can use either the CLI or the webUI.
You can configure general system settings, including hostname, login banner, message of the day (MOTD) banner, and an advisory banner from the system controller webUI. When enabled and configured, the advisory banner will display at the top of the webUI after authentication. The product name displays but cannot be changed.
  2. On the left, click SYSTEM SETTINGS > General.
  3. For Hostname, enter a custom hostname for the system.
  4. For Login Banner, enter any text to be displayed when users log in to the system.
  5. For MOTD Banner, enter any text to be displayed as a MOTD when users log in to the system.
  6. For Advisory Banner, select Enabled or Disabled.
  7. For Advisory Banner Color, select the color for the banner.
  8. For Advisory Banner Text, enter the text for the banner. The maximum number of characters is 80.
  9. Click Save.
You can configure general system settings, including login banner, message of the day (MOTD) banner, advisory banner, and time zone/location from the chassis partition webUI. When enabled and configured, the advisory banner will display at the top of the webUI after authentication.
  3. For Login Banner, enter any text to be displayed when users log in to the chassis partition.
  4. For MOTD Banner, enter any text to be displayed as a MOTD when users log in to the chassis partition.
  5. For Advisory Banner, select Enabled or Disabled.
  6. For Advisory Banner Color, select the color for the banner.
  7. For Advisory Banner Text, enter the text for the banner. The maximum number of characters is 80.
  8. From Time Zone/Locations, select the time zone region.
  9. Click Save.
You can manually configure the hostname for your system from either the system controller or chassis partition CLI. F5 recommends you to configure a Fully Qualified Domain Name (FQDN) hostname.
    config
  3. Change the hostname.
    system config hostname <*hostname*>
    The minimum length is 1 character, and the maximum length is 253 characters.
    In the examples below, you can see the hostname for the system either set to ’test-hostname’ or ‘f5lab.f5net.com’:
    syscon-1-active(config)# system config hostname test-hostname
    syscon-1-active(config)# system config hostname f5lab.f5net.com
    Note: You can set a Fully Qualified Domain Name (FQDN) or plain text as a hostname.
    commit
    Note: The system hostname is now updated. By default, the system hostname will be included in the subsequent logs.
  5. To verify the hostname included in the logs.
    show system logging state include-hostname
    In this example, the hostname is included in the logs:
    syscon-1-active# show system logging state include-hostname true
You can manually configure the log settings to include hostname that is configured for your system in the subsequent logs from the CLI.
    config
  3. To include hostname in the logs, set ‘include-hostame’ to true.
    system logging config include-hostname <*\{ false \| true \}*>
    Note: The default value is set to true.
    In this example, the configured system hostname is included in the logs:
    syscon-1-active(config)# system logging config include-hostname true
    commit
  5. Return to user (operational) mode.
    end
  6. To verify the hostname is included in the subsequent logs.
    In the examples below, the system hostname “test-hostname” or “f5lab.f5net.com” is included in the logs:
    test-hostname# show system logging
    test-hostname#
    f5lab.f5net.com# show system logging
    f5lab.f5net.com#
The system hostname is now included in the subsequent logs.
You can configure the login banner for your system manually from either the system controller or chassis partition CLI. The login banner displays before users log in to each respective system.
    config
  3. Change the login banner text.
    system config login-banner
    In this example, you change the login banner text to notify users that unauthorized access is prohibited:
    syscon-1-active(config)# system config login-banner
    (<string>):
    UNAUTHORIZED ACCESS TO THIS DEVICE IS PROHIBITED
    commit
The login banner is now updated.
You can manually configure the message-of-the-day (MOTD) banner for your system from either the system controller or chassis partition CLI. The MOTD banner displays after users log in to each respective system.
    config
  3. Change the MOTD banner text.
    system config motd-banner
    In this example, you change the login banner text to notify users of upcoming system maintenance:
    syscon-1-active(config)# system config motd-banner
    (<string>):
    ATTENTION!
    This system is scheduled for maintenance in two days.
    commit
The MOTD banner is now updated.
You can verify the current MAC allocation data from the system controller CLI.
  1. Log in to the command line interface (CLI) of the system controller using an account with admin access.
  2. Display the current MAC allocation data.
    show system mac-allocation
    syscon-1-active# show system mac-allocation
    system mac-allocation state free-single-macs 144
    system mac-allocation state allocated-single-macs 16
    system mac-allocation state free-large-blocks 24
    system mac-allocation state allocated-large-blocks 0
    system mac-allocation state total-free-mac-count 912
    system mac-allocation state total-allocated-mac-count 16
    system mac-allocation state total-mac-count 928
You can verify the current runtime status of the MAC pool from the system controller CLI.
