Updated Date: 07/07/2026
Platform Specifications
This table lists general specifications for system features for VELOS platforms.
| Item | Specification |
| Transceiver modules hot swap | Support for hot swap of optical transceiver modules |
| Dynamic routing protocols | BFD, BGP4, IS-IS, OSPFv2, OSPFv3, RIPv1/RIPv2, RIPng |
| Jumbo frames | Support for maximum Ethernet frame size of 9216 bytes and MTU of 9128 bytes |
| Tenant software | Supports provisioning and managing multiple, hosted instances of tenant software on a single hardware system |
This table lists hardware specifications for VELOS CX410 chassis with single wide BX110 blades.
Item |
Specification |
Dimensions |
H: 6.9 inches (17.5 cm) x W: 17.4 inches (44.2 cm) x D: 32.0 inches (81.3 cm) rack-mount chassis |
Chassis weight |
Fully-loaded system (8 blades, 4 power supply units (PSUs), 1 fan tray, 2 system controllers, 2 PSU controllers): 192 pounds (87 kg) Half-loaded system (4 blades, 4 blanks, 2 PSUs, 1 fan tray, 2 system controllers, 2 PSU controllers): 150 pounds (68 kg) Empty chassis, as shipped (0 blades, 8 blanks, 2 PSUs, 1 fan tray, 2 system controllers, 2 PSU controllers): 132 pounds (60 kg) Empty chassis, components removed for installation (0 blades, 0 blanks, 0 PSUs, 0 fan tray, 2 system controllers): 91 pounds (41 kg) |
Components weight |
AC power supply: 6.4 pounds (2.9 kg) Power supply blank: 0.2 pounds (0.09 kg) BX110 blade: 7.3 pounds (3.3 kg) Blank: 0.1 pounds (0.05 kg) Fan tray: 12.0 pounds (5.4 kg) System controller: 10.5 pounds (4.8 kg) PSU controller: 0.5 pounds (0.2 kg) |
Processor |
See blade specifications |
Storage drive capacity |
RAM |
AC power input requirements |
2 to 4 x 3000W 200-240 VAC input 17A per input (max) Requires NEMA 6-20R wall outlet or a region-specific equivalent Important: The VELOS CX410 chassis supports only AC power supply units (PSUs). Other PSU types are incompatible, and the chassis is designed to physically prevent use of an incompatible PSU type. |
Important: Specifications are subject to change without notification.
This table lists hardware specifications for VELOS CX410-N (NEBS) chassis with single wide BX110 Blades.
Item |
Specification |
Chassis weight |
Components weight |
DC power supply: 7.0 pounds (3.18 kg) Power supply blank: 0.2 pounds (0.09 kg) BX110 blade: 7.3 pounds (3.3 kg) Blank: 0.1 pounds (0.05 kg) Fan tray: 12.0 pounds (5.4 kg) System controller: 10.5 pounds (4.8 kg) PSU controller: 0.5 pounds (0.2 kg) |
Processor |
RAM |
DC power supply |
2 to 4 x 3000W 40-72 VDC input (operating minimum range) 85A (max) Input Voltage Range −38 to −75 VDC Turn-off Voltage (falling) −38.5 +/− 1 VDC Turn-on Voltage (rising) -43.0 +/- 0.5 VDC Important: The VELOS CX410-N chassis supports only DC power supply units (PSUs). Other PSU types are incompatible, and the chassis is designed to physically prevent use of an incompatible PSU type. |
This table lists hardware specifications for VELOS CX1610 chassis with double wide BX520 blades.