  2. Display the current chassis MAC allocation.
    show system chassis-macs
    syscon-1-active# show system chassis-macs
    system chassis-macs base 000a49ff1800
        ALLOCATED
    IDENTIFIER  UUID                                  OFFSET  MAC ADDRESS        INDEX  AS SINGLE
    1           c2c66fb4-7426-4134-8110-a0fb4547c866  8       00:0a:49:ff:18:08  -      -
                                                      9       00:0a:49:ff:18:09  -      -
                                                      10      00:0a:49:ff:18:0a  -      -
                                                      11      00:0a:49:ff:18:0b  -      -
                                                      12      00:0a:49:ff:18:0c  -      -
                                                      13      00:0a:49:ff:18:0d  -      -
                                                      14      00:0a:49:ff:18:0e  -      -
                                                      15      00:0a:49:ff:18:0f  -      -
                                                      16      00:0a:49:ff:18:10  -      -
                                                      17      00:0a:49:ff:18:11  -      -
                                                      18      00:0a:49:ff:18:12  -      -
                                                      19      00:0a:49:ff:18:13  -      -
                                                      20      00:0a:49:ff:18:14  -      -
                                                      21      00:0a:49:ff:18:15  -      -
                                                      22      00:0a:49:ff:18:16  -      -
                                                      23      00:0a:49:ff:18:17  -      -
                                                      28      00:0a:49:ff:18:1c  0      false
                                                      29      00:0a:49:ff:18:1d  0      false
                                                      30      00:0a:49:ff:18:1e  0      false
                                                      31      00:0a:49:ff:18:1f  0      false
                                                      32      00:0a:49:ff:18:20  0      false
                                                      33      00:0a:49:ff:18:21  0      false
                                                      34      00:0a:49:ff:18:22  0      false
                                                      35      00:0a:49:ff:18:23  0      false
                                                      36      00:0a:49:ff:18:24  0      false
                                                      37      00:0a:49:ff:18:25  0      false
                                                      38      00:0a:49:ff:18:26  0      false
                                                      39      00:0a:49:ff:18:27  0      false
                                                      40      00:0a:49:ff:18:28  0      false
                                                      41      00:0a:49:ff:18:29  0      false
                                                      42      00:0a:49:ff:18:2a  0      false
                                                      43      00:0a:49:ff:18:2b  0      false
                                                      44      00:0a:49:ff:18:2c  0      false
                                                      45      00:0a:49:ff:18:2d  0      false
                                                      46      00:0a:49:ff:18:2e  0      false
                                                      47      00:0a:49:ff:18:2f  0      false
                                                      48      00:0a:49:ff:18:30  0      false
                                                      49      00:0a:49:ff:18:31  0      false
                                                      50      00:0a:49:ff:18:32  0      false
                                                      51      00:0a:49:ff:18:33  0      false
                                                      52      00:0a:49:ff:18:34  0      false
                                                      53      00:0a:49:ff:18:35  0      false
                                                      54      00:0a:49:ff:18:36  0      false
                                                      55      00:0a:49:ff:18:37  0      false
                                                      56      00:0a:49:ff:18:38  0      false
                                                      57      00:0a:49:ff:18:39  0      false
                                                      58      00:0a:49:ff:18:3a  0      false
                                                      59      00:0a:49:ff:18:3b  0      false
You can verify the system uptime for the CLI:
  2. Display the system uptime.
    show system uptime
    syscon-1-active# show system uptime
    system uptime state up-time "6h, 26m, 0s"
If you are having an issue with a chassis partition (such as unusually high CPU or memory usage or lockup), it is possible that rebooting a blade in the chassis partition might help to resolve the issue.
When there is a problem, the system sends alerts that you would see on the dashboard or on the Alarms & Events screen. A blade status of Not ready for a prolonged time on the General screen can also indicate the need to reboot the blade. You should rarely have to reboot a blade, however, because typically if the VELOS system needs to reboot a blade, it will do so automatically without administrator intervention. F5 recommends working with customer support if you think a blade reboot is necessary.
You can manually reboot a system controller in your VELOS system from the system controller CLI.
  3. Reboot a system controller.
    system reboot controllers controller { active | standby ]
    In this example, you reboot the standby system controller:
    syscon-1-active# system reboot controllers controller standby
The specified system controller reboots.
You can reboot a system controller from the system controller webUI.
  3. Review the status of the system controllers.
    The Reboot button will not be available for a system controller that is currently being rebooted.
  4. If you decide that a reboot is necessary, click Reboot to the right of the system controller that you want to reboot.
    If the system controller has the active role, a popup displays asking you to confirm the reboot operation. This causes a failover to the standby controller.
    The It takes a few minutes for the system controller to reboot. The status will show Reboot in progress, then Not ready, and when reboot is complete, it says Ready.
You can manually reboot a blade in your system from the chassis partition CLI.
  1. Connect using SSH to the chassis partition management IP address.
  2. Log in to the command line interface (CLI) of the chassis partition using an account with admin access.
  3. Reboot a blade.
    cluster nodes node <*blade-number*> reboot
    In this example, you reboot blade-1:
    default-1#(config) cluster nodes node blade-1 reboot
The specified blade reboots.
You can reboot a blade within a chassis partition from the chassis partition webUI.
  3. Review the status of each of the blades in the chassis partition.
    The Reboot button will not be available for slots that do not have blades present, or for blades that are currently being rebooted.
  4. If you have tenants running on the chassis partition you might want to warn users that their service might be interrupted temporarily.
  5. If you decide that a reboot is necessary, click Reboot to the right of the slot containing the blade that you want to reboot.
    It takes a few minutes for the blade to reboot. The status will show Reboot in progress, then Not ready, and when reboot is complete, it says Ready.
OpenTelemetry streamlines observability in distributed systems through standardized APIs, libraries, and tools for collecting telemetry data, including traces, metrics, and logs.
F5OS OpenTelemetry enables the efficient collection of streaming metrics and logs in a structured format from the F5OS product to display in your observability platform. All the metrics and logs will be exported through a gRPC connection. The F5OS supports gRPC endpoints and each OpenTelemetry Line Protocol (OTLP) endpoint is provided with the ability to toggle instrument based filtering.
Telemetry subsystem within the F5OS platform layer generates common attributes and different metrics to display in your observability platform.
An instrument is an area of metrics, which contain multiple metrics and can be enabled selectively. F5OS Resource includes instruments.
Summarizes the metrics that are associated with each tenant as they enters and exits the platform hardware at the DMA level.
The following tenant metrics are currently reported by the BIG-IP tenant into the F5OS platform layer. The metrics visible at the platform layer are only a limited subset of the total number of metrics available to the tenant. You can view the full tenant metrics by using the BIG-IP metric reporting capability.
F5OS OpenTelemetry exporter will only report the metrics that are associated with the Docker containers managed by the platform layer. For more information about the docker container metrics, see Docker stats documentation.
The platform hardware sensors represent physical sensors associated with the hardware which measure: temperature, current, power, voltage, RPM and percent humidity.
The metric schema is heavily dependent upon the internal representation of the tmstat tables within F5OS.
Instument name Description
all All the logs and metrics produced by the F5OS platform layer
logs All the F5OS logs file
platform-log All the F5OS platform logs file
event-log All the F5OS ConfD event log
metrics All the F5OS metrics
platform Standard platform metrics such as memory, disk, CPU, and interface
hardware The low-level platform hardware sensors
optics The front-panel optic DDM metrics
tenant Tenant-initiated metrics such as memory, disk, CPU, and interface
datapath F5OS data-path metrics such as those generated by the FPGA and DMA
tmstat F5OS tmstat tables exported as metrics
container Docker container metrics for F5OS services
Note: Support for the intrument “tenant” is provided only for BIG-IP tenants.
This image provides a representation how the F5OS Resource includes instruments with multiple metrics:
Example of system inventory
The table lists the set of attributes that can be applied to all metrics produced by the platform.
The scope indicates which product the attribute applies to:
  • F5 - Applies to all metrics produced by F5
  • F5OS - Applies to all metrics produced by the F5OS product
Name
Value
Type
Scope
Description
host.name
<*name of host*>
string
F5
The host-name for F5OS, derived from ConfD system hostname.
f5.system.id
<*instance ID*>
string
F5
A unique instance ID per product.
f5.product.version
<*version string*>
string
F5
A version string, which represents the version of the product.
f5.product.name
<*product\_name*>
string
F5
The high-level F5 product generating the metric/log: - F5OS
  • BIGIP-Next
  • SPK
  • CNF
f5.product.type
<*v6h-hi*>
string
F5OS
The platform type.
f5.platform.serial_number
<*platform\_serial\_no*>
string
F5OS
Serial number of an appliance, blade, or controller.
f5.platform.role
<*platform\_role*>
string
F5OS
The appliance is straight-forward. However, for chassis products, the telemetry data can originate from multiple places. The role can help identify a location. - Blade - The data originated from a blade within a partition
  • Partition - The data originated from a partition-level service
  • Controller - The data originated from a system controller
f5.platform.pid
C137
string
F5OS
The platform ID
f5.platform.name
<*platform\_name*>
string
F5OS
The Platform Name - rSeries - The appliance products
  • VELOS - The chassis products
instrument.name
<*name*>
string
F5OS
F5OS Instrument name associated with the metric.
f5.data_type
<*f5os-analytics*>
string
F5
The attribute used by BIG-IP Central Manager to help direct F5OS specific metrics
f5.tenant.name
<*f5os\_tenant\_name*>
string
F5OS
The deployed tenant name
The following attributes apply for the tenant based metrics.
Name
Value
Type
Description
f5.tenant.name
<*tenant name*>
string
The name of the tenant which acts as a tenant ID
f5.tenant.image
<*image version*>
string
The tenant image version
f5.tenant.type
  • BIG-IP
  • BIG-IP Next
string
The tenant type name
Note: These metrics are relevant to Platforms.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.interface.packets
Counter
int64
interface.name="1.0"
direction="receive"
{packets}
Counter
int64
direction="transmit"
{packets}
f5.interface.bytes
Counter
int64
direction="receive"
Bytes
f5.interface.bytes
Counter
int64
Bytes
f5.interface.errors
Counter
int64
direction="receive"
{packets}
f5.interface.errors
Counter
int64
{packets}
f5.interface.dropped
Counter
int64
direction="receive"
{packets}
Counter
int64
{packets}
f5.interface.broadcast
Counter
int64
direction="receive"
{packets}
Counter
int64
{packets}
f5.interface.multicast
Counter
int64
direction="receive"
{packets}
Counter
int64
{packets}
f5.interface.ethernet
Counter
int64
name="1.0"
state=<field>
{packets}
Reports the front-panel Optic DDM metrics.
Common Attributes include:
port.group=<string>
    -   The F5OS port group name associated with the Optic
-   ``` {#codeblock_cld_wtz_z1c}
 port.name="1.0"..
-   The front-panel port number
channel=1..N
    -   For metrics which are per-channel, identifies the individual channel number
-   ``` {#codeblock_zkj_wtz_z1c}
direction="transmit" | "receive"
-   An indication of transmit or receive direction
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.optic.temperature
Gauge
float
port.group=<string>
port.name="1.0"
C
f5.optic.voltage
Gauge
float
port.group=<string>
port.name="1.0"
V
f5.optic.power
Gauge
float
port.group=<string>
port.name="1.0"
channel=1..N
dbm
f5.optic.tx-bias
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
f5.optic.los
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
f5.optic.tx-fault
Gauge
int64
port.group=<string>
port.name="1.0"
channel=1..N
The schema of the CPU metrics is based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.cpu.time
Counter
int64
cpu=cpu0..cpuN
thread=0...N
state=<field>
Seconds
system.cpu.utilization
Gauge
float64
pu=cpu0...cpuN
thread=0..N
state=<field>
{percent}
The Disk IO Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.disk.io_time
Counter
float64
device=<name>
direction=total
Seconds
system.disk.operations
Counter
int64
device=<name>
direction=read
{operations}
Counter
int64
device=<name>
direction=write
{operations}
system.disk.io
Counter
int64
device=<name>
direction=read
Bytes
system.disk.io
Counter
int64
device=<name>
direction=write
Bytes
system.disk.merged
Counter
int64
device=<name>
direction=read
{operations}
system.disk.merged
Counter
int64
device=<name>
direction=write
{operations}
system.disk.operation_time
Counter
float64
device=<name>
direction=read
Seconds
Counter
float64
device=<name>
direction=write
Seconds
system.disk.usage
Counter
float64
device=<name>
Bytes
The Memory Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.disk.usage
Counter
int64
state="<*field*>"
Bytes
system.disk.utillization
Gauge
float64
state=used
{percent}
Gauge
float64
state=platform
{percent}
Gauge
float64
state=available
{percent}
The File system Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.filesystem.usage
Gauge
int64
state = "free" || "total" || "used" system.device = </*dev/mapper/partition\_image-export\_chassis*> system.filesystem.mountpoint = <*/var/export/chassis*> system.filesystem.type = <*ext4*>
By
system.filesystem.utilization
Gauge
float64
state =used system.device = <*/dev/mapper/partition\_image-export\_chassis*> system.filesystem.mountpoint = <*/var/export/chassis*> system.filesystem.type = <*ext4*>
Percent
The Uptime Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Metric Name
Metric Type
Value Type
Attributes
Unit
system.uptime
Counter
int64
S
The Raid Metrics are based on the OpenTelemetry semantic conventions. For more information, see Metrics Semantic Conventions
Note: Applicable for F5 r10000/12000 platforms with only two hard disks.