Item |
Specification |
Dimensions |
H: 27.9 inches (707.7 mm) x W: 17.4 inches (441 mm) x D: 32.6 inches (828 mm) rack-mount chassis |
Chassis weight |
Fully-loaded chassis (32 blades, 12 power supply units (PSUs), 4 fan trays, 2 system controllers, 4 PSU controllers): 616 pounds (280 kg) Half-loaded chassis (16 blades, 16 blanks, 6 PSUs, 4 fan trays, 2 system controllers, 4 PSU controllers): 472 pounds (214 kg) Empty chassis, as shipped (0 blades, 32 blanks, 6 PSUs, 4 fan trays, 2 system controllers, 4 PSU controllers): 328 pounds (149 kg) Empty chassis, components removed for installation (0 blades, 0 blanks, 0 PSUs, 0 fan trays, 2 system controllers): 220 pounds (100 kg) |
Components weight |
AC power supply: 6.4 pounds (2.9 kg) Power supply blank: 0.2 pounds (0.09 kg) BX520 blade: 18.0 pounds (8.2 kg) Blank: 0.1 pounds (0.05 kg) Fan tray: 12.0 pounds (5.4 kg) System controller: 10.5 pounds (4.8 kg) PSU controller: 0.5 pounds (0.2 kg) |
Processor |
RAM |
Up to 12 x 3000W 200-240 VAC input 17A per input (max) Requires NEMA 6-20R wall outlet or a region-specific equivalent Each system controller consumes up to 500W. Each fan consumes up to 400W. Each BX520 blade consumes up to 900W. A CX1610 chassis with two (2) system controllers, sixteen (16) BX520 blades, and twelve (12) DC PSUs will consume 15,565 watts. A CX1610 chassis with two (2) system controllers, sixteen (16) BX520 blades, and six (6) DC PSUs will consume 16,150 watts. Each PSU is capable of sourcing 3000 watts. |
This table lists hardware specifications for VELOS CX1610-N (NEBS) chassis with double wide BX520 blades.
Item |
Specification |
Dimensions |
Chassis weight |
Components weight |
DC power supply: 7.0 pounds (3.2 kg) Power supply blank: 0.2 pounds (0.09 kg) BX520 blade: 18.0 pounds (8.2 kg) Blank: 0.1 pounds (0.05 kg) Fan tray: 12.0 pounds (5.4 kg) System controller: 10.5 pounds (4.8 kg) PSU controller: 0.5 pounds (0.2 kg) |
Processor |
RAM |
DC power supply |
6 to 12 x 3000W PSUs 85A (max) Input Voltage Range −38 to −75 VDC Turn-off Voltage (falling) −38.5 +/− 1 VDC Turn-on Voltage (rising) -43.0 +/- 0.5 VDC Important: The VELOS CX410-N chassis supports only DC power supply units (PSUs). Other PSU types are incompatible, and the chassis is designed to physically prevent use of an incompatible PSU type. |
This table lists hardware specifications for VELOS SX410 system controller.
Specification |
SX410 |
Dimensions |
Proprietary to fit F5 chassis |
Weight |
10.5 pounds (4.8 kg) |
Processor |
1 x 8-Core Intel Atom processor (total 8 hyperthreaded logical processing cores) |
Communication interfaces |
1 x 10GbE management port 1 x RJ45 console port 1 x USB 3.0 interface |
1 x 1 TB solid-state drive (SSD) |
RAM |
32 GB |
This table lists hardware specifications for VELOS SX1610 system controller.
Specification |
SX1610 |
Dimensions |
Weight |
16 pounds (7.3 kg) |
Processor |
1 x16-Core Intel Atom processor (total 16 hyperthreaded logical processing cores) |
1 x 3 TB solid-state drive (SSD) |
RAM |
32 GB |
This table lists hardware specifications for VELOS BX110 blades.
Note:
Each QSFP28 port also supports these alternate transceiver modules or breakout modes:
- 40GbE QSFP+ modules
- 4 x 25GbE using QSFP28 or QSFP+ breakout or AOC cables
- 4 x 10GbE using QSFP28 or QSFP+ breakout or AOC cables
| Specification | BX110 |
| Dimensions | Proprietary to fit F5 chassis |
| Weight | 7.3 pounds (3.3 kg) |
| Processor | 1 x 14-Core Intel Xeon processor (total 28 hyperthreaded logical processing cores) (22 usable for tenants) |
| Communication interfaces | 2 x 100GbE QSFP28 ports |
| Storage drive capacity | 1 x 1 TB solid-state drive (SSD) |
| RAM | 128 GB |
Important: F5 only provides support for F5-branded or F5-provided optical modules.
This table lists hardware specifications for VELOS BX520 blades.
Specification |
BX520 | ||||||
Dimensions |
Proprietary to fit F5 chassis | ||||||
Weight |
18.0 pounds (8.2 kg) | ||||||
Processor |
2 x 28-Core Intel Xeon processors (total 112 hyperthreaded logical cores) (96 usable for tenants) | ||||||
Note: The VELOS BX520 blade support homogeneous and limited mixed portgroup mode combinations per blade. You can configure the port groups using the specific port group combination. | ||||||
1 x 3 TB solid-state drive (SSD) | ||||||
RAM |
512 GB |
This table lists environmental operating specifications for the VELOS chassis.
Note: NEBS platforms meet NEBS environmental requirements per GR-63-CORE, with exceptions noted under “Guidelines for NEBS platforms.”
Item |
Specification |
Operational temperature |
32° to 104°F (0° to 40°C) |
Operational temperature (NEBS-compliant system) |
23° to 131°F (-5° to 55°C) Note: NEBS platforms meet NEBS requirements per GR-63-CORE. |
Operational relative humidity |
5% to 85% (40°C) non-condensing Up to 93% (40°C) non-condensing for a maximum of 96 hours |
Non-operational temperature |
-40° to 158°F (-40° to 70°C) |
Non-operational temperature (NEBS-compliant system) |
-40 to 158°F (-40° to 70°C) Note: NEBS platforms meet NEBS requirements per GR-63-CORE. |
Non-operational relative humidity |
5% to 93% (40°C) non-condensing |
The system automatically load-balances power across all power supply units (PSUs) installed in the chassis. No configuration is required for PSUs to supply power.
The PSU redundancy mode setting controls only when the system generates warnings and alerts about PSU capacity. It does not change how power is distributed. The default mode is no-redundancy.
The VELOS chassis supports these power configuration modes:
No redundancy The chassis has enough working power supply units (PSUs) to support all installed components.
N+1 redundancy The chassis has more working PSUs than are required to support all installed components. The system will remain fully functional if a single PSU fails.
N+N redundancy The chassis has twice as many working PSUs than are required to support all installed components. This configuration is typically used in DC installations with two independent DC power buses. The system will remain fully functional if half of the working PSUs fail (or if one of the facility’s two DC buses fails).
In the event that there is insufficient power to support all installed components, the system provides a warning. These warnings are configurable.
CX410 supports one to four AC or DC power supply units (PSUs). At high-line input, a single PSU has sufficient capacity to support up to four blade slots with no redundancy. This table shows some of the possible blade and PSU redundancy configurations.
VELOS CX410 AC and DC power provisioning recommendations
| Blade quantity | Number of required PSUs | ||
| No redundancy | N + 1 redundancy | N + N redundancy | |
| 1 | 1 | 2 | 2 |
| 2 | 1 | 2 | 2 |
| 3 | 1 | 2 | 2 |
| 4 | 1 | 2 | 2 |
| 5 | 2 | 3 | 4 |
| 6 | 2 | 3 | 4 |
| 7 | 2 | 3 | 4 |
| 8 | 2 | 3 | 4 |
VELOS CX1610 AC and DC power provisioning recommendations
| 1 | 2 | 3 | 4 |
| 2 | 2 | 3 | 4 |
| 3 | 2 | 3 | 4 |
| 4 | 3 | 4 | 6 |
| 5 | 3 | 4 | 6 |
| 6 | 3 | 4 | 6 |
| 7 | 3 | 4 | 6 |
| 8 | 4 | 5 | 8 |
| 9 | 4 | 5 | 8 |
| 10 | 4 | 5 | 8 |
| 11 | 4 | 5 | 8 |
| 12 | 5 | 6 | 10 |
| 13 | 5 | 6 | 10 |
| 14 | 5 | 6 | 10 |
| 15 | 6 | 7 | 12 |
| 16 | 6 | 7 | 12 |
You can view the redundancy state of power supply units (PSUs) installed in the chassis from the system controller CLI.
Connect using SSH to the system controller floating management IP address.
Log in to the command line interface (CLI) of the system controller using an account with admin access.
When you log in to the system, you are in user (operational) mode.