Metric Name
Metric Type
Value Type
Attributes
Unit
system.raid.blocks
Gauge
int64
state= "blocksTotal" || "blocks-synced"
system.raid.devices = <*nvme0n1p1,nvme1n1p1*>
system.raid.name = <*md124*>
Blocks
system.raid.state
Gauge
int64
state = "disks-total" || "disks-active" || "disks-failed" || "disks-down" || "disks-spare"
Count
system.raid.status
Gauge
int64
state = “active” || “blocks-synced”
{status}
system.raid.sync.estimation
Gauge
float64
Seconds
system.raid.sync.percent
Gauge
float64
Percent
system.raid.sync.speed
Gauge
float64
KbPerSecInterface Counter Metrics
Note: This metric is the sum of all internal tenant interfaces and independent of the F5 platform front-panel interface.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.datapath.packets
Counter
int
direction="transmit | receive"
f5.datapath.area="dma"
{packet}
f5.datapath.bytes
Counter
int
By
This table lists the attributes that are associated with the tenant-based metrics.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tenant.cpu.utilization
Gauge
float64
state="<*field-name*>"
cpu = cpuN
Percent
f5.tenant.cpu.time
Couner
int64
state= "<*field-name*>"
cpi = cpuN
s
Metric Name
Metric Type
Value Type
Attributes
Unit
Gauge
float64
state="<*field*>"
Percent
system.disk.usage
Gauge
int64
state="<*field*>"
Bytes
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tenant.disk.operations
Counter
int64
device=<*name*>
direction=total
operation
Counter
int64
device=<*name*>
direction=read
operation
Counter
int64
device=<*name*>
direction=write
operation
f5.tenant.disk.io
Counter
int64
device=<*name*>
direction=read
Bytes
f5.tenant.disk.io
Counter
int64
device=<*name*>
direction=write
Bytes
f5.tenant.disk.merged
Counter
int64
device=<*name*>
direction=read
operation
Counter
int64
device=<*name*>
direction=write
operation
f5.tenant.disk.operation_time
Counter
float64
device=<*name*>
direction=read
s
Counter
float64
device=<*name*>
direction=write
s
Metric Name
Metric Type
Value Type
Attributes
Unit
f5os.tenant.interface.packets
Counter
float64
interface.name="<interface-name>"
direction="receive"
packets
Counter
int64
packets
f5os.tenant.interface.bytes
Counter
int64
direction="receive"
Bytes
Counter
int64
Bytes
Attributes
Metric value type
Description
container.name
string
The name of the container
container.image.name
string
The container image name
Metric Name
Metric Type
Value Type
Attributes
Unit
container.cpu.usage.<*field-name*>
Gauge
float
ns
container.memory.<*field-name*>
Gauge
float
By
container.memory.usage <*field-name*>
Gauge
float
By
container.memory.percent
Gauge
float
{percent}
container.blockio.io_service_bytes_recursive
Gauge
float
operation="read" | "write"
By
container.network.io.usage.<*field-name*>
Gauge
float
interface=<name>
By | {percent}
container.cpu.percent
Gauge
float
cpu=<name>
{percent}
f5.sensor.name=
    Eamples:
    -   Temperature:
        -   Inlet
        -   Outlet
        -   Central
    -   Voltage:
        -   12V
        -   3.3V BCM
    -   Current:
        -   12V Main
        -   Current In
    -   Power:
        -   Controller Power
        -   Total Power Supply Unit \(PSU\) Power In
        -   Total Power Supply Unit \(PSU\) Power Out
-   ``` {#codeblock_onv_mj1_1bc}
f5os.sensor.source=<component name>
Eamples:
-   psu-\[1..N\]
-   fantray-\[1..N\]
-   psu-controller-\[1..N\]
-   blade-\[1..N\]
-   controller-\[1..2\]
-   platform
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.sensor.temperature
Gauge
float64
f5.sensor.name="<name of sensor>"
sensor.source="?<component name>"
C
f5.sensor.voltage
Gauge
float64
V
f5.sensor.current
Gauge
float64
A
f5.sensor.power
Gauge
float64
W
f5.sensor.humidity
Gauge
float64
{percent}
f5.sensor.fan.speed
Gauge
float64
RPM
Note: When you select instrument type as “all” and/or “metrics”, the instrument type “tmstat” is set to off and cannot be selected. You have to manualy enable the instrument “tmstat”. Using this instrument is more tailored to internal ‌F5 use cases, such as deep diagnostics.
Metric Name
Metric Type
Value Type
Attributes
Unit
f5.tmstat.<*table*>
Gauge
int
f5.tmstat.column=<*name*>
You can configure an exporter from the webUI.
  2. On the left, clickSYSTEM SETTINGS > Telemetry.
    The Telemetry screen displays.
  3. Under the Telemetry exporters area, click Add.
    The Add Exporter screen displays.
  4. Enter Name of the Exporter (up to 20 characters).
    The first character in the name cannot be a number. After that, only lowercase alphanumeric characters and hyphens are allowed.
  5. For Endpoint
    • For IP Address, enter the IPv4 address, IPv6 address, or Fully Qualified Domain Name (FQDN) for an exporter.
    • For Port, enter the port number of the Server.
  6. For Enable, select True if you want to enable and send the telemetry data to the exporter or False to disable it.
  7. For Instruments, select one or more instruments for an exporter.
    Following table lists the avaialble options:
    Note: Note: “tenant” and “datapath” instruments are only supported on Chassis partition.