View the current PSU redundancy state.
show components component chassis psu stateA summary similar to this example displays:
syscon-1-active# show components component chassis psu state psu state redundancy-mode no-redundancy psu state severity warning
You can change the redundancy alert mode for power supply units (PSUs) installed in the chassis from the system controller CLI.
syscon-1-active# show components component chassis psu state psu state redundancy-mode no-redundancy psu state severity warning -
Change to config mode.
configThe CLI prompt changes to include
(config). -
Set the PSU redundancy alert mode.
components component chassis psu config redundancy-mode [ n+1 | n+n | no-redundancy ]In this example, you configure the PSU redundancy mode to be
n+n:syscon-1-active(config)# components component chassis psu config redundancy-mode n+n -
Commit the configuration changes.
commit -
Return to user (operational) mode.
end -
Confirm that the configured PSU redundancy mode is active.
In this example, the
n+nredundancy mode is now active:syscon-1-active# show components component chassis psu state psu state redundancy-mode n+n psu state severity warning
You can configure the severity level for power supply units (PSUs) redundancy modes from the system controller CLI.
(config). -
Change the severity level for a specified PSU redundancy mode.
components component chassis psu config severity [ alert | critical | emergency | error | notice | warning ] redundancy-mode [ n+1 | n+n | no-redundancy ]Severity Description Emergency Emergency system panic messages Alert Serious errors that require administrator intervention Critical Critical errors, including hardware and file system failures Error Non-critical, but possibly important, error messages Warning (default) Warning messages that should be logged and reviewed Notice Messages that contain useful information, but might be ignored In this example, you configure the severity level for the
n+nPSU redundancy mode to beerror:syscon-1-active(config)# components component chassis psu config severity error redundancy-mode n+n -
commit -
end -
Confirm that the selected PSU severity level is active.
n+nredundancy mode now has a severity level oferror:syscon-1-active# show components component chassis psu state psu state redundancy-mode n+n psu state severity error
You can view information about active system alarm conditions from the system controller CLI.
View a list of active system alarm conditions.
show system alarms | tabThis example shows a power supply unit (PSU) redundancy fault:
syscon-1-active# show system alarms ID RESOURCE SEVERITY TEXT TIME CREATED –––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––––- 65796 psu-controller WARNING PSU redundancy fault detected 2021-07-01-11:11:11.992270499 UTC 65793 psu-2 ERROR PSU fault detected 2021-07-01-11:11:11.999825828 UTC
When working with an AC-powered VELOS platform, it is important to understand the AC power options and requirements.
The power cable supplied with the hardware is a 220V high-line input cable. This type of cable requires a NEMA 6-20R wall outlet or a region-specific equivalent. Region-specific power cables are available from F5.
Note: The power cables included with this unit are for exclusive use with this unit and should not be used with other electrical appliances.
製品には、同梱された電源コードセットを使用すること及び同梱された電源コー ドセットは、他の製品に使用しないこと.
The actual amount of power draw from the AC source depends on the type and number of blades, and the power supply AC source voltage and redundancy configuration.
This table shows several possible configurations for high-line input voltage (220 VAC) and the typical and maximum power draw measured at the input of the power supply.
| Blade quantity and type | Number of power supplies installed | Typical system power draw (W) [^1] | Maximum system power draw (W) [^2] | Typical system heat, including power supply losses (BTU/hr) | Maximum system heat, including power supply losses (BTU/hr) |
| 1 x BX110 | 2+0 | 935W | 1195W | 3195 BTU/hr | 4080 BTU/hr |
| 1 x BX110 | 2+2 | 965W | 1225W | 3295 BTU/hr | 4180 BTU/hr |
| 2 x BX110 | 2+0 | 1300W | 1635W | 4440 BTU/hr | 5580 BTU/hr |
| 2 x BX110 | 2+2 | 1325W | 1670W | 4525 BTU/hr | 5700 BTU/hr |
| 3 x BX110 | 2+0 | 1645W | 2075W | 5615 BTU/hr | 7080 BTU/hr |
| 3 x BX110 | 2+2 | 1670W | 2100W | 5700 BTU/hr | 7170 BTU/hr |
| 4 x BX110 | 2+0 | 2020W | 2520W | 6895 BTU/hr | 8600 BTU/hr |
| 4 x BX110 | 2+2 | 2040W | 2525W | 6965 BTU/hr | 8620 BTU/hr |
| 5 x BX110 | 2+0 | 2350W | 2945W | 8020 BTU/hr | 10050 BTU/hr |
| 5 x BX110 | 2+2 | 2370W | 2950W | 8090 BTU/hr | 10070 BTU/hr |
| 6 x BX110 | 2+0 | 2715W | 3390W | 9265 BTU/hr | 11570 BTU/hr |
| 6 x BX110 | 2+2 | 2725W | 3380W | 9300 BTU/hr | 11535 BTU/hr |
| 7 x BX110 | 2+0 | 3075W | 3830W | 10495 BTU/hr | 13070 BTU/hr |
| 7 x BX110 | 2+2 | 3080W | 3815W | 10510 BTU/hr | 13020 BTU/hr |
| 8 x BX110 | 2+0 | 3455W | 4280W | 11790 BTU/hr | 14605 BTU/hr |
| 8 x BX110 | 2+2 | 3425W | 4240W | 11690 BTU/hr | 14470 BTU/hr |
| Blade quantity and type | Number of power supplies installed | Typical system power draw (W) [^3] | Maximum system power draw (W) [^4] | Typical system heat, including power supply losses (BTU/hr) | Maximum system heat, including power supply losses (BTU/hr) |
| 1 x BX520 | 2+0 | 1330W | 1540W | 4530 BTU/hr | 5245 BTU/hr |
| 1 x BX520 | 2+2 | 1360W | 1580W | 4640 BTU/hr | 5395 BTU/hr |
| 2 x BX520 | 2+0 | 2080W | 2385W | 7085 BTU/hr | 8135 BTU/hr |
| 2 x BX520 | 2+2 | 2100W | 2400W | 7165 BTU/hr | 8190 BTU/hr |
| 3 x BX520 | 2+0 | 2820W | 3205W | 9615 BTU/hr | 10940 BTU/hr |
| 3 x BX520 | 2+2 | 2830W | 3215W | 9650 BTU/hr | 10970 BTU/hr |
| 4 x BX520 | 2+0 | 3600W | 4095W | 12280 BTU/hr | 13970 BTU/hr |
| 4 x BX520 | 2+2 | 3615W | 4120W | 12330 BTU/hr | 14045 BTU/hr |
| Blade quantity and type | Number of power supplies installed | Typical system power draw (W) [^5] | Maximum system power draw (W) [^6] | Typical system heat, including power supply losses (BTU/hr) | Maximum system heat, including power supply losses (BTU/hr) |
| 1 x BX520 | 6+0 | 2365W | 2965W | 8055 BTU/hr | 10105 BTU/hr |
| 1 x BX520 | 6+6 | 2475W | 3065W | 8440 BTU/hr | 10455 BTU/hr |
| 2 x BX520 | 6+0 | 3125W | 3820W | 10655 BTU/hr | 13035 BTU/hr |
| 2 x BX520 | 6+6 | 3180W | 3905W | 10850 BTU/hr | 13325 BTU/hr |
| 3 x BX520 | 6+0 | 3825W | 4620W | 13040 BTU/hr | 15760 BTU/hr |