    Option Description
    all Reports all logs and metrics produced by the F5OS platform layer
    logs Reports all F5OS logs file through the OpenTelemetry ’ log’ API
    platform-log Exports the F5OS platform log through the OpenTelemetry ’ log’ API
    event-log Exports the F5OS confd event log through the OpenTelemetry ’ log’log’ API
    metrics Report all F5OS metrics through the OpenTelemetry ’ log’metric’ API
    platform F5OS platform metrics such as memory, disk, cpu, interface, and file system
    hardware F5OS hardware sensors such as voltage, current, temperature, power, fan-speeds
    optics F5OS front-panel Optic DDM metrics
    tenant Low level tenant reported metrics such as memory, disk, cpu, interface stats
    container F5OS Per-Container metrics such as cpu, block-io, network, memory
  8. For Compression, select the compression type. By default gzip will be selected.
  9. For Attributes, specify the attributes for the exporter.
    You can then click + or x to add or remove additional attributes.
    Attributes are reference data which can be associated with the exporter. Attributes can be specified in the key & value format.
  10. For Secure input, select True to enable and configure the Transport Layer Security (TLS) to secure the connections. The default option is False.
    Note: Before you can enable TLS encryption, you must configure a key and certificate on the system.
    1. If you have selected True for secure connections, you can use one of these methods:
      • Server Authentication only:
        • For TLS CA Certificate, paste the contents of the certificate (self-signed or from a CA) for server TLS authentication.
      • Both Server and Client Authentication
        1. For TLS CA Certificate, paste the contents of the certificate (self-signed or from a CA) for server TLS authentication.
        2. In the TLS Certificate field, paste the text of the local certificate for client TLS authentication.
        3. In the TLS Key field, paste the text of the private key for client TLS authentication.
  11. For Reload Interval, specify the duration to reload the certificate within the specified timeframe.
    Note: You can only specify the duration value in nanoseconds (ns), microseconds (us (or µs)), milliseconds (ms), seconds, minutes, and hours.
  12. Click Save & Close.
You can delete an exporter from the webUI.
  2. On the left, click SYSTEM SETTINGS > Telemetry.
    The Telemetry screen displays the existing exporter and associated details.
  3. To delete an exporter, in the Telemetry exporters area, select the exporter from the list and then click Delete.
  4. Click Save.
Attributes are reference data which can be associated with the exporter. Attributes can be specified in the key:value format. Spaces must be included between each entry. You can add attributes to all the configured exporters from the webUI.
  3. Under Telemetry Attributes, specify the attributes.
Before configuring an exporter, you can display supported instruments from the CLI.
    config
  4. Show the total and available instruments:
    show system telemetry instruments
    Following is an example for the instruments that are supported on System Controller:
    syscon-2-active# show system telemetry instruments
    NAME          DESCRIPTION
    all           Report all logs and metrics produced by the F5OS platform layer
    logs          Report all F5OS logs file through the OpenTelemetry 'log' API
    platform-log  Export the F5OS platform log through the OpenTelemetry 'log' API
    event-log     Export the F5OS confd event log through the OpenTelemetry 'log' API
    metrics       Report all F5OS metrics through the OpenTelemetry 'metric' API
    platform      F5OS platform metrics such as: memory, disk, cpu, interface, and file system
    hardware      F5OS hardware sensors such as: voltage, current, temperature, power, fan-speeds
    container     F5OS Per-Container metrics such as: cpu, block-io, network, memory
    Following is an example for the instruments that are supported on Chassis Partition:
    default-2# show system telemetry instruments
    NAME          DESCRIPTION
    tenant        Low level tenant reported metrics such as: memory, disk, cpu, interface stats
An exporter defines an OpenTelemetry gRPC endpoint to which the F5OS Platform will push metrics/logs.
You can configure the exporter from the CLI.
    config
  4. Configure the exporter.
    You must specify the IP address or DNS name of the server and the port number of the server on which OpenTelemetry (OTEL) is running
    system telemetry exporters exporter <*server name*> config endpoint address <*address*> port <*port number*> instruments <*instrument name*> tls sercure { false | true }
    Following example displays the configuration for an exporter in the System Controller :
    syscon-2-active(config)# system telemetry exporters exporter test config endpoint address 10.146.243.109 port 4317 instruments [ platform hardware ] tls secure false
    Following example dispalys the configuration for an exporter in the Chassis Partition:
    default-2# system telemetry exporters exporter test1 config endpoint address 10.144.74.171 port 4317 instruments [all] tls secure false
    commit
Note: To optimize ‌performance, F5 recommends to configure minimum exporters, as they utilize system resources.
Note: You can enable ‌Transport Layer Security (TLS) and secure the connections for telemetry streaming. Before you can enable TLS encryption, you must generate a private key and self-signed certificate.
    config
    A summary similar to this example displays:
    syscon-1-active(config)# system telemetry exporters exporter test1 config endpoint address 10.144.74.171 port 4317 instruments [all] tls secure true
    Possible completions:
      ca-certificate    Specifies the CA Certificate content.
      certificate       Specifies the PEM-encoded telemetry client certificate (Configure for mTLS).
      key               Specifies the PEM-encoded telemetry client private key (Configure for mTLS)
      reload-interval   Specifies reload-interval in duration strings.
      <cr>
  5. You can secure the connections by using one of these methods:
    • To authenticate the server, add the certificate:
      system telemetry exporters exporter <*server name*> config ca-certificate
      Press Enter to enable multi-line mode and then paste the contents. Press Ctrl-D to exit multi-line mode.
      system telemetry exporters exporter test1 config ca-certificate
      (<string>):
      Following example displays the configuration for an exporter with secure connection in the System Controller:
      syscon-2-active(config)# system telemetry exporters exporter test config endpoint address 10.146.243.109 port 4317 instruments [ platform hardware ]tls secure true ca-certificate
      Value for 'system telemetry exporters exporter test-tls config tls ca-certificate' (<string, min: 1 chars>):
      > -----BEGIN CERTIFICATE-----
      > MIIFiTCCA3GgAwIBAgIJAOhKpL9Y2XI0MA0GCSqGSIb3DQEBCwUAMFsxCzAJBgNV
      > BAYTAklOMQswCQYDVQQIDAJUUzEMMAoGA1UEBwwDSHlkMQswCQYDVQQKDAJGNTER
      > MA8GA1UECwwIQVBJU1ZDR1cxETAPBgNVBAMMCE15Um9vdENBMB4XDTIzMTExMzA3
      > MTgzOVoXDTI0MTExMjA3MTgzOVowWzELMAkGA1UEBhMCSU4xCzAJBgNVBAgMAlRT
      > MQwwCgYDVQQHDANIeWQxCzAJBgNVBAoMAkY1MREwDwYDVQQLDAhBUElTVkNHVzER
      > MA8GA1UEAwwITXlSb290Q0EwggIiMA0GCSqGSIb3DQEBAQUAA4ICDwAwggIKAoIC
      > AQDQ/BzhFOmjSQpi/IHCaD8lGB353a5Lbq42WRM37DJXbZ1aOL57JNEdenHmqi9C
      > 8KQSM5E4rtEvEnNL667JeYzXZA6W8Juf6fgMhjvPhK1knFB1Hs1wROgPVhv2Xd0Q
      > cVVHBE4CWCrazVD2dM/lRgCr/kxJVI+u5y16Kpe4c/0qoUetkcCEGnm04hC7N41O
      > 5UfbDGHFyqYNVU+f5EnCG0fV/LrWxqKGMSB8KUywAEJ32pteUxpsI5fq50XKPBkK
      > PFrSM2T4lipwt2A1bKOq+GU8J8YefEIQNBxznQdMHOntWyJ+9spxxa2MVco045kH
      > XVX6YpVe3OQ8Ogd41TgXHPLcCzCtSeblXn2OkxNB8LjcdGDtRTOEc+mvUIZrw5YZ
      > FxegJOsoOm1Ul7YLaIvT281dyueqaAxq85OB+SYlcVe7BiorjoiF44ABAkBcQYrf
      > /byNoQJ/y4pPjD0suKznyC0q+MZSjra7ezv8mquT/nRo5v0XwtlC1hLOxRr6ljqH
      > s/irTqqzosqF/PidfaWopninLEGtMm2w5J4nqZn2XzHfCXs8uFxNlfy3X79E497r
      > jP/MfbFzjfZuJI/PjFVSF4I9Jj9sNbOIY4YVeKU65vjDnADFu0wZ5GA2O964hhX/
      > J24RqVLVnsieMvaW5cfIvMXSAIYU7h2hyny308JA72X44QIDAQABo1AwTjAdBgNV
      > HQ4EFgQU2tPO6b+uiyewldxz0htrBLy6hI4wHwYDVR0jBBgwFoAU2tPO6b+uiyew
      > ldxz0htrBLy6hI4wDAYDVR0TBAUwAwEB/zANBgkqhkiG9w0BAQsFAAOCAgEAsGsA
      > j9rqRoCbbbQfGcdcxhNbDv05kICCyVn51rwc7iHYmY5PHZbUuaTo4nfJF7yiAjtD
      > wqSdZf3iRMAipHMInjHsWi+Aiv6JGABUHexnN1QNY99fw1XuvevC7XFSzOXH5Vq4
      > 0mn0s9LEk4gyGZm2WqEZ887sbe8xEM1yG5IQkt0N5Sfg6PADjPXc6IwPVAltvzVi
      > 1ZuoIUqrryQsT1KlaWgZW5zx+N9oWgeE934zC3JpxnbHKZduCsPhIiwc/MQRdLFD
      > ElXzaAVLM3qFsPu9UMynT1IdbN1Z2dtCiwDxP+gvUflnENRFISBuYG0WA+D/7p2I
      > OkV7WeCs5AVeRrgnCNYDdxqPaRDoSfxKfNOMaXWV4519nW1DdfonDVnw0dITB0wG
      > 7ur/2Y2QfmAKjCoCI/gtDls60L8sNVpZgXVhkDjbYVELQN7uYSuMFYmZAeKDuXyH
      > 7hq+3oa+B3Nr9+h8A8fg3tIjeH6B/A0vz8zyBhtFctesmOV10TBZ6eCG+h+VvxPk
      > S65kZxcp+KuR41esUYjbTbnN58QqUDMfDWb7nbYRr9sxBcktfxSDnUzLzhGfvnDa
      > EF1MDwL8ivR1Fzh1B0YaMU7CNsDba7B3QgG08hrG18SiAFVuW/dcLnyIx9YHaPox
      > +1efl7PuS/ILKF78pMnHur+xpt5oQmHf1erqqBE=
      > -----END CERTIFICATE-----
    • To authenticate the server and client, add the certificates and key.