| 3 x BX520 | 6+6 | 3935W | 4735W | 13425 BTU/hr | 16155 BTU/hr |
| 4 x BX520 | 6+0 | 4580W | 5445W | 15615 BTU/hr | 18570 BTU/hr |
| 4 x BX520 | 6+6 | 4715W | 5610W | 16080 BTU/hr | 19135 BTU/hr |
| 5 x BX520 | 6+0 | 5325W | 6265W | 18165 BTU/hr | 21375 BTU/hr |
| 5 x BX520 | 6+6 | 5435W | 6355W | 18540 BTU/hr | 21680 BTU/hr |
| 6 x BX520 | 6+0 | 6110W | 7120W | 20840 BTU/hr | 24280 BTU/hr |
| 6 x BX520 | 6+6 | 6240W | 7230W | 21285 BTU/hr | 24670 BTU/hr |
| 7 x BX520 | 6+0 | 6830W | 7910W | 23300 BTU/hr | 26980 BTU/hr |
| 7 x BX520 | 6+6 | 6940W | 7970W | 23670 BTU/hr | 27180 BTU/hr |
| 8 x BX520 | 6+0 | 7650W | 8835W | 26090 BTU/hr | 30135 BTU/hr |
| 8 x BX520 | 6+6 | 7670W | 8760W | 26165 BTU/hr | 29885 BTU/hr |
| 9 x BX520 | 6+0 | 8300W | 9475W | 28320 BTU/hr | 32320 BTU/hr |
| 9 x BX520 | 6+6 | 8360W | 9520W | 28525 BTU/hr | 32470 BTU/hr |
| 10 x BX520 | 6+0 | 9085W | 10385W | 30995 BTU/hr | 35420 BTU/hr |
| 10 x BX520 | 6+6 | 9090W | 10380W | 31010 BTU/hr | 35420 BTU/hr |
| 11 x BX520 | 6+0 | 9775W | 11105W | 33340 BTU/hr | 37885 BTU/hr |
| 11 x BX520 | 6+6 | 9795W | 11125W | 33420 BTU/hr | 37950 BTU/hr |
| 12 x BX520 | 6+0 | 10565W | 12040W | 36040 BTU/hr | 41080 BTU/hr |
| 12 x BX520 | 6+6 | 10585W | 12080W | 36110 BTU/hr | 41215 BTU/hr |
| 13 x BX520 | 6+0 | 11250W | 12755W | 38380 BTU/hr | 43520 BTU/hr |
| 13 x BX520 | 6+6 | 11240W | 12710W | 38340 BTU/hr | 43360 BTU/hr |
| 14 x BX520 | 6+0 | 12040W | 13720W | 41065 BTU/hr | 46805 BTU/hr |
| 14 x BX520 | 6+6 | 12015W | 13650W | 40990 BTU/hr | 46565 BTU/hr |
| 15 x BX520 | 6+0 | 12670W | 14350W | 43230 BTU/hr | 48960 BTU/hr |
| 15 x BX520 | 6+6 | 12665W | 14265W | 43205 BTU/hr | 48670 BTU/hr |
| 16 x BX520 | 6+0 | 13575W | 15480W | 46315 BTU/hr | 52805 BTU/hr |
| 16 x BX520 | 6+6 | 13455W | 15235W | 45900 BTU/hr | 51975 BTU/hr |
When working with a DC-powered VELOS CX410 Series platform, it is important to understand the DC power options and requirements.
The platform supports up to four hot swappable DC power supplies. One power supply powers a chassis that contains zero to four blades, with no redundancy. Four power supplies power a chassis with any blade configuration, with full redundancy.
The actual amount of power draw from the DC power source depends on the type and number of blades and the redundancy configuration.
This table shows several possible configurations, and the typical and maximum power draw measured at the output of the power supply (at an input voltage of 48 VDC).
F5® recommends that you add 10% to the numbers in the table due to conversion loss in power supplies when you are provisioning power and cooling.
| Blade quantity and type | Number of power supplies installed | Typical system power draw (W) [^7] | Maximum system power draw (W) [^8] | Typical system heat, including power supply losses (BTU/hr) | Maximum system heat, including power supply losses (BTU/hr) |
| 1 x BX110 | 2+0 | 970W | 1220W | 3310 BTU/hr | 4165 BTU/hr |
| 1 x BX110 | 2+2 | 1065W | 1355W | 3635 BTU/hr | 4625 BTU/hr |
| 2 x BX110 | 2+0 | 1345W | 1715W | 4590 BTU/hr | 5855 BTU/hr |
| 2 x BX110 | 2+2 | 1415W | 1765W | 4830 BTU/hr | 6025 BTU/hr |
| 3 x BX110 | 2+0 | 1710W | 2175W | 5835 BTU/hr | 7425 BTU/hr |
| 3 x BX110 | 2+2 | 1785W | 2215W | 3095 BTU/hr | 7560 BTU/hr |
| 4 x BX110 | 2+0 | 2075W | 2620W | 7080 BTU/hr | 8940 BTU/hr |
| 4 x BX110 | 2+2 | 2160W | 2675W | 7370 BTU/hr | 9130 BTU/hr |
| 5 x BX110 | 2+0 | 2440W | 3075W | 8330 BTU/hr | 10495 BTU/hr |
| 5 x BX110 | 2+2 | 2475W | 3095W | 8445 BTU/hr | 10565 BTU/hr |
| 6 x BX110 | 2+0 | 2800W | 3550W | 9555 BTU/hr | 12115 BTU/hr |
| 6 x BX110 | 2+2 | 2840W | 3555W | 9695 BTU/hr | 12130 BTU/hr |
| 7 x BX110 | 2+0 | 3200W | 4030W | 10920 BTU/hr | 13755 BTU/hr |
| 7 x BX110 | 2+2 | 3180W | 3990W | 10855 BTU/hr | 13615 BTU/hr |
| 8 x BX110 | 2+0 | 3575W | 4505W | 12200 BTU/hr | 15375 BTU/hr |
| 8 x BX110 | 2+2 | 3555W | 4445W | 12130 BTU/hr | 15170 BTU/hr |
| Blade quantity and type | Number of power supplies installed | Typical system power draw (W) [^9] | Maximum system power draw (W) [^10] | Typical system heat, including power supply losses (BTU/hr) | Maximum system heat, including power supply losses (BTU/hr) |
| 1 x BX520 | 2+0 | 1450W | 1655W | 4940 BTU/hr | 5650 BTU/hr |
| 1 x BX520 | 2+2 | 1475W | 1705W | 5025 BTU/hr | 5820 BTU/hr |
| 2 x BX520 | 2+0 | 2210W | 2565W | 7540 BTU/hr | 8755 BTU/hr |
| 2 x BX520 | 2+2 | 2220W | 2580W | 7565 BTU/hr | 8805 BTU/hr |
| 3 x BX520 | 2+0 | 2985W | 3460W | 10175 BTU/hr | 11810 BTU/hr |
| 3 x BX520 | 2+2 | 2990W | 3460W | 10190 BTU/hr | 11810 BTU/hr |
| 4 x BX520 | 2+0 | 3815W | 4440W | 13015 BTU/hr | 15150 BTU/hr |
| 4 x BX520 | 2+2 | 3775W | 4370W | 12880 BTU/hr | 14915 BTU/hr |
| Blade quantity and type | Number of power supplies installed | Typical system power draw (W) [^11] | Maximum system power draw (W) [^12] | Typical system heat, including power supply losses (BTU/hr) | Maximum system heat, including power supply losses (BTU/hr) |
| 1 x BX520 | 6+0 | 2635W | 3245W | 8985 BTU/hr | 11065 BTU/hr |
| 1 x BX520 | 6+6 | 2790W | 3470W | 9520 BTU/hr | 11830 BTU/hr |
| 2 x BX520 | 6+0 | 3395W | 4095W | 11580 BTU/hr | 13975 BTU/hr |
| 2 x BX520 | 6+6 | 3625W | 4440W | 12355 BTU/hr | 15145 BTU/hr |
| 3 x BX520 | 6+0 | 4065W | 4890W | 13860 BTU/hr | 16670 BTU/hr |
| 3 x BX520 | 6+6 | 4330W | 5165W | 14770 BTU/hr | 17615 BTU/hr |
| 4 x BX520 | 6+0 | 4790W | 5715W | 16345 BTU/hr | 19495 BTU/hr |
| 4 x BX520 | 6+6 | 5065W | 5955W | 17270 BTU/hr | 20310 BTU/hr |
| 5 x BX520 | 6+0 | 5560W | 6630W | 18970 BTU/hr | 22620 BTU/hr |
| 5 x BX520 | 6+6 | 5715W | 6595W | 19490 BTU/hr | 22500 BTU/hr |
| 6 x BX520 | 6+0 | 6295W | 7475W | 21465 BTU/hr | 25490 BTU/hr |