      system telemetry exporters exporter <*server name*> config tls certificate
      system telemetry exporters exporter server1 config tls certificate (<string>): [Multiline mode, exit with ctrl-D.] > ... syscon-2-active(config)# config tls key (<string>): [Multiline mode, exit with ctrl-D.] > syscon-2-active(config)# config tls certificate (<string>): [Multiline mode, exit with ctrl-D.] >
      Following example displays the configuration for an exporter with secure connection in the System Controller :
      syscon-2-active(config)# system telemetry exporters exporter test-mtls config endpoint address 10.238.678.16 port 4315 instruments [ all ] tls secure true
      Value for 'system telemetry exporters exporter test-mtls config tls ca-certificate' (<string, min: 1 chars>):
      syscon-2-active(config-exporter-test-mtls)# config tls key
      syscon-2-active(config-exporter-test-mtls)# config tls certificate
      (<string>):
      > MIIFSTCCAzGgAwIBAgIBATANBgkqhkiG9w0BAQsFADBbMQswCQYDVQQGEwJJTjEL
      > MAkGA1UECAwCVFMxDDAKBgNVBAcMA0h5ZDELMAkGA1UECgwCRjUxETAPBgNVBAsM
      > CEFQSVNWQ0dXMREwDwYDVQQDDAhNeVJvb3RDQTAeFw0yMzExMTMwODE4MDFaFw0y
      > NDExMTIwODE4MDFaMGAxCzAJBgNVBAYTAklOMQswCQYDVQQIDAJUUzEMMAoGA1UE
      > BwwDSHlkMQswCQYDVQQKDAJGNTERMA8GA1UECwwIQVBJU1ZDR1cxFjAUBgNVBAMM
      > DTEwLjE0NC43NC4xNzEwggIiMA0GCSqGSIb3DQEBAQUAA4ICDwAwggIKAoICAQDI
      > HecdJvgITByPhLgtp8duUd0slfWABZYcRjpeLQj2FN7lPXMeKsuJn55zOSS9l/qv
      > uOij7+FYj7asMLVfKBOZlLtR0AFEFSChM+bR48mTGMLpTo0pqEzod0KlxPt7P1bp
      > DNkkfNlZZfIBFUvuDKgO4/ao45YEwD0DdXrswsnEh25e+NRLaPlmFbMRNhvfZKk6
      > xkWW9Gd4int3EaXruHCc9FeMZAEyDelGxd5QlXU5VE9q3sJh6yHe0zssIAGatggR
      > HzdxFxYwJsdDGedl1K9Z7v4zz7YG+3ziqZOdYtX+RXb/kJtTF1Xwk3gt6ZDH2BaU
      > sDAZHHr87oei1qmISCaM2WMgHVo4XX2/R7dKLYvm/od91Fm1DLmpjNaHhWcNLbzH
      > HdLbNwtlSPX7+6kBQbFTllyLcvmP6J2JTA+hVWkUNo6Ta82YAi2vW2bMKKkruNnt
      > 8XCsi23Yvh9EyiBWTGanaiVbA7FDs2fw9FRHeKqpN21cb5w29zacwJnHGjkwi/uI
      > tUVjHDdUOCvawJbAsDj3oGkwSzHElUg6WsiQ/lY9ZdjoumHRbeY19RfXt33gfwgr
      > Nx/J/VVTbrR94Ysk6+NMW5M4M6EzktR3ikdnY3BoHCWIrE11eFWGwmTtQM5BxkbX
      > zKPP9kc6rD9eNbvnxa8ZihVdsFHjh45LnXApDAHRDQIDAQABoxMwETAPBgNVHREE
      > CDAGhwQKkEqrMA0GCSqGSIb3DQEBCwUAA4ICAQCL4WPnxZxkHQmWixwESO+r15hl
      > Stys4rwY7okRk9jLu90pV+TumO+/oWS+/ZbsKr0gbnGuvKiCZbsjzS9FHdBCDJTI
      > ZMbj2FLU4vwQZdaNRmmHJ8PjGVDrk5flAvM6mOBarZTuyElE8vAMlekjwcBwdEn3
      > 9Cyh10V+4U6C/6yJPdImsG2VCBN4UtiiROoUqBVFOZ8Us9tYjDtg7e85ZBtzNthK
      > 4rZ7cEbYMkYdQogC4J2LKGi+EDFEW7qbG1USArOo3mC2p4cAMTIhk5mfWPbyH8Ka
      > apOQU9o3/TrWCGMnSTYkrTV7IAtkjqEnlJzclMa1p4slYPVYgfsRS4JMtjnTxVtd
      > 9QoeNjlm81jqtUdxZLNTPJlLW6+tsonK12fkBFpiYHlFXR80VmVJ/llzjhSV8M7h
      > phB1mzgVuhRSwEV7ZKtltYEvuXXnoI53AOJ8uZfK+a3OKTD/LNzfeKIDT9iYUznR
      > K118PFLjRns25+ZsMsf+l72c9rvu4hpywnnTPp/1xT1OjfBh1Df66VNLjssg00d5
      > cNqwtS3wQkTvrNk1ivSUr0fnq6EAtK5HALVs7+USXiHtfV7H1rqN8f6cMSdVGcHl
      > GIuN7GXyY+Kclg+uFcRHTFGryESl1YhTV0LRdSBrR4Im1kPcuxqhOu65104jIlx7
      > 9P1GdQ6vjkCt8i0hXQ==
  6. Commit the configuration changes.
    commit
After you configure the exporter, you can display the state of the exporter from the CLI.
    When you log in to the system, you are in user (operational) mode.
  3. Display the state of a specific exporter
    show system telemetry exporters exporter <*server name*>
    Following example displays the state of an exporter with secure connection enabled in system controller for both server and client:
    syscon-2-active# show system telemetry exporters exporter test-mtls
    state enabled
    state endpoint address 10.238.678.16
    state endpoint port 4315
    state instruments [ all ]
    state tls secure true
    state tls certificat
     "-----BEGIN CERTIFICATE-----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\n9P1GdQ6vjkCt8i0hXQ==\n-----END CERTIFICATE-----\n"
    state tls key  "$8$j6uZb0TF3fbN/hX/iayVBUJLDpyz1LJE3w2DkQXEB6BkBAi3PCWNLUAaQIopIND0EAdrN/Pq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\ncj1q/npvZJldbe4eet/wtplOdd9vzDxN"
    state tls ca-certificate
    "-----BEGIN CERTIFICATE-----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\n+1efl7PuS/ILKF78pMnHur+xpt5oQmHf1erqqBE=\n-----END CERTIFICATE-----\n"
    state options compression gzip
You can modify the configuration of an exporter from the CLI.
  1. Connect using SSH to the system controller floating management IP address or chassis partition management IP address.
  2. Log in to the command line interface (CLI) of the system controller or chassis partition using an account with admin access.
  3. Change to config mode.
    config
    The CLI prompt changes to include (config).