| 6 x BX520 | 6+6 | 6495W | 7515W | 22155 BTU/hr | 25630 BTU/hr |
| 7 x BX520 | 6+0 | 7010W | 8295W | 23910 BTU/hr | 28290 BTU/hr |
| 7 x BX520 | 6+6 | 7100W | 8300W | 24220 BTU/hr | 28320 BTU/hr |
| 8 x BX520 | 6+0 | 7795W | 9250W | 26590 BTU/hr | 31550 BTU/hr |
| 8 x BX520 | 6+6 | 7820W | 9155W | 26670 BTU/hr | 31235 BTU/hr |
| 9 x BX520 | 6+0 | 8490W | 9985W | 28960 BTU/hr | 34060 BTU/hr |
| 9 x BX520 | 6+6 | 8530W | 9945W | 29105 BTU/hr | 33920 BTU/hr |
| 10 x BX520 | 6+0 | 9275W | 10890W | 31645 BTU/hr | 37155 BTU/hr |
| 10 x BX520 | 6+6 | 9240W | 10740W | 31515 BTU/hr | 36640 BTU/hr |
| 11 x BX520 | 6+0 | 10015W | 11800W | 34170 BTU/hr | 40250 BTU/hr |
| 11 x BX520 | 6+6 | 9960W | 11555W | 33970 BTU/hr | 39420 BTU/hr |
| 12 x BX520 | 6+0 | 10750W | 12640W | 36675 BTU/hr | 43130 BTU/hr |
| 12 x BX520 | 6+6 | 10665W | 12390W | 36390 BTU/hr | 42265 BTU/hr |
| 13 x BX520 | 6+0 | 11480W | 13460W | 39165 BTU/hr | 45910 BTU/hr |
| 13 x BX520 | 6+6 | 11395W | 13070W | 38870 BTU/hr | 44595 BTU/hr |
| 14 x BX520 | 6+0 | 12235W | 14305W | 41735 BTU/hr | 48805 BTU/hr |
| 14 x BX520 | 6+6 | 12095W | 13845W | 41265 BTU/hr | 47230 BTU/hr |
| 15 x BX520 | 6+0 | 12985W | 15245W | 44305 BTU/hr | 52005 BTU/hr |
| 15 x BX520 | 6+6 | 12850W | 14805W | 43830 BTU/hr | 50510 BTU/hr |
| 16 x BX520 | 6+0 | 13795W | 16215W | 47055 BTU/hr | 55320 BTU/hr |
| 16 x BX520 | 6+6 | 13590W | 15695W | 46365 BTU/hr | 53555 BTU/hr |
Available Network Equipment-Building System (NEBS)-compliant VELOS system configurations.
Note: For a system to be completely NEBS-compliant, you must use a NEBS-compliant DC-powered chassis and blades.
| Configuration | Blade Type | Chassis |
| 1 | BX110 | CX410-N |
| 2 | BX520 | CX1610-N |
This declaration of conformity is issued under the sole responsibility of the manufacturer. This product conforms to the relevant Union harmonised legislation: Directives 2014/35/EU, 2014/30/EU, and 2011/65/EU.
IEC 62368-1:2014 (Second Edition) |
EN 62368-1:2014+A11:2017 |
CSA C22.2 No. 62368-1-14, UL 62368-1, 2nd edition |
ETSI EN 300 386 V1.6.1 (2012) Class A |
EN 55032:2012/AC:2013 Class A |
EN 55024:2010 Class A |
IEC 63000:2018 |
This table lists acoustic levels and operational altitude specifications for VELOS platforms.
Specification type |
Detail |
Value |
Notes |
Acoustic |
Sound power |
81.4 dBA |
A-weighted Sound Power at 27°C full system load. |
Altitude |
Operational |
6,000 Feet |
Per Telcordia GR-63-CORE, section 4.1.3: This unit is functional when installed at elevations between 60m (197 feet) below sea level and 1800m (6000 feet) above sea level at the aisle ambient temperatures of 40°C. Note: NEBS-compliant platforms conform to NEBS specifications above 6000 feet. |
Non-operational |
40,000 Feet |
This table lists airflow movement specifications for VELOS platforms.
Note: Fan tray airflow measurements are taken at 100% duty cycle and in open air.
| Platform | Value (max) |
| CX410 | 711 CFM (237 CFM per fan x 3 fans) |
| CX1610 | 2,845 CFM (237 CFM per fan x 12 fans) |