  4. You can use the following commands to modify the exporter configuration:
    • Disable the exporter
      system telemetry exporters exporter <*server name*> config disabled
      When you specify an exporter, a summary to this example displays:
      syscon-2-active(config)# system telemetry exporters exporter server1 config disabled
    • Modify option compression
      system telemetry exporters exporter server1 config options compression <*new value*>
      A summary to this example displays:
      syscon-2-active(config)# system telemetry exporters exporter server1 config options compression zstd
  5. Commit the configuration changes.
    commit
    end
  7. You can verify the state of the exporter. see Display exporter state from the CLI.
You can add attributes to all the configured exporters from the CLI
  1. Log in to the command line interface (CLI) of the system controller or chassis partition using an account with admin access.
  2. Change to config mode.
    config
  3. You can add attributes to all the configures exporters:
    system telemetry attributes attribute <*attribute name*> <*attribute value*>
    Following example displays the configuration for an Attributes for all the configured exporters in the System Controller :
    syscon-2-active(config)# system telemetry attributes attribute test.key config key test.key value test.value
  4. Commit the configuration changes.
    commit
    end
  6. You can verify the added attributes.
    show system telemetry attributes
    syscon-2-active# show system telemetry attributes
    KEY       KEY       VALUE
    test.key  test.key  test.value
You can add, modify, or delete the instruments that are configured for an exporter from the CLI.
    config
    • Add a new instrument
      system telemetry exporters exporter <*server name*> config instruments <*instrument name*>
      syscon-2-active(config)#  system telemetry exporters exporter server1 config instruments hardware
    • Modify the instrument
      system telemetry exporters exporter <*server name*> config instruments [<*instrument name*>]
      syscon-2-active(config)#  system telemetry exporters exporter server1 config instruments [ optics ]
    • Delete the instrument
      no system telemetry exporters exporter <*server name*> config instruments <*instrument name*>
      syscon-2-active(config)#  no system telemetry exporters exporter server1 config instruments platform
    commit
  6. Return to user (operational) mode.
    end
You can monitor data and metrics related to the usage, performance, and behavior of the system from the webUI. These statistics are crucial for monitoring, managing, and optimizing the system. You can monitor the following system details:
  • System CPU Usage: Shows the measurement of CPU utilization by the system.
  • System Memory Usage: Shows the measurement of memory utilization by the system.
  • System Disk Usage: Shows the measurement of disk utilization by the system.
You can monitor system’s statistics from the webUI.
  2. On the left, click SYSTEM SETTINGS > System Details.
  3. Select a configured blade from the Blade dropdown to see the system statistics.
    You can now see the following statistics and status of the system.
    • System CPU Usage: Displays the vCPU’s current utilization of the system by default. However, if multiple vCPUs are available, you can select a vCPU and change the time series to view the historical data and analyze the vCPU utilization.
    • System Memory Usage: Displays the current memory utilization of the system by default. However, you can change the time series to view the historical data and analyze ‌memory utilization.
    • System Disk Usage: Displays the disk’s current utilization of the system by default. However, if multiple disks are available, you can select a disk, data type, and change the time series to view the historical data and analyze ‌memory utilization
You can monitor data and metrics related to the usage, performance, and behavior of a tenant from the CLI. These statistics, tenant CPU usage, memory usage and disk usage, are crucial for monitoring, managing, and optimizing the tenant.
  1. Log in to the command line interface (CLI) of the chassis partition using an account with admin access.
  2. Show ‌tenants status and statistics.
    tenants tenant <*tenant name*> state <*action*>
    Note: You can get the stats with an average of 10 seconds, 30 seconds, 1 minute, 5 minutes, and 10 minutes.
    • For CPU stats that average for every 1 minute:
      default-1(config)# components component blade-1 state cpu-thread-stats average 1m-avg
      averages {
              unix-seconds 1717588320
              cpu-threads {
                  cpu-thread {
                      thread-index 0
                      busy-percent 1
                  cpu-thread {
                      thread-index 1
                      busy-percent 0
                  cpu-thread {
                      thread-index 2
                      busy-percent 0
                  cpu-thread {
                      thread-index 3
                      busy-percent 4
                  cpu-thread {
                      thread-index 4
                      busy-percent 4
                  cpu-thread {
                      thread-index 5
                      busy-percent 4
                  cpu-thread {
                      thread-index 6
                      busy-percent 4
                  cpu-thread {
                      thread-index 7
                      busy-percent 12
                  cpu-thread {
                      thread-index 8
                      busy-percent 4
                  cpu-thread {
                      thread-index 9
                      busy-percent 1
                  cpu-thread {
                      thread-index 10
                      busy-percent 4
                  cpu-thread {
                      thread-index 11
                      busy-percent 4
                  cpu-thread {
                      thread-index 12
                      busy-percent 4
      default-1(config)#
    • For disk stats that average for every 1 minute:
      default-1(config)# components component blade-1 state disk-stats average 1m-avg
      averages {
              unix-seconds 1717588260
              used-percent 88
              disk-list {
                  disk {
                      disk-name nvme0n1
                      total-iops 0
                      read-iops 0
                      read-bytes 148
                      write-iops 154
                      write-bytes 1691163
      default-1(config)#
    • For interface stats that average for every 1 minute:
      default-1(config)# components component blade-1 state interface-stats average 1m-avg
      averages {
              unix-seconds 1717588380
              interface-list {
                  interface {
                      interface-name 1.0
                      ifc-bytes-in 1466
                      ifc-bytes-out 0
                      ifc-packets-in 0
                      ifc-packets-out 0
                  interface {
                      interface-name 2.0
                      ifc-bytes-in 135
                      ifc-bytes-out 0
                      ifc-packets-in 0
                      ifc-packets-out 0
      default-1(config)#
    • For memory stats that average for every 1 minute:
      default-1(config)# components component blade-1 state memory-stats average 1m-avg
      averages {
              unix-seconds 1717588440
              available 8493508881
              free 1060426615
              used-percent 93
              platform-total 16107667456
              platform-used 8114811835
      default-1(config)